    Charging as a liquid or a gas



    Hey folks is there any documents detailing whether to charge as a gas or a liquid

    Can R59 be charged both forms

    Thanks in advance



  2. #2
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Charging as a liquid or a gas

    Charge everything as a liquid - then you can't go wrong!
    Tony

  3. #3
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Charging as a liquid or a gas

    Quote Originally Posted by hammy View Post
    ... Can R59 be charged both forms
    Never heard of R59. Are you sure this is the correct name?

    Tony is right though, you can always charge in liquid phase but be careful to evaporate the liquid if you are charging to the low side, unless you do it in reasonable amounts and have a suction accumulator in between.

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Charging as a liquid or a gas

    Hi Hammy,

    R59/R417A needs to be charged as a liquid.

    Have a look here

    http://refrigerants.dupont.com/Suva/.../isceon59.html

    Jon

  5. #5
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Charging as a liquid or a gas

    Thanks! so R59 is indeed a wrong name!

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Charging as a liquid or a gas

    High glide refrigerant blends such as HFC R407C, HCFC R409A and other zeotropic
    refrigerant blends (to a lesser extent HFC R410A and HFC R507) fractionate during
    transfers of the blends from one container (e.g., tank or cylinder) to another
    causing the composition of the blend to change. This change in composition can
    make the product off specification, change it's performance and/or make the material hazardous.

    All of the R4 series need to be charged as a liquid to stop this happening.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Charging as a liquid or a gas

    ... or charge full containers!

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Charging as a liquid or a gas

    Quote Originally Posted by GXMPLX View Post
    ... or charge full containers!
    Will only work if the entire cylinder is being used; otherwise use liquid charging as stated by others.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Feb 2001
    Location
    Doncaster, England
    Posts
    199
    Rep Power
    25

    Re: Charging as a liquid or a gas

    High glide refrigerant blends such as HFC R407C, HCFC R409A and other zeotropic
    refrigerant blends (to a lesser extent HFC R410A and HFC R507) fractionate during
    transfers of the blends from one container (e.g., tank or cylinder) to another
    causing the composition of the blend to change.
    Marc - R507 is an azeotrope not a zeotrope and therefore can be charged as a gas without fractionating (if thats a word)
    Tony

  10. #10
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Charging as a liquid or a gas

    Quote Originally Posted by Tony View Post
    Marc - R507 is an azeotrope not a zeotrope and therefore can be charged as a gas without fractionating (if thats a word)
    Wow it took me long to see this!

    R507a is only a NEAR azeotrope like all the 500 family.

    Glide is about 0.04C you COULD change composition if charging near 25C.

    But I agree you normally get by this, like we always did with R502 ... or was it luck?

  11. #11
    Join Date
    Aug 2006
    Location
    England
    Posts
    50
    Rep Power
    18

    Re: Charging as a liquid or a gas

    The best advice is;-

    If the refrigerant begins with a capital R it is ASHRAE approved.
    Then if the first number after the R is a 4, 5 or 6 it's a blend and should be liquid charged.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Liquid charging through the suction side
    By deu58 in forum Fundamentals
    Replies: 13
    Last Post: 02-07-2010, 05:23 AM
  3. Charging liquid through suction line?
    By SloFuse in forum Trouble Shooting
    Replies: 15
    Last Post: 20-06-2010, 09:26 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •