Results 1 to 8 of 8
Thread: howden xrv compressors
14-07-2008, 08:17 AM #1
I have 4 x new ammonia chillers (400KW/600KW) that we have had a lot of teething/snagging issues on. 2 of these units are currently out of action due to ammonia leaks around shaft seals. I have heard rumours that howdens are prone to these with ammonia due to the use of carbon based seals.
Has any one had similar issues/problems or know of them?
14-07-2008, 06:00 PM #2
Re: howden xrv compressors
DAVID
It's possibly due to swarf or slag from the pipework installations.
Were Suction Socks used?
Howdens are usually very reliable and the carbon to steel faced s/seal is very common and reliable itself!
But they are susceptible to particulate contamination
within the oil.
Hence my suggestion.
It may be worth having the oil analysed?
Cheers Grizzly
14-07-2008, 08:22 PM #3
In my experience its not the carbon/steel seals that are the problem - its almost always the "O" ring material thats at fault.
I've lost count of the number of Howden shaft seals I've replaced due to the wrong "O" ring being supplied.
Once the mistake was realised the correct "O" rings were supplied straight away, still look a chump in front of the client when the third seal in as many months fails, but they did sort it out in the end.
Check that the material is compatible with oil and refrigerant together. Make sure Howden check it, not just send a standard seal
I've only once seal a howden shaft seal fail from another cause, that was a crack around the circumfrence of the carbon, probably due to being dropped during delivery.
Regards,
Plank!
14-07-2008, 10:23 PM #4
Hi Plank
A very good point you are making there.
One which I have also experienced.
May I ask has this happened to you on a Ammonia based plant.
I ask because I have yet to experience this type of failure on Ammonia.
BUT YOU DEFIANTLY MAY BE ON TO SOMETHING?
Frick s/seals leak like a sieve if the wrong one of 2 identical (looking) "o" rings is fitted.
Thanks Grizzly
14-07-2008, 10:24 PM #5
Hi, David Atkinson
Howden is using John Crane shaft seals and they are good, but this was a problem....
Originally Posted by Plank!
Originally Posted by Grizzly
Best regards, Josip
14-07-2008, 11:08 PM #6
Originally Posted by GrizzlyIf all else fails, ask for help.
15-07-2008, 11:01 PM #7
Grizzly, This same problem has occoured 3 times now in 6 - 8 years, in all cases it was ammonia tho each time it was on a different site, one during commisioning, the others less than 1 or 2 years old.
I can't remember the exact details of the oil tho one i know was REFLO 68A and I'm certain atleast one of the other sites was on a fully synthetic oil.
Offhand i don't remember the "O" ring material that cured the problem, will try and find out next week when i'm back at work.
I think the solution here is to speak with Howden direct and not just let the office order the standard seal, I think most of us here know there is no such thing as a standard plant
15-07-2008, 11:19 PM #8
Hi David
Plank is right about the type of O ring material, I had problems similar to yours several years ago and we found the O ring material was incorrect. If you Google O ring usage you might find a comparison chart. I have one but I am out of the office for a few days, if you can't find one let me know and I will post it when I am back.
Also if the replacement seal is not a genuine check the grade of carbon used, this can also cause a problem, from memory I think it's F35.
As Josip stated John Crane seals are usually very reliable.
Paul
Howden H&HP Screw Compressors
By Josip in forum Industrial CompressorsReplies: 15Last Post: 21-11-2009, 02:36 PM -
Howden compressors with different oil injection
By Mark VI in forum Industrial CompressorsReplies: 32Last Post: 14-06-2009, 11:14 AM -
Compressors - screw or reciprocating?
By Josip in forum Industrial CompressorsReplies: 18Last Post: 27-01-2009, 10:36 PM -
Do we have some expert in replacing compressors
By Zahid in forum Air ConditioningReplies: 2Last Post: 01-07-2008, 07:59 AM