    CO2 storage tanks
    One of our customers is looking for Ref system to condense the CO2 gas stored in the tanks. ( like Horton Spheres for Ammonia). Has any one done a similar project?
    Sep 2006
    Mindanao, Phils.
    257
    Re: CO2 storage tanks
    One of our customer used bare pipe as evaporator installed inside the CO2 tank coupled with a 30HP compressor and an air cooled condensing unit.
    winfred
    Pls. Remember K.I.S.S.
    Keep It Simple, . . . . . .
    Aug 2005
    5,302
    The tanks I have worked on were somewhat small. The tanks have an evaporator installed in the tank to condense the CO2 at a certain temperature. This helps to control or limit the pressure in the CO2 tank (to keep CO2 relief valves from opening).
    The compressors for these were 5 HP Copeland I think, but the principle is the same on any scale.
    In ammonia storage tanks they simply compress and liquefy the ammonia without heat exchangers in the tank. However, with the pressures of CO2 the heat exchanger is probably the easiest way to do this.
    India
    688
    What type of system is that. Is the coil submerged in the co2 tank?
    Aug 2005
    5,302
    I don't remember who made the CO2 tank. It was owned by the company supplying the gas and rented to the customer.
    The evaporator was above the liquid (in the gas space). As the vapor formed from the boiling (due to heat absorption) the evaporator was simply maintained at a temperature low enough to condense the CO2 so that the pressure was maintained below the relief valve setting.
    Rather simple actually.
    Oct 2006
    1,843
    21
    I have worked on what sound like similar storage tanks aswell.
    I remember that the evap was a coil inside the tank made from steel and then it was just a normal direct expansion system with the copland comp on the side in a weather houseing (as the Iceman stated).
    Very simple in design and construction. The ones I worked at were at BOC (British oxygen company)
    but I dont recall who made the tanks.
    taz.
    Sep 2003
    ISRAEL
    72
    4,248
    I maintain these monsters for years, Tomco is one of the biggest manufaturers.
    Evaporator is made from bare pipes inside the tanks, Copeland condensing units up to 15 Hp.
    Sep 2006
    Mindanao, Phils.
    257
    Quote Originally Posted by smpsmp45 View Post
    Refrigeration is just the simple DX system, Compressor, Aircooled Condenser, Liquid Receiver, TXV, Bare Pipe Evaporator.
    Bare Pipe Evaporator entering the tank, looping inside and coming back where it enters the tank before connecting to the Air cooled Condensing Unit.
    winfred
  1. water cooling storage system
    Last Post: 28-05-2008, 11:02 PM
  2. ice storage issue
    Last Post: 04-05-2008, 10:38 PM
  3. No. of temperature sensors required in cold storage?
    By dipankarmohanty in forum Technical Speculations
    Last Post: 14-03-2008, 07:45 AM
  4. Sizing a Vegetable/Fruit Cold Storage
    By Samarjit Sen in forum Industrial
    Last Post: 07-05-2007, 10:58 AM
  5. Energy management contract issue
    Last Post: 30-03-2006, 03:01 PM