Results 1 to 20 of 20
Thread: expention valve equalizer
-
04-12-2003, 06:35 PM #1
expention valve equalizer
this is a question to Prof Sporlan but other views are welcome,
In all of my installations through the years using TEV`s with ext. equalizer, the length of the of that 1/4 tube is allways different.
sometimes short and sometimes longer. On big evaporators it is very long. I do not recall that any manufacturer gives any specific istructions.
I would like to hear (read) your view, and others of course are most welcome to post any idea.
thanks, chemiLast edited by chemi-cool; 04-12-2003 at 06:39 PM.
-
04-12-2003, 09:58 PM #2
Since there is almost no flow - it is only a pressure egalisation - in this 1/4 tube, i should say that it makes no difference.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
04-12-2003, 11:03 PM #3
You want the equalizer line to connect to the suction line downstream of the TEV bulb. If you reuqire a long capillary on the bulb, you will also require a long equalizing line.
-
05-12-2003, 12:08 AM #4
As Daliti notes, there is normally little to no flow thru the external equalizer line when the TEV is in proper working order. As a result, you can run your 1/4" OD equalizer line as far as you need. 1/8" OD equalizer lines are also popular.
If you see sweating and/or frosting on the equalizer line near the TEV, that would be an indication of valve pushrod leakage which would result in excess flow thru the equalizer line. It would be a good idea to replace the valve in this case.Prof Sporlan
-
05-12-2003, 04:23 AM #5
Thank you all,
I belive that the subject is coverd.
chemi
-
07-12-2003, 11:57 AM #6Originally posted by Prof Sporlan
If you see sweating and/or frosting on the equalizer line near the TEV, that would be an indication of valve pushrod leakage which would result in excess flow thru the equalizer line. It would be a good idea to replace the valve in this case.
Thanks Prof.
-
07-12-2003, 12:16 PM #7If you see sweating and/or frosting on the equalizer line near the TEV, that would be an indication of valve pushrod leakage which would result in excess flow thru the equalizer line. It would be a good idea to replace the valve in this case.
Last edited by Gary; 07-12-2003 at 12:19 PM.
-
07-12-2003, 11:08 PM #8
Great!.. I need to learn something, everyday... and I just did
-
09-12-2003, 10:25 AM #9When so much liquid leaks into the equalisation chamber that a false high suction pressure is indicated then the valve does tend to close some. On an AC system you will tend to end up with a starved evaporator and some frost buildup earlier on in the starved evaporator.
-
09-12-2003, 03:04 PM #10
hi Gary,
since there is no way to measure that amount of leakage, I would suggest that " WHEN THERE IS A DOUBT - THERE IS NO DOUBT" and replace the TEV.
CHEMI
-
10-12-2003, 11:33 PM #11
It really depends on who you talk to on where to place an ex. line. Danfoss I believe prints in their instruction sheets to place the TX bulb BEFORE the ex. line so the valve will have better control but on the other hand Copeland on several occasions has told me to mount the TX bulb AFTER the ex. line to stop flood back to the compressor even though the pressure drop across the push rods would almost certainly boil off any liquid before it ever got back to the compressor. Basically a lot of discussion over something that to be honest is a little trivial in real life situations. I agree 100% with chemi-cool. " WHEN THERE IS A DOUBT - THERE IS NO DOUBT" ……replace the TEV if you see frosting on a ex. line
-
31-12-2005, 12:45 PM #12
Re: expention valve equalizer
sorry, but may i ask TEV is abbreviation of what?
-
31-12-2005, 02:14 PM #13
Re: expention valve equalizer
Thermal Expansion Valve. Sometimes called TXV.
-
01-01-2006, 08:08 AM #14
Re: expention valve equalizer
thx star
is TEV is the JT valve up stream any chiller(evaporator)
-
04-01-2006, 02:14 AM #15
Re: expention valve equalizer
is there any difference for the senser bulb installed vertically or horizontally ? thx
rgds
LCI hear...I forget;I see...I remember;I do...I understand
-
04-01-2006, 11:07 AM #16
Re: expention valve equalizer
Always horizontal becose of thermostatic charge in sensing bulb.
Renato RR
-
05-01-2006, 01:13 AM #17
Re: expention valve equalizer
Always horizontal becose of thermostatic charge in sensing bulb.why???
I hear...I forget;I see...I remember;I do...I understand
-
05-01-2006, 06:45 AM #18
Re: expention valve equalizer
You can mount it also vertical with capillary upright. Done it 100 times and more.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
05-01-2006, 08:54 AM #19
Re: expention valve equalizer
Originally Posted by lc_shi
Upside down and with capillary at bottom and contents will leave sensing bulb.
Most manufacturers have instructions with valve.
-
07-01-2006, 04:54 PM #20
Re: expention valve equalizer
I am very empressed to everyone showing their briliant explaination and advice for the TEV external equalizer. I am new here needs more information about the deffirent in external TEV equalizer and internal equalizer. Which most probably used the TEV with internal equalizer?
Please, I need to be inlighten.
rudimustardseed:) :) :)
Similar Threads
-
Fitting an expansion valve question
By Larry2 in forum Air ConditioningReplies: 20Last Post: 08-04-2008, 04:17 PM -
Scotsman commercial H2O inlet valve
By fullcourt in forum Trouble ShootingReplies: 9Last Post: 25-04-2006, 11:41 PM -
Need a correctly sized valve
By Abe in forum CommercialReplies: 2Last Post: 26-10-2005, 08:42 PM -
TEV with MOP: how to keep valve body temp above bulb temp?
By DaBit in forum FundamentalsReplies: 5Last Post: 16-10-2002, 12:38 AM -
Valve "Hunting"
By Abe in forum Trouble ShootingReplies: 20Last Post: 21-01-2002, 12:29 AM