    0C Coldroom Evaporator operating at 20C



    Hi all,

    I need to pick some brains.

    I have to create a large coldroom (to be operated at 0C) and have selected the evaporator with the following:
    • 3 off evaporators
    • 25 kW duty
    • Propylene glycol (35%) Supply/Return at -10C / -6C
    • Air on / Air off at 2C / 0C
    • 2off 800 diameter fans (100 Pa) per unit
    From the above evaporators can be selected.

    Here comes my Story/Question: During the early project lifespan, the Coldroom shall be used for other purpose and operate at 20C (air off). However, the 3 evaporators must not change when changing from a 20C room to 0C room.

    From my calculations - when operating at 20C, the evaporators are physically oversized as the LMTD differ greatly.

    Any tips?
    Does this mean that my valve station will be modulating alot?
    Has anyone done this before.
    Whats the dehumidification effect?

    Regards,



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: 0C Coldroom Evaporator operating at 20C

    Hi, samiam

    .... what is your cold room for... onion .... potato... something else ...

    Best regards,Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Jun 2007
    Location
    South Africa
    Posts
    80
    Rep Power
    17

    Re: 0C Coldroom Evaporator operating at 20C

    Hi Josip,

    Its a general coldroom - no product spec yet.

    Regards,

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: 0C Coldroom Evaporator operating at 20C

    First of all that is a diverse range of temperatures you have. One main issue I see initially is the need to provide uniform air flow of the area to be maintained by temperature.

    Is this area constant during the operation at 20°C? And, is this the same area that will be maintained at 0°C? If so, then you need to maintain a uniform air flow throughout the space, which eliminates the possibility of of only using one or two coils at 20°C as opposed to three coils at 0°C.

    When the space temperature is 0°C the coil will probably operate with frost on them. During the operation with 20°C the coils will be operating wet. Therefore, you either need to ensure the face velocity of air off of the coils is low enough to prevent water being pulled off of the coils. This could be done with VFD's or by carefully selecting the coils so that operate with low face velocity in either condition.

    Then...you can evaluate the need for control valve modulation, floating set points for temperature control, etc.

    And, just as important is the need to have the refrigeration system designed so that it can operate at both conditions (20­C or 0°C) with the most efficient mode to deliver the lowest operating cost.

    It's not impossible...it just takes some work and careful review.
    If all else fails, ask for help.


  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: 0C Coldroom Evaporator operating at 20C

    Keep the fans running on all evaporators, but let just one actually working. The total air flow will allow uniform air mixing, but the cooling capacity will just be 1/3.
    Please note that the compressors or condensing unit that is, must be capable of working at 1/3 of design load.

  6. #6
    Join Date
    Jun 2007
    Location
    South Africa
    Posts
    80
    Rep Power
    17

    Re: 0C Coldroom Evaporator operating at 20C

    Hi - thanks for the feedback thus far.

    A point that I forgot to mention. The room is a 0C Coldroom but until they build the reminder of the warehouse (in 3 years time). Until then it needs to operate at 20C.
    (I do have VSD fans)

    any more tips

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: 0C Coldroom Evaporator operating at 20C

    Look at using water cooling through evaps and a dry cooler, you know the wet buld condition, if necessary add a high temp water chiller to suppliment cooling capacity, later on design a chilled glycol system for total duty once at 0'C, don't forget partial defrost on evaps.
    magoo

Similar Threads

  1. new coldroom installation
    By chilltech in forum Fundamentals
    Replies: 8
    Last Post: 23-07-2009, 05:38 PM
  2. Coldroom
    By Ray Ang SM in forum Trouble Shooting
    Replies: 16
    Last Post: 11-06-2008, 08:16 AM
  3. Coldroom
    By Ray Ang SM in forum Technical Speculations
    Replies: 1
    Last Post: 08-06-2008, 04:00 AM
  4. problems with coldroom icing up
    By goody in forum Trouble Shooting
    Replies: 40
    Last Post: 28-03-2008, 07:26 PM
  5. defrost on freezer coldroom
    By andyh in forum Electrical
    Replies: 11
    Last Post: 01-09-2006, 10:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •