10-07-2008, 09:29 AM #1
hot gas defrost for large ref. units - monoblock
We had installed 5nos 60 HP units for a large cold store. The defrost is with elec heaters at present. Now the system is almost 10 years old. When te heaters in the coil get damaged, the replacement is a big issue. So we are planning to change over to Hot gas defrost system I had seen a carrier article on precautions on such large units.
But I want to get the practical aspects on this. What I had seen that the Liquid from evaporator during HGD is transferred to Receiver & does not go to the compressor. But then how compressor runs as it ahs to get gas somehow?
-
10-07-2008, 02:18 PM #2
Re: hot gas defrost for large ref. units - monoblock
Don't do it.
If the evaporator is not designed for gas defrost you will get leaks very soon more if it is old or has corrosion.
The suction accumulator is undersized and you would need to change it.
Try placing electric defrot in the front of the evap and below the coil with metal clips. With this you should easily remove them.
If you have frost problems you should recalculate your evaporator surface, placement or defrost control. This also means to think where does the water come from and defrost thermostat bulb placement.
-
10-07-2008, 03:34 PM #3
Re: hot gas defrost for large ref. units - monoblock
I can't imagine a more difficult project than trying to convert a lot of electric defrost evaporators to hot gas! The amount of retro-fitting that would have to occur would be very high.
I don't think it's impossible, however, the evaporator modification required would be the most difficult.
And, as you say you have to have a gas source for the compressor to provide hot gas.
A company called Kramer-Trenton many years ago had a system like this that used hot gas defrost on a single compressor/evaporator system. Their patent covered a concept that used a small tank that evaporated the returning defrost condensate from the evaporator to create the suction gas for the compressor. You might still be able to find some links for this on the web.
They were complicated little systems that did work, but not much fun to service...If all else fails, ask for help.
-
11-07-2008, 05:47 AM #4
Re: hot gas defrost for large ref. units - monoblock
That is what I was thinking. Since no one is doing that, there must be some reasons As explained by USiceman.
-
11-07-2008, 08:39 PM #5
Re: hot gas defrost for large ref. units - monoblock
-
11-07-2008, 09:38 PM #6
Re: hot gas defrost for large ref. units - monoblock
Depending on the system configuration hot gas could(notice I said could) be an alternative. If the existing systems are a single evaporator/compressor it would definitely be the worse case scenario.
An alternative solution might be to group the compressors into something like a rack system (common system) so that using hot gas defrost could be done.
The easiest way I can think to convert the coils to DX is to change the distributors and use a side port distributor for the hot gas. Dump the hot gas into the distributor tubes and voila, instant hot gas defrost. You still have some modifications required for valve, etc but these are discussed in the hot gas paper smpsmp45 found the other day.If all else fails, ask for help.
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Toshiba RAV SM/SP1400 defrost problem
By SteinarN in forum Heat PumpsReplies: 11Last Post: 20-02-2008, 04:25 PM -
No Power for Defrost Timer Motor
By kln in forum DomesticReplies: 6Last Post: 21-01-2008, 08:22 AM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 06:25 PM -
Hot gas defrost vs Electric defrost
By herdian in forum IndustrialReplies: 19Last Post: 13-08-2007, 11:25 PM