09-07-2008, 02:04 AM #1
question on ventilation rate for a/c system
Dear friends:
My daily work is mostly related to refrigeration but I´ve been asked to perform the preliminary design of an a/c system to be installed in a 185 square meter money receiving/counting/sorting area such as those existing in some large banking/financial institutions. Heat load due to the automatic counting machines accounts to less than 6 Kw. What I´m more insterested in is in learning about the ventilation requirements for the air handling system: should I estimate ventilation air using minimum per person rates or are we talking about a 100% fresh air system due to possible odor/contaminants? Any comments welcomed.
09-07-2008, 05:46 PM #2
Re: question on ventilation rate for a/c system
coldkeeper
I would base the design on 15 percent makeup air that is conditioned thru the air handler.
use a mixed air calculation for your load
A good rootop unit with an economizer section will work well.
100 percent out side is possible for cooling with the economizer section if ambient is ok to use.
Odor control should not be a big issue in the type facility you described.
I would think without knowing the details- 350 to 400 ft2/ton should give a good budget size
Bruceboldy
10-07-2008, 01:48 AM #3
Thank you Bruceboldy for your sound advice. I didn´t think this area qualified as a 100% fresh air application, but wasn´t sure though.
10-07-2008, 07:03 PM #4
12-07-2008, 02:50 AM #5
Good evening 2007eng and thank you very much for your link!!!
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
What is System balance?
By shogun7 in forum Technical SpeculationsReplies: 56Last Post: 19-01-2006, 09:47 AM -
Refrigeration system proposal; comments please.
By DaBit in forum Technical SpeculationsReplies: 13Last Post: 01-01-2003, 03:42 PM -
Automotive A/C Vent Temp Range vs System
By Don Browney in forum Air ConditioningReplies: 1Last Post: 15-05-2002, 06:19 AM -
ventilation for laundry
By watana in forum FundamentalsReplies: 1Last Post: 29-04-2002, 06:03 AM