Results 1 to 8 of 8
Thread: looking for some advice
-
04-07-2008, 08:00 PM #1
looking for some advice
I would like to know if I can convert a chill room to a cold room without changing any of the evap. or shutting down the systems. It is Hussaman rack system.
-
04-07-2008, 11:58 PM #2
Re: looking for some advice
should not be a problem just fit a epr into suction line of room
-
16-07-2008, 12:56 PM #3
Re: looking for some advice
Just to be clear, do you mean to convert from low temp (freezer) to medium temp (cooler)? Or vice versa?
An epr will allow you to run a medium temp circuit from a low temp rack, but not vice versa.
-
16-07-2008, 02:27 PM #4
Re: looking for some advice
Right,if you convert a chiller room to say freezer room,comes many factor to consider.
1.Panel Insulation.
2.Product Load.
3.Required Temp.
After computing the above factors, you may now arrive at the required capacity.Existing equipment capacity should now be checked if it matched based on the converted refrigeration load.
abet
-
16-07-2008, 05:50 PM #5
Re: looking for some advice
Mr JamCoool.
One thing many people forget is, that even if your equipment has sufficient spare duty.
To run at the lower temperatures and pressures.
The fabric of the chamber or more importantly the floor is unlikely to be insulated sufficiently.
Without the proper insulated floor, you will be using huge amounts of energy to freeze the floor.
Which as a result may well crackup and suffer from frost heave.
WORTH LOOKING AT! Prior to spending out on equipment conversions.
Cheers Grizzly.
-
16-07-2008, 06:32 PM #6
Re: looking for some advice
No can do.
The fins on the evaporator are designed for +C°, you will need some kind of defrost for a freezer.
Cold room controller doe's not "know" how to control a freezer, new wiring and piping is required.
As Grizzly have said, the insulation is not sufficient, heating around the door, air pressure relief valve.
To make a long story short, you cant.
-
16-07-2008, 07:46 PM #7
Re: looking for some advice
I would say that you can.
A chill room and a cold room is the same thing.
You need to be more specific.
ChillinIF AT FIRST YOU DON`T SUCCEED.
DESTROY ALL EVIDENCE THAT YOU TRIED!
and go get a cuppa
-
16-07-2008, 07:49 PM #8
Re: looking for some advice
In this case just set the temp a few ° lower.
Similar Threads
-
Advice needed for a friend
By marc5180 in forum TrainingReplies: 10Last Post: 10-06-2009, 10:56 PM -
Career advice please.
By james 100 in forum Chit Chat & Service StoriesReplies: 14Last Post: 13-09-2007, 06:37 PM -
Dont be shy, advice needed.
By Sledge in forum Air ConditioningReplies: 9Last Post: 27-06-2007, 03:09 PM -
Your advice to Split Air buyers.
By mick2me in forum Air ConditioningReplies: 5Last Post: 15-07-2006, 04:59 PM