    How to cool the water from 48 deg. C to 16 deg. C?



    Hi,

    Could someone tell me how I can cool the water from 48 deg. C to 16 deg. C?

    I want to use a BAC cooling tower to cool the water from 48 deg. C to 27 deg. C (wet bulb 22 deg. C). Then I'd like to use York air-cooled chiller to cool the water from 27 deg. C to 16 deg. C... How can achieve such a big delta T? Mixing? Does the ***** chiller manage the water of 27 deg. C (or after mixing 27 deg. C)?

    Many thanks in advance for your help.

    Regards from Poland.

    Jacek



  2. #2
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: How to cool the water from 48 deg. C to 16 deg. C?

    Is the water being recirculated? At what temp it is coming back? One important aspect is that since you are passing the water thru cooling tower, it can not be used in a chiller or for process due to contamiations etc.

    In case the water is being recirculated, the aspects are different. If you can specify the flow rates & return temp I can suggest a system

  3. #3
    Join Date
    Jun 2002
    Location
    Mumbai, India
    Age
    66
    Posts
    25
    Rep Power
    0

    Re: How to cool the water from 48 deg. C to 16 deg. C?

    Hi,
    Regardless of your application, you can get such a high delta T in a Plate Heat Exchanger. The only other alternative - though not very practical - is to use a number of shell and tube heat exchangers in series.

  4. #4
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: How to cool the water from 48 deg. C to 16 deg. C?

    Yes you can use BPHE but large delta in the water side is not energy efficient.

    I'd rather use two.

    Yes you can use ***** but do not under size the first evap in order not to overload the compressor. Instead use a suction (crankcase) pressure regulator.

  5. #5
    Join Date
    Jun 2007
    Location
    hants
    Age
    63
    Posts
    6
    Rep Power
    0

    Re: How to cool the water from 48 deg. C to 16 deg. C?

    Jacek,
    One problem with the York chiller is that the comp's are probably semi - hermetic. Normally the highest allowed leaving water temp is 10 deg. This is to ensure you get motor cooling. I have used them at 14 deg with problem but in a low ambient enviroment. To get from 27 - 16 deg hot and cold tank method the best. you a primary and secondary pump circuit.

  6. #6
    Join Date
    Jun 2007
    Location
    hants
    Age
    63
    Posts
    6
    Rep Power
    0

    Re: How to cool the water from 48 deg. C to 16 deg. C?

    Jacek, Ignore the first post had a keyboard problem.
    One problem with the York chiller is that the comp's are probably semi - hermetic. Normally the highest allowed leaving water temp is 10 deg. This is to ensure you get motor cooling. I have used them at 14 deg with no problem but in a low ambient enviroment. To get from 27 - 16 deg the best method would be a hot and cold tank system with a primary and secondary pump circuit. Very popular on injection moulding and bottling plants using conventional chillers.

  7. #7
    Join Date
    Jul 2005
    Location
    SOMEWHERE IN THE PLANET
    Age
    46
    Posts
    67
    Rep Power
    19

    Re: How to cool the water from 48 deg. C to 16 deg. C?

    If the water is circulated. Use BAC is good idea, the energy will be saved compared to using a chiller. I don't think it is a problem to cool the water from 27C to 16 C. It is only non standard evaporator.

  8. #8
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: How to cool the water from 48 deg. C to 16 deg. C?

    You may also consider placing an air cooled heat exchanger ahead of the cooling tower to remove a substantial amount of the high quality heat. Tower would be smaller and evaporation losses less.

    You should investigate putting the waste heat to good use elsewhere if possible.

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 06:19 PM
  3. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  4. Condenser water causing corrosion
    By 750 Valve in forum Technical Discussions
    Replies: 7
    Last Post: 28-05-2008, 10:21 AM
  5. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •