Thread: frick slidevalve
-
07-07-2008, 02:19 PM #1
frick slidevalve
hi, I have an account with an RXF85E compressor that the slidevalve takes about 30 minutes to fully load up after a shut down. I have not seen this before in other units, and this one has been doing this for a couple of months and getting a little worse as time goes by. The oil pressure drops a little with higher discharge pressures due to higher ambiants, but does not seem to effect this situation. Any help is appreciated.
-
07-07-2008, 02:58 PM #2
Re: frick slidevalve
Have you checked to see if the solenoid valve is opening? Sounds like it might have some trash or something obstructing it.
-
07-07-2008, 07:53 PM #3
Re: Frick slide valve
Hi ridekc
My first question is when was this compressor last serviced.
IE tired old oil and an old filter my be all that is wrong.
On the other hand NH3 wizard may have a point.
Below is attachments with a maintenance schedule to refer to.
Also lists of possible causes to your dilemma!
Cheers Grizzly
-
07-07-2008, 07:56 PM #4
-
08-07-2008, 06:44 AM #5
Re: frick slidevalve
Either a solenoid valve issue or the glide ring is passing. Due to the op dropping while loading, I would pull the slide assembly and replace the glide ring, check valve etc. The parts are pretty cheap and its an easy project.
How many hours are on the comp?
-
11-07-2008, 11:57 PM #6
Re: frick slidevalve
If sounds like oil is not getting to the loading piston. There is sometimes a needle valve the regulates the flow rate of oil to the loading piston, I assume you have already checked this. It very much sounds like the 4 way loading valve is not passing oil through it. I would take the 4 way valve off and bench test it with compressed air to determine if it is working correctly.
-
12-07-2008, 09:56 AM #7
Re: frick slidevalve
hi ridekc,
you need to analyze sectionally. as the other guys mentioned, do some inspection (or probable stripping the assy. with kits on hand just incase)in the capacity valve block esp. on the valve seats ang in-line stainers. else you need to check the capacity slide piston. check also your oil cooling if it's on right temp.
is this comp. undergo service / overhauling sometime ago?
-
13-07-2008, 02:45 AM #8
-
17-07-2008, 03:06 PM #9
Re: frick slidevalve
Sorry for the delay, lots of stuff going on. I found the frick manual for this unit & has the rxf plus micro controller. I did more inspection, and opened the needle valve alittle, and isresponding better. The valve is getting energized. There is about 8,000 hrs on this machine and will be serviced soon. I will check slide assembly at that time. The unit is staying online and not causing trouble for now. Thanks for the useful info and links. I will use them.
-
27-07-2008, 09:44 AM #10
Re: frick slidevalve
Your slide valve seals need
replacing. Pressure from the discharge side is causing the slide valve to load.
This can be done with out stripping the complete compressor.
-
12-09-2008, 10:10 PM #11
Re: frick slidevalve
Please Grizzly, can you send literature Frick RXF85E compressor? Please.
Thank you
rvt@ono.com
Similar Threads
-
Frick compressor RXF 101-H
By PaulZ in forum Industrial CompressorsReplies: 11Last Post: 19-02-2009, 02:29 AM -
Ammonia Circulation rate - by Frick/ Vitler
By smpsmp45 in forum NH3Replies: 12Last Post: 16-06-2008, 10:06 AM -
Frick Quantum Panel
By LEE40 in forum Trouble ShootingReplies: 4Last Post: 27-03-2008, 05:24 PM -
old frick system monitor
By rasgrant in forum NH3Replies: 5Last Post: 17-01-2007, 06:15 PM