    how the split unit consume less energy then a window type unit



    hi every one

    i came to know that split unit consume less energy then a window type AC boths are having same capcity

    please give some solid reason

    thanks a lot

    jahangir ahmad khan

    lahore pakistan


    More doors are opened with 'Please'then with keys (Hitler)

  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: how the split unit consume less energy then a window type unit

    Window rattlers are built down to both size and price.

    Modern splits has various technologies, like inverters, built in to them just to increase their energy efficiency.

    Generally, the split would also have larger coils.

  3. #3
    Join Date
    Feb 2006
    Location
    Mumbai
    Posts
    49
    Rep Power
    0

    Re: how the split unit consume less energy then a window type unit

    Hi,

    Window air conditioner of 1.0 TR capacity with rotary compressor draws 1100watts while hi wall split unit of 1.0 TR capacity draws 1220 watts for two star rated units.

    Power consumption of 4star rated units are identical with that of window air conditioner.

    Therefore, I believe window air conditioenrs have lower power consumption.

    Visit www.bluestarindia.com

    Thanks
    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

  4. #4
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: how the split unit consume less energy then a window type unit

    Are the capacities really equal? Did you measure them?

  5. #5
    Join Date
    Feb 2008
    Location
    PAKISTAN
    Age
    36
    Posts
    62
    Rep Power
    17

    Re: how the split unit consume less energy then a window type unit

    hi GXMPLX


    no i'm not measure them
    but written on the sticker pastae on the out door unit boths are same capcity 18000BTU/hr

    in my mind becuse the compressor and condensor in a single box thats why it consume more energy compressor working more.
    what u think?????

    best regrads

    jahangir ahmad khan
    lahore pakistan
    More doors are opened with 'Please'then with keys (Hitler)

  6. #6
    Join Date
    Feb 2006
    Location
    Mumbai
    Posts
    49
    Rep Power
    0

    Re: how the split unit consume less energy then a window type unit

    Actually since the compressor, condensor and evap are located in same box, power consumption should be less due to reduced refrigerant piping lengths.
    Vijay Kumar
    HVAC Design Engineer

    BMCPL

    "The more you sweat in peace less you bleed in war"

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: how the split unit consume less energy then a window type unit

    If pipes are proper selected, then the nit will not consume more power. Every VRV/VRf should then be the worst made AC- machine ever and this isn't so.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: how the split unit consume less energy then a window type unit

    Hmmm before I say anything, I would like the model and manufacturer of each compressor.

    I think there you could have efficiency differences that could be larger than pipe losses (unless one system is too far appart).

    If they had the same compressor, yes piping and different operating conditions would explain differences unless one of the compressor is worn out.

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: how the split unit consume less energy then a window type unit

    Window units have smaller fan at the condenser side, the condenser is a bit smaller, condenser is up to 4 rows deep, thats where the differences are

  10. #10
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    349
    Rep Power
    16

    Re: how the split unit consume less energy then a window type unit

    Quote Originally Posted by chemi-cool View Post
    Window units have smaller fan at the condenser side, the condenser is a bit smaller, condenser is up to 4 rows deep, thats where the differences are
    With smaller condenser so should condense worse.

    You have higher thermal losses in compact design.

    Smaller evap means you evaporate lower.

    So you won't see me jump into conclusions too fast!

    I think compressor differences could explain more.

    But I am not saying you are wrong ... You see even a LADA has been down those roads!

  11. #11
    Join Date
    Jul 2007
    Location
    UK
    Posts
    6
    Rep Power
    0

    Re: how the split unit consume less energy then a window type unit

    Hi,

    The difference would be due to the size of the evaporator and condenser. The size and ratio of these is important in getting the maximum efficiency. This can be acheived easier on a split system. The window/wall unit has a smaller evaporator and a lower evaporating temperature. They also use the same motor to drive both indoor and outdoor fans, so are restricted as to the airflow and head pressure control.

  12. #12
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: how the split unit consume less energy then a window type unit

    Quote Originally Posted by vijay_study View Post
    Actually since the compressor, condensor and evap are located in same box, power consumption should be less due to reduced refrigerant piping lengths.
    also the last window unit i purchased also had the liquad line looped thru the evaporator condensate tray adding more subcooling surely that would help to make it even more efficient

  13. #13
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: how the split unit consume less energy then a window type unit

    or is the difference is that the window rattler has only one fan motor?

  14. #14
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: how the split unit consume less energy then a window type unit

    Window shakers have evolved along with everything else. If the energy consumption is not currently competitive, it eventually will be. And along with the lower price they will have the huge advantage of being easy to install.
    Last edited by Gary; 27-07-2009 at 11:57 PM.

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Installing pipework for single split unit
    By electro in forum Air Conditioning
    Replies: 51
    Last Post: 05-03-2009, 07:02 PM
  3. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 08:23 PM
  4. TK basic micro-p features and functions
    By REEFER-TEK in forum Transport
    Replies: 0
    Last Post: 05-12-2007, 07:25 PM
  5. carrier split unit R22
    By airconadam in forum Air Conditioning
    Replies: 24
    Last Post: 07-11-2007, 12:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •