Thread: Section Pressure: 105f
-
09-07-2008, 09:10 AM #1
Section Pressure: 105f
Goodman condenser: GSC130241AE LENNOX furnace: g40uh-24a-045-11 LENNOX Coil: 2.5ton outside tem:106f
Section Line Temperature :56f. pressure: 105f
Liquid Line Temperature: 116f Pressure: 275f
S AIR :59F R AIR: 86F
does anyone know what's the problem? is it the TXV TOO BIG? or something else?
-
09-07-2008, 12:40 PM #2
Re: Section Pressure: 105f
Last edited by BigJon3475; 09-07-2008 at 12:43 PM.
-
09-07-2008, 12:55 PM #3
Re: Section Pressure: 105f
Do you mean 105 psig and 275 psig?
For SI users:
Suction: 13.3°C, liquid 46.6°C
Evap.p.: 7.2 bar, cond.p. 19.0 bar
Assuming R22 refrigerant, 105psig is 63F which is impossible given a suction of 56F
-
09-07-2008, 01:09 PM #4
Re: Section Pressure: 105f
If you used the same temp probes for the line sets as you did the return and supply air temps....you maybe have a bad thermometer.