    heat exchanger between subcooling and superheat line



    Does anyone use heat exchanger between subcooling line and superheat line? It works or not? I remember there is a discussion post about this in forum. But I couldnt find it now. Thanks.

    David



  2. #2
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: heat exchanger between subcooling and superheat line


  3. #3
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: heat exchanger between subcooling and superheat line

    Quote Originally Posted by SteinarN View Post
    TKS SteinarN, great post!

    You should add to it a discussion on useful and not useful superheat, because of the possitive effect a SG/LL HE would have to reduce energy loss in a suction line that can't improve insulation like the ones in trenches in old supermarkets.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: heat exchanger between subcooling and superheat line

    It works, but as most people due, irresponsibly increase superheat to increase subcooling as much as they can. This is the best way to have a high efficiency, quickly dying, compressor. It will suck rarefied, superheated vapour at high temperature, and the motor will soon burn.

  5. #5
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: heat exchanger between subcooling and superheat line

    Quote Originally Posted by NoNickName View Post
    It works, but as most people due, irresponsibly increase superheat to increase subcooling as much as they can. This is the best way to have a high efficiency, quickly dying, compressor. It will suck rarefied, superheated vapour at high temperature, and the motor will soon burn.
    I think this is way oversimplified. I agree it is not the best idea to install a SG/LL HE on a system running at -40C evaporating and 50C condensing. However there is many systems running at operating conditions where a SG/LL HE can be aplied with great success. If very high condensing is experienced only a short time every year, then a SG/LL HE can be combined with a demand cooling system for lowering the suction gas temperature those days ambient is very high.

    The efficiency of the compressor is also an important factor under these circumstances. An ineficcient compressor leads to even higher discharge temperatures than a more efficient compressor does.

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: heat exchanger between subcooling and superheat line

    Quote Originally Posted by SteinarN View Post
    I think this is way oversimplified. I agree it is not the best idea to install a SG/LL HE on a system running at -40C evaporating and 50C condensing. However there is many systems running at operating conditions where a SG/LL HE can be aplied with great success. If very high condensing is experienced only a short time every year, then a SG/LL HE can be combined with a demand cooling system for lowering the suction gas temperature those days ambient is very high.

    The efficiency of the compressor is also an important factor under these circumstances. An ineficcient compressor leads to even higher discharge temperatures than a more efficient compressor does.

    Agreed, but these days I've seen too many pirates, who simply downsize the compressor and gets the extraquid with a SG/LL HE, causing 25K subcooling and 40K superheating, with a discharge temperature in excess of 130-140°C.
    For example icecream makers of an important italian brand.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: heat exchanger between subcooling and superheat line

    Quote Originally Posted by NoNickName
    Agreed, but these days I've seen too many pirates,...
    Unfortunately, this is what the refrigeration business is becoming. A situation where owners (or accountants) are making business decisions on the lowest initial cost without any regard for equipment life.

    The lowest common denominator everyone sees is cost, because they don't understand the long term effects and usually don't want to listen to someone.

    If all else fails, ask for help.


  8. #8
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: heat exchanger between subcooling and superheat line

    Quote Originally Posted by US Iceman View Post
    Unfortunately, this is what the refrigeration business is becoming. A situation where owners (or accountants) are making business decisions on the lowest initial cost without any regard for equipment life.

    The lowest common denominator everyone sees is cost, because they don't understand the long term effects and usually don't want to listen to someone.

    I thought this happened only here! Good to know we are not alone!

  9. #9
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: heat exchanger between subcooling and superheat line

    Thank you everyone. Great discussion. Let me digest them before I can make new comments. Thanks.

    Happy holiday!

    David

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: heat exchanger between subcooling and superheat line

    Holiday you said??? What's a holiday??
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Mar 2008
    Location
    US
    Posts
    74
    Rep Power
    17

    Re: heat exchanger between subcooling and superheat line

    Peter, I think this long weekend is holiday. July 4.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. Superheat and subcooling
    By marc5180 in forum Training
    Replies: 27
    Last Post: 08-10-2007, 09:21 PM
  4. Efficient Water-Source Condenser Design?
    By Enginerd in forum Fundamentals
    Replies: 4
    Last Post: 28-05-2007, 05:11 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •