    evaporator leaving temp too high in trane centravac chiller with 1350 tons capacity



    need help... what the main cause if the evaporator leaving temp very high? what is the effect to compressor winding ?

    what will i do to ,maintain the evap temp?



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    Quote Originally Posted by chillout_rg View Post
    need help... what the main cause if the evaporator leaving temp very high? what is the effect to compressor winding ?

    what will i do to ,maintain the evap temp?
    Why is the temperature too high? Is the sensor out of range is entering water also too high?

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    low refrigerant, fouled evaporator tubes, low water flow, loading vanes out of calibration(positive pressure relay) or pneumatic motor defective bad sensors, defective thermostats etc.

  4. #4
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    You need to give more info. Water temps in and out of cond and evap, pressures, amps, fla, refrigerant temps, etc. Could be anyones guess at this point with what litlle you've info given.
    Quote Originally Posted by chillout_rg View Post
    need help... what the main cause if the evaporator leaving temp very high? what is the effect to compressor winding ?

    what will i do to ,maintain the evap temp?

  5. #5
    Join Date
    Jul 2008
    Location
    philippines
    Posts
    7
    Rep Power
    0

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    Quote Originally Posted by chillout_rg View Post
    need help... what the main cause if the evaporator leaving temp very high? what is the effect to compressor winding ?

    what will i do to ,maintain the evap temp?
    thank you for responding.. yes sir how will imaintain the ideal and setpoint of the evaporator leaving temp... tnx..

  6. #6
    Join Date
    Jul 2008
    Location
    philippines
    Posts
    7
    Rep Power
    0

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    how will i cool down the compressor winding temp? what are the possible causes of approaching to high temp of compressor winding?

  7. #7
    Join Date
    Jul 2008
    Location
    philippines
    Posts
    7
    Rep Power
    0

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    Quote Originally Posted by Lowrider View Post
    Why is the temperature too high? Is the sensor out of range is entering water also too high?
    Quote Originally Posted by absrbrtek View Post
    You need to give more info. Water temps in and out of cond and evap, pressures, amps, fla, refrigerant temps, etc. Could be anyones guess at this point with what litlle you've info given.
    active CHW set point (40-45F): 41 - 46 F
    temp enter in evaporator ( 54-56F):48F
    temp leaving evaporator (40-45F) : 44F
    Temp enter condenser (max86F): 80 F
    temp leaving condenser(max 95F) : 86 F

    evap enter pressure : 80 psi
    evap leaving pres. : 63 psi
    condenser enter pres. : 32 psi
    condenser leaving pres. :16
    evop refrigerant temp : 92.8F
    condenser refrigerant temp : 40.4
    evap approch : 0.6
    cond approch : 7.4
    refrigerant type : R123

    the evap leaving temp too high? does it affect the compressor winding temp?
    what adjustment will needed to maintain the evap keaving temp to 41F ?

  8. #8
    Join Date
    Jul 2008
    Location
    philippines
    Posts
    7
    Rep Power
    0

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    what is the differantial oil pressure? discharge oil presssure? what is the main function and importance ?

  9. #9
    Join Date
    Jul 2008
    Location
    philippines
    Posts
    7
    Rep Power
    0

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    Quote Originally Posted by chillout_rg View Post
    active CHW set point (40-45F): 41 - 46 F
    temp enter in evaporator ( 54-56F):48F
    temp leaving evaporator (40-45F) : 44F
    Temp enter condenser (max86F): 80 F
    temp leaving condenser(max 95F) : 86 F

    evap enter pressure : 80 psi
    evap leaving pres. : 63 psi
    condenser enter pres. : 32 psi
    condenser leaving pres. :16
    evop refrigerant temp : 92.8F
    condenser refrigerant temp : 40.4
    evap approch : 0.6
    cond approch : 7.4
    refrigerant type : R123

    the evap leaving temp too high? does it affect the compressor winding temp?
    what adjustment will needed to maintain the evap keaving temp to 41F ?
    Quote Originally Posted by chillout_rg View Post
    what is the differantial oil pressure? discharge oil presssure? what is the main function and importance ?
    when is the time to charge refrigerant? how will i know if the refrigerant need to charge? what are the proper procedure og charging refrigerant?

    what are the main causes of forming acids i the system? how will i prevent that acids ? what is the effect in the system of having acids?

  10. #10
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    Quote Originally Posted by chillout_rg View Post
    active CHW set point (40-45F): 41 - 46 F ((4.44 dgr C))
    temp enter in evaporator ( 54-56F):48F ((8.88 dgr C))
    temp leaving evaporator (40-45F) : 44F ((6.66 dgr C))
    Temp enter condenser (max86F): 80 F ((26.6 dgr C))
    temp leaving condenser(max 95F) : 86 F ((30 dgr C))

    evap enter pressure : 80 psi ((5.51 bar))(chw?)
    evap leaving pres. : 63 psi ((4,34 bar))(chw?)
    condenser enter pres. : 32 psi ((2.2 bar))(cw?)
    condenser leaving pres. :16 ((1.1 bar))(cw?)
    evop refrigerant temp : 92.8F ((33.7 dgr C))
    condenser refrigerant temp : 40.4 ((4.66 dgr C)
    evap approch : 0.6
    cond approch : 7.4
    refrigerant type : R123

    the evap leaving temp too high? does it affect the compressor winding temp?
    what adjustment will needed to maintain the evap keaving temp to 41F ?
    I've added the temperatures and pressures in metric system.Doesn't something strike you as odd, or did you miss type?

  11. #11
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    The pressures you mention are the waterpressure? What we need is the refridgerant pressures!

  12. #12
    Join Date
    Feb 2004
    Location
    USA
    Posts
    132
    Rep Power
    0

    Re: evaporator leaving temp too high in trane centravac chiller with 1350 tons capaci

    7.4F approach is high on the condenser. I have CVHF's running under 2F approaches at full load. When was the last time the tubes were cleaned? When was the last time the strainers were cleaned? .6F for an evap approach is about normal.

    What model chiller is it?
    Seems like pretty high pressure drops across the barrels. Are the gauges accurate?
    What is the average 30 day pumpout rate?