    hot gas defrost for large ref. units - monoblock



    We had installed 5nos 60 HP units for a large cold store. The defrost is with elec heaters at present. Now the system is almost 10 years old. When te heaters in the coil get damaged, the replacement is a big issue. So we are planning to change over to Hot gas defrost system I had seen a carrier article on precautions on such large units.

    But I want to get the practical aspects on this. What I had seen that the Liquid from evaporator during HGD is transferred to Receiver & does not go to the compressor. But then how compressor runs as it ahs to get gas somehow?



  2. #2
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: hot gas defrost for large ref. units - monoblock

    Don't do it.

    If the evaporator is not designed for gas defrost you will get leaks very soon more if it is old or has corrosion.

    The suction accumulator is undersized and you would need to change it.

    Try placing electric defrot in the front of the evap and below the coil with metal clips. With this you should easily remove them.

    If you have frost problems you should recalculate your evaporator surface, placement or defrost control. This also means to think where does the water come from and defrost thermostat bulb placement.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: hot gas defrost for large ref. units - monoblock

    I can't imagine a more difficult project than trying to convert a lot of electric defrost evaporators to hot gas! The amount of retro-fitting that would have to occur would be very high.

    I don't think it's impossible, however, the evaporator modification required would be the most difficult.

    And, as you say you have to have a gas source for the compressor to provide hot gas.

    A company called Kramer-Trenton many years ago had a system like this that used hot gas defrost on a single compressor/evaporator system. Their patent covered a concept that used a small tank that evaporated the returning defrost condensate from the evaporator to create the suction gas for the compressor. You might still be able to find some links for this on the web.

    They were complicated little systems that did work, but not much fun to service...
    If all else fails, ask for help.


  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: hot gas defrost for large ref. units - monoblock

    That is what I was thinking. Since no one is doing that, there must be some reasons As explained by USiceman.

  5. #5
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: hot gas defrost for large ref. units - monoblock

    Quote Originally Posted by smpsmp45 View Post
    That is what I was thinking. Since no one is doing that, there must be some reasons As explained by USiceman.
    In a one evaporator one compressor system it is not even clear if you would save energy doing hot gas defrost.

    You can save if you can defrost some evaps while using the compressor on others to cool.

    In this case I don't think it is worth the trouble either.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: hot gas defrost for large ref. units - monoblock

    Depending on the system configuration hot gas could(notice I said could) be an alternative. If the existing systems are a single evaporator/compressor it would definitely be the worse case scenario.

    An alternative solution might be to group the compressors into something like a rack system (common system) so that using hot gas defrost could be done.

    The easiest way I can think to convert the coils to DX is to change the distributors and use a side port distributor for the hot gas. Dump the hot gas into the distributor tubes and voila, instant hot gas defrost. You still have some modifications required for valve, etc but these are discussed in the hot gas paper smpsmp45 found the other day.
    If all else fails, ask for help.


Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Toshiba RAV SM/SP1400 defrost problem
    By SteinarN in forum Heat Pumps
    Replies: 11
    Last Post: 20-02-2008, 04:25 PM
  3. No Power for Defrost Timer Motor
    By kln in forum Domestic
    Replies: 6
    Last Post: 21-01-2008, 08:22 AM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 06:25 PM
  5. Hot gas defrost vs Electric defrost
    By herdian in forum Industrial
    Replies: 19
    Last Post: 13-08-2007, 11:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •