05-07-2008, 10:35 AM #1
how the split unit consume less energy then a window type unit
hi every one
i came to know that split unit consume less energy then a window type AC boths are having same capcity
please give some solid reason
thanks a lot
jahangir ahmad khan
lahore pakistan
More doors are opened with 'Please'then with keys (Hitler)
-
05-07-2008, 11:16 AM #2
Re: how the split unit consume less energy then a window type unit
Window rattlers are built down to both size and price.
Modern splits has various technologies, like inverters, built in to them just to increase their energy efficiency.
Generally, the split would also have larger coils.
-
05-07-2008, 11:25 AM #3
Re: how the split unit consume less energy then a window type unit
Hi,
Window air conditioner of 1.0 TR capacity with rotary compressor draws 1100watts while hi wall split unit of 1.0 TR capacity draws 1220 watts for two star rated units.
Power consumption of 4star rated units are identical with that of window air conditioner.
Therefore, I believe window air conditioenrs have lower power consumption.
Visit www.bluestarindia.com
ThanksVijay Kumar
HVAC Design Engineer
BMCPL
"The more you sweat in peace less you bleed in war"
-
05-07-2008, 04:59 PM #4
Re: how the split unit consume less energy then a window type unit
Are the capacities really equal? Did you measure them?
-
07-07-2008, 06:11 AM #5
Re: how the split unit consume less energy then a window type unit
hi GXMPLX
no i'm not measure them
but written on the sticker pastae on the out door unit boths are same capcity 18000BTU/hr
in my mind becuse the compressor and condensor in a single box thats why it consume more energy compressor working more.
what u think?????
best regrads
jahangir ahmad khan
lahore pakistanMore doors are opened with 'Please'then with keys (Hitler)
-
08-07-2008, 01:04 PM #6
Re: how the split unit consume less energy then a window type unit
Actually since the compressor, condensor and evap are located in same box, power consumption should be less due to reduced refrigerant piping lengths.
Vijay Kumar
HVAC Design Engineer
BMCPL
"The more you sweat in peace less you bleed in war"
-
08-07-2008, 10:00 PM #7
Re: how the split unit consume less energy then a window type unit
If pipes are proper selected, then the nit will not consume more power. Every VRV/VRf should then be the worst made AC- machine ever and this isn't so.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
14-07-2008, 05:10 PM #8
Re: how the split unit consume less energy then a window type unit
Hmmm before I say anything, I would like the model and manufacturer of each compressor.
I think there you could have efficiency differences that could be larger than pipe losses (unless one system is too far appart).
If they had the same compressor, yes piping and different operating conditions would explain differences unless one of the compressor is worn out.
-
14-07-2008, 07:50 PM #9
Re: how the split unit consume less energy then a window type unit
Window units have smaller fan at the condenser side, the condenser is a bit smaller, condenser is up to 4 rows deep, thats where the differences are
-
14-07-2008, 08:19 PM #10
Re: how the split unit consume less energy then a window type unit
With smaller condenser so should condense worse.
You have higher thermal losses in compact design.
Smaller evap means you evaporate lower.
So you won't see me jump into conclusions too fast!
I think compressor differences could explain more.
But I am not saying you are wrong ... You see even a LADA has been down those roads!
-
17-07-2008, 11:10 AM #11
Re: how the split unit consume less energy then a window type unit
Hi,
The difference would be due to the size of the evaporator and condenser. The size and ratio of these is important in getting the maximum efficiency. This can be acheived easier on a split system. The window/wall unit has a smaller evaporator and a lower evaporating temperature. They also use the same motor to drive both indoor and outdoor fans, so are restricted as to the airflow and head pressure control.
-
20-07-2008, 08:25 AM #12
-
27-07-2009, 11:11 PM #13
Re: how the split unit consume less energy then a window type unit
or is the difference is that the window rattler has only one fan motor?
-
27-07-2009, 11:53 PM #14
Re: how the split unit consume less energy then a window type unit
Window shakers have evolved along with everything else. If the energy consumption is not currently competitive, it eventually will be. And along with the lower price they will have the huge advantage of being easy to install.
Last edited by Gary; 27-07-2009 at 11:57 PM.
Similar Threads
-
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Installing pipework for single split unit
By electro in forum Air ConditioningReplies: 51Last Post: 05-03-2009, 07:02 PM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 08:23 PM -
TK basic micro-p features and functions
By REEFER-TEK in forum TransportReplies: 0Last Post: 05-12-2007, 07:25 PM -
carrier split unit R22
By airconadam in forum Air ConditioningReplies: 24Last Post: 07-11-2007, 12:22 AM