    Question expention valve equalizer



    this is a question to Prof Sporlan but other views are welcome,
    In all of my installations through the years using TEV`s with ext. equalizer, the length of the of that 1/4 tube is allways different.
    sometimes short and sometimes longer. On big evaporators it is very long. I do not recall that any manufacturer gives any specific istructions.
    I would like to hear (read) your view, and others of course are most welcome to post any idea.

    thanks, chemi
    Last edited by chemi-cool; 04-12-2003 at 06:39 PM.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Since there is almost no flow - it is only a pressure egalisation - in this 1/4 tube, i should say that it makes no difference.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    You want the equalizer line to connect to the suction line downstream of the TEV bulb. If you reuqire a long capillary on the bulb, you will also require a long equalizing line.

  4. #4
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    As Daliti notes, there is normally little to no flow thru the external equalizer line when the TEV is in proper working order. As a result, you can run your 1/4" OD equalizer line as far as you need. 1/8" OD equalizer lines are also popular.

    If you see sweating and/or frosting on the equalizer line near the TEV, that would be an indication of valve pushrod leakage which would result in excess flow thru the equalizer line. It would be a good idea to replace the valve in this case.
    Prof Sporlan

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    Thank you all,
    I belive that the subject is coverd.

    chemi

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Originally posted by Prof Sporlan

    If you see sweating and/or frosting on the equalizer line near the TEV, that would be an indication of valve pushrod leakage which would result in excess flow thru the equalizer line. It would be a good idea to replace the valve in this case.
    This was a good tip for me. Never thought that was the reason but saw it many times. I always thought this was normal. I will make a note here in the company with your tip.
    Thanks Prof.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    If you see sweating and/or frosting on the equalizer line near the TEV, that would be an indication of valve pushrod leakage which would result in excess flow thru the equalizer line. It would be a good idea to replace the valve in this case.
    I would add that this is the reason the equalizer line should be after the TXV bulb, else this leakage will fool the TXV into starving the coil. With the equalizer line after the bulb the result will be slightly decreased superheat in the suction line but otherwise the valve should still work okay. Leakage was common in the older valves, but pushrod seal materials have improved over the years and this problem is far less common now.
    Last edited by Gary; 07-12-2003 at 12:19 PM.

  8. #8
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Great!.. I need to learn something, everyday... and I just did

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    When so much liquid leaks into the equalisation chamber that a false high suction pressure is indicated then the valve does tend to close some. On an AC system you will tend to end up with a starved evaporator and some frost buildup earlier on in the starved evaporator.
    This would depend upon the amount of leakage and the equalizer line sizing. If the line is large enough or the leak small enough, then the pressure in the equalization chamber would not be substantially effected. But yes, if we are talking about extremes, then I would agree.

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    hi Gary,
    since there is no way to measure that amount of leakage, I would suggest that " WHEN THERE IS A DOUBT - THERE IS NO DOUBT" and replace the TEV.

    CHEMI

  11. #11
    Join Date
    Oct 2003
    Location
    Edmonton Alberta, Canada
    Posts
    14
    Rep Power
    0
    It really depends on who you talk to on where to place an ex. line. Danfoss I believe prints in their instruction sheets to place the TX bulb BEFORE the ex. line so the valve will have better control but on the other hand Copeland on several occasions has told me to mount the TX bulb AFTER the ex. line to stop flood back to the compressor even though the pressure drop across the push rods would almost certainly boil off any liquid before it ever got back to the compressor. Basically a lot of discussion over something that to be honest is a little trivial in real life situations. I agree 100% with chemi-cool. " WHEN THERE IS A DOUBT - THERE IS NO DOUBT" ……replace the TEV if you see frosting on a ex. line

  12. #12
    Join Date
    Dec 2005
    Location
    Egypt
    Posts
    21
    Rep Power
    0

    Re: expention valve equalizer

    sorry, but may i ask TEV is abbreviation of what?

  13. #13
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: expention valve equalizer

    Thermal Expansion Valve. Sometimes called TXV.

  14. #14
    Join Date
    Dec 2005
    Location
    Egypt
    Posts
    21
    Rep Power
    0

    Re: expention valve equalizer

    thx star
    is TEV is the JT valve up stream any chiller(evaporator)

  15. #15
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: expention valve equalizer

    is there any difference for the senser bulb installed vertically or horizontally ? thx

    rgds
    LC
    I hear...I forget;I see...I remember;I do...I understand

  16. #16
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Cool Re: expention valve equalizer

    Always horizontal becose of thermostatic charge in sensing bulb.

    Renato RR

  17. #17
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: expention valve equalizer

    Always horizontal becose of thermostatic charge in sensing bulb.why???
    I hear...I forget;I see...I remember;I do...I understand

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: expention valve equalizer

    You can mount it also vertical with capillary upright. Done it 100 times and more.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: expention valve equalizer

    Quote Originally Posted by lc_shi
    Always horizontal becose of thermostatic charge in sensing bulb.why???
    G'day Ic_shi

    Upside down and with capillary at bottom and contents will leave sensing bulb.

    Most manufacturers have instructions with valve.

  20. #20
    Join Date
    Jan 2006
    Location
    Newcastle, United Kingdom
    Posts
    30
    Rep Power
    0

    Re: expention valve equalizer

    I am very empressed to everyone showing their briliant explaination and advice for the TEV external equalizer. I am new here needs more information about the deffirent in external TEV equalizer and internal equalizer. Which most probably used the TEV with internal equalizer?

    Please, I need to be inlighten.

    rudi
    mustardseed:) :) :)

Similar Threads

  1. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  2. Scotsman commercial H2O inlet valve
    By fullcourt in forum Trouble Shooting
    Replies: 9
    Last Post: 25-04-2006, 11:41 PM
  3. Need a correctly sized valve
    By Abe in forum Commercial
    Replies: 2
    Last Post: 26-10-2005, 08:42 PM
  4. Replies: 5
    Last Post: 16-10-2002, 12:38 AM
  5. Valve "Hunting"
    By Abe in forum Trouble Shooting
    Replies: 20
    Last Post: 21-01-2002, 12:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •