    Air Cooled Condenser Leakage Problem with R-404A



    Dear sir,
    we have a wonder problem.
    we have prepared the condensing unit with air cooled conderser.
    Data: Compressor- Semi-hermatic
    Conderser- 4 Row -4 fans(sucking type)
    comperssor Oil- Fuchs SE-55 Polyster oil.
    Gas -R-404A
    We provide Liquid line filter,
    Suction line Filter.
    Suction Accumaltor
    Oil separator.
    Design Parameters : (-30'C) Evap. temp.
    Condesing temp. -(+45'C)
    Cold room temp- (-25'C)

    Since last six months we have problem with condenser. condenser leak at bottom row at liquid header side inside the fins.
    During this period the condenser leak 7 times. we have replaced the condenser twice.During lekage we found the dischar pressure was 270-310 psig only.
    and suction pressure- 18 Psig. Oi pressure-105 Psig.
    The condenser tube guage is 26.

    The palnt is working smoothly but within the month the condenser fails.
    whenever the cond. fails we replaced the filters ,oil and charged the New Gas. (too much expansive)
    Pl. give some suugestion so that we can slove the problem.



  2. #2
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Quote Originally Posted by RADHAKRISHNARAO View Post
    ...Pl. give some suugestion so that we can slove the problem.
    Congratulations you are one of the few that gives a lot of information in your post.

    Unfortunately for you, all you give is IRRELEVANT!

    If the system is working smoothly and you change filters and I suppose you don't have acid or corrosion fro inside then the things that cause this are (in general):

    Thermal stress usually residual stress due to solder malpractice.

    Mechanical stress this could be it, check the base of the condenser is leveled and you don't have a bump in the middle.

    Corrosion. There are several types of corrosion electrolytical could be the most common in this case but you must have water, an electrolyte like salt or any other dissolved in water and two different metals like copper and aluminium.

    Other type of corrosion is caused by using cleaning materials in the floor or around the area of the condenser that contains for example ammonia? Even if you have smell of NH3 in the air it could affect.
    In the case of corrosion you should take a sample of the failed material and look at it under a microscope or take it to an expert. It's very easy to tell.

    Vibration is also a possible cause. In combination with residual thermal stress it can byte you in the ...

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Very interesting phenomena,
    I like that kind of problems.

    If its inside the finned area, where about? between the Finns? or at the inside of the frame?

    Are the Finns end under the lowest rows or just at the bottom of that pipe?

    how long doe's the condenser frame is below the pipes?

    Doe's the pipe leak at some soldered point or lengths wise?

    doe's the condenser has a "bottom" steel sheet underneath the finns?

    What doe's the condenser manufacturer says abut it?

  4. #4
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Air Cooled Condenser Leakage Problem with R-404A

    how are the fans controlled ? are they on fan speed controlers or pressure sensors? i can only think that the head pressure is getting to high before the fans are dropping it causing alot of expansion/contraction and movement weakening the coil ends, it does not take alot with the newer thiner wall copper coils, we fitted one this week where the test pressure was only 400 psi!!

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Since last six months we have problem with condenser. condenser leak at bottom row at liquid header side inside the fins.
    During this period the condenser leak 7 times. we have replaced the condenser twice.
    Sounds like your getting faulty condenser coils ? Are they coming pressurised / pressure tested as 7 leaks on a condenser in six months is ridiculus. You need to buy a decent condenser coil as it seems the ones you are buying are leaking like a sieve.
    Transvestites are men who like to eat, drink, and be Mary.

  6. #6
    Join Date
    Feb 2004
    Location
    USA
    Posts
    136
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Is the header fan running continuosly or cycling on and off on pressure? Almost all manufacturers nowadays specify that the header fan be on when the refrigeration is running to prevent thermal stressing of the headers.

  7. #7
    Join Date
    May 2007
    Location
    India
    Posts
    695
    Rep Power
    17

    Re: Air Cooled Condenser Leakage Problem with R-404A

    There is also a possibility of SEBEC effect taking place. Due to dissimilar metal joints & with temp difference, the current causes this type of typical isses. YOu need to check the earthing of the system We had faced similar issue & after struggling many times, we could set it right after proper Earthing. So may be that is the problem.

  8. #8
    Join Date
    Jun 2008
    Location
    india
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Thanks sir
    the leakage at bottom row which line is entered in the liquid header side between the frame and fins and not at joints but a blow hole in straight pipe.lenghts wise The condenser has G.I sheet at bottom.
    The conenser manufacture has told that the 27 guage pipe is suitable for R-404a gas. and they have no idea. there are also warried about this.

    we have checked the oil at lab. but it has no such kind of acid particles the PH shows 6.7.

    as per your que. the length of pipe below from the pipe is 10".


    Quote Originally Posted by chemi-cool View Post
    Very interesting phenomena,
    I like that kind of problems.

    If its inside the finned area, where about? between the Finns? or at the inside of the frame?

    Are the Finns end under the lowest rows or just at the bottom of that pipe?

    how long doe's the condenser frame is below the pipes?

    Doe's the pipe leak at some soldered point or lengths wise?

    doe's the condenser has a "bottom" steel sheet underneath the finns?

    What doe's the condenser manufacturer says abut it?

  9. #9
    Join Date
    Jun 2008
    Location
    india
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Thanks sir,

    There is no vibration in unit.
    we are checked the oil at lab. the results are normal the oil PH is 6.7 only.

    And there is no Ammonia smell. near the plant.




    Quote Originally Posted by GXMPLX View Post
    Congratulations you are one of the few that gives a lot of information in your post.

    Unfortunately for you, all you give is IRRELEVANT!

    If the system is working smoothly and you change filters and I suppose you don't have acid or corrosion fro inside then the things that cause this are (in general):

    Thermal stress usually residual stress due to solder malpractice.

    Mechanical stress this could be it, check the base of the condenser is leveled and you don't have a bump in the middle.

    Corrosion. There are several types of corrosion electrolytical could be the most common in this case but you must have water, an electrolyte like salt or any other dissolved in water and two different metals like copper and aluminium.

    Other type of corrosion is caused by using cleaning materials in the floor or around the area of the condenser that contains for example ammonia? Even if you have smell of NH3 in the air it could affect.
    In the case of corrosion you should take a sample of the failed material and look at it under a microscope or take it to an expert. It's very easy to tell.

    Vibration is also a possible cause. In combination with residual thermal stress it can byte you in the ...

  10. #10
    Join Date
    Jun 2008
    Location
    india
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Thanks sir
    the leakage at bottom row which line is entered in the liquid header side between the frame and fins and not at joints but a blow hole in straight pipe.lenghts wise The condenser has G.I sheet at bottom.
    The conenser manufacture has told that the 27 guage pipe is suitable for R-404a gas. and they have no idea. there are also warried about this.

    we have checked the oil at lab. but it has no such kind of acid particles the PH shows 6.7.

    as per your que. the length of pipe below from the pipe is 10".

  11. #11
    Join Date
    Jun 2008
    Location
    india
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Thanks sir,

    There is no vibration in unit.
    we are checked the oil at lab. the results are normal the oil PH is 6.7 only.

    And there is no Ammonia smell. near the plant.

  12. #12
    Join Date
    Jun 2008
    Location
    india
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Thanks,
    We have done proper earthing in plant . the earth shows between natural and earth is 0.00.

  13. #13
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Quote Originally Posted by smpsmp45 View Post
    There is also a possibility of SEBEC effect taking place. Due to dissimilar metal joints & with temp difference, the current causes this type of typical isses. YOu need to check the earthing of the system We had faced similar issue & after struggling many times, we could set it right after proper Earthing. So may be that is the problem.
    I would rate this as "most probable".
    Please check for galvanic bonding between copper and zinc-coated frame. If so, either remove the bonding, or change the electric potential of the assembly.

  14. #14
    Join Date
    Jul 2008
    Location
    FRANCE
    Age
    49
    Posts
    5
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Quote Originally Posted by RADHAKRISHNARAO View Post
    Dear sir,
    we have a wonder problem.
    we have prepared the condensing unit with air cooled conderser.
    Data: Compressor- Semi-hermatic
    Conderser- 4 Row -4 fans(sucking type)
    comperssor Oil- Fuchs SE-55 Polyster oil.
    Gas -R-404A
    We provide Liquid line filter,
    Suction line Filter.
    Suction Accumaltor
    Oil separator.
    Design Parameters : (-30'C) Evap. temp.
    Condesing temp. -(+45'C)
    Cold room temp- (-25'C)

    Since last six months we have problem with condenser. condenser leak at bottom row at liquid header side inside the fins.
    During this period the condenser leak 7 times. we have replaced the condenser twice.During lekage we found the dischar pressure was 270-310 psig only.
    and suction pressure- 18 Psig. Oi pressure-105 Psig.
    The condenser tube guage is 26.

    The palnt is working smoothly but within the month the condenser fails.
    whenever the cond. fails we replaced the filters ,oil and charged the New Gas. (too much expansive)
    Pl. give some suugestion so that we can slove the problem.


    105psig -18psig=87psig(fault) it's not good the dif it's entre 30psig to 45psig ( 18psig+45psig it's good for oil pressure) that you are a more quantity of oil in your installation you must find manufacture informations for a juste volum of oil and a type ester huile big sensibelity to!!!wate=acide?,semi-hermitic is very complicate if silencieux in decharge of compresseur .

  15. #15
    Join Date
    Jul 2008
    Location
    FRANCE
    Age
    49
    Posts
    5
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Quote Originally Posted by sinx712 View Post
    105psig -18psig=87psig(fault) it's not good the dif it's entre 30psig to 45psig ( 18psig+45psig it's good for oil pressure) that you are a more quantity of oil in your installation you must find manufacture informations for a juste volum of oil and a type ester huile big sensibelity to!!!wate=acide?,semi-hermitic is very complicate if silencieux in decharge of compresseur not user in this installation .
    the cause of your probleme is the oil,your condenseur is big, if is not big your compressor is domag, compressor pumping the liquid not gas.

  16. #16
    Join Date
    Apr 2008
    Location
    India
    Age
    52
    Posts
    6
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Dear Radha,

    Please check if your CDU is located in corrosive environment i.e. Is there ammonia in environment ( this could be due to presence of a sewage canal, industrial etc )

    Please get back on this . I have faced similar prob five years back in a window AC. The reason was presence of a sewage disposal nullah in viscinity.

    Best of luck

    Anuraag Panchal

  17. #17
    Join Date
    Jun 2008
    Location
    india
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Thanks,
    There Is No Swage Line Near The Plant. The Plant Is In Open Air Only.
    And No Chemical Factory Near This Plant.

  18. #18
    Join Date
    Jun 2008
    Location
    india
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Quote Originally Posted by chemi-cool View Post
    Very interesting phenomena,
    I like that kind of problems.

    If its inside the finned area, where about? between the Finns? or at the inside of the frame?

    Are the Finns end under the lowest rows or just at the bottom of that pipe?

    how long doe's the condenser frame is below the pipes?

    Doe's the pipe leak at some soldered point or lengths wise?

    doe's the condenser has a "bottom" steel sheet underneath the finns?

    What doe's the condenser manufacturer says abut it?


    I WILL ATTACH THE PHOTO FOR YOUR KNOWLEDGE.
    Attached Images Attached Images

  19. #19
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    331
    Rep Power
    17

    Re: Air Cooled Condenser Leakage Problem with R-404A

    You state that for the past six months you've had leaks. What about before that? Did the unit run fine for years? History can be very important when solving problems.

    Next, if you are replacing the condensers with BOCK factory coils, it's time to get them involved. Have them come to the job site or send the leaking coils to them for inspection.

  20. #20
    Join Date
    Jun 2008
    Location
    india
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: Air Cooled Condenser Leakage Problem with R-404A

    Dear sir,
    This is a new unit only, we have commissioned in Nov.07. we could not get any solution from old condenser. In unit we have replaced the condenser twice and 4 times we brazed the leakage.

Similar Threads

  1. water cooled ice making machine problem
    By racktech2008 in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 22-03-2008, 04:21 PM
  2. method to design air cooled condenser
    By abbasi in forum New Technologies
    Replies: 4
    Last Post: 12-02-2008, 09:34 AM
  3. Carrier Air Cooled Condenser
    By Brads in forum Commercial
    Replies: 0
    Last Post: 03-12-2007, 01:26 PM
  4. Making a simple water cooled condenser
    By The MG Pony in forum Fundamentals
    Replies: 19
    Last Post: 01-08-2007, 11:02 AM
  5. air cooled condenser design
    By abbasi in forum Fundamentals
    Replies: 1
    Last Post: 26-03-2005, 09:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •