    I've recently got back into the trade after being offered a job by a friend of a friend. Since then i've been asked to install a sanyo heat pump cassette. I obviously excepted the work to make a bit of extra cash. So i was just reading through the installation instructions for the unit and noticed a few things that my boss does not do.

    The things the manual says youm must do that my boss doesn't;

    1. Apply refrigerant lubricant to all flares. ( I assume refrigerant lubricant is oil ? )

    2. Remove the knock-out hole from the side of the cassette unit and connect to a insulated duct drawing in outside air with a fan motor controlled by a bipolar ON-OFF swich with safety fuses.( my boss simply removes the knock-out hole )

    After noticing this I looked through a few more instruction manuals and noticed that when installing a Sanyo multi system you are supposed to replace air inside the copper tubing with Nitrogen gas to prevent copper oxide film forming during the brazing process!

    Are these things neccessary or are the manufacturers just going over the top to protect themselves.

    Basically, is my boss a cowboy or are cutting these corners acceptable within the trade ?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Cutting Corners

    Quote Originally Posted by eggman08.2008 View Post
    ............

    Basically, is my boss a cowboy or are cutting these corners acceptable within the trade ?
    I think that you have answered your own question.

    Be aware also that you should hold a Refrigerant Safe Handling ticket before working on these things.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Cutting Corners

    Quote Originally Posted by eggman08.2008
    Are these things necessary or are the manufacturers just going over the top to protect themselves.
    Let me answer this in this manner...

    Anytime an equipment manufacturer includes a recommendation for the installation to proceed in a specific way you would do well to follow those instructions. These requirements are stipulated by the manufacturer for specific reasons:

    1) To enable the equipment to reach it's maximum life span

    2) To get the equipment through the warranty period

    Not following the manufacturers recommendations are short-sighted and not based on any valid reason from the customer/equipment point of view.

    When someone tells you not to follow the manufacturers instructions they are usually:

    1) Hoping the equipment breaks soon so they can charge more money

    2) don't think the manufacturers know anything; i.e., I know more than they do!

    3) just plain stupid...
    If all else fails, ask for help.


  4. #4
    Join Date
    Jun 2008
    Location
    england
    Posts
    17
    Rep Power
    0

    Re: Cutting Corners

    I've got my nvq level 2 & a 2078 refrigerant handling certificate, so I am legally qualified. And I have the experience to install small systems.( cowboy style it turns out ). I just wanted to do a good job on my own installation.

    Can I ask then, what is refrigerant lubricant and what is a bipolar ON-OFF switch ?

    Also how do I fit the switch, is it simple? As I work with cowboys I dont think I've seen one.

    And just for training, what about the nitrogen, how do I do this?

  5. #5
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Cutting Corners

    Can I ask then, what is refrigerant lubricant and what is a bipolar ON-OFF switch ?

    Also how do I fit the switch, is it simple? As I work with cowboys I dont think I've seen one.

    And just for training, what about the nitrogen, how do I do this?
    The refrigerant lubricant is as you guessed the oil.

    If you choose to lube the flares then use same type of oil as used in the equipment.(oil will help a bad flare)

    The bipolar switch is just another name for double pole isolater.(does the space require fresh air in this manner) Make sure you use the correct knock-out and size your fan carefully.

    The OFN is trickled through the pipe/section you are brazing to displace the air not to pressurise in any form so make sure it is opened ended.

    Sometimes gas handling courses are not enough and good tuition is hard to get.

    There are some good courses out there try contacting POOH hes a good bloke

  6. #6
    Join Date
    Jun 2008
    Location
    england
    Posts
    17
    Rep Power
    0

    Talking Re: Cutting Corners

    Where would I get the electrical feed from to power the fan, would I get it from the indoor unit or directly from the mains? And how do I calclaute what size fan I need ?


    Oh... and thanks

  7. #7
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Cutting Corners

    OFN and lubricated flares=absolutely necessary.

    The fan to introduce fresh air is an optional accessory and it's really down to what the customer need/have ordered. But if the fresh air option isn't used then the knock out plate should be left in situ.

    If you fit a fan then you have to look in to the rating of the fan motor and decide if the feed can come from the A/C or if it needs a separate supply.

  8. #8
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Cutting Corners

    Just to complicate things, depending on the site, the fresh air fan may need to be integrated with the fire alarm system so that its shut off in case of a fire.... Also it would need its own filter as it supplies air to the cassette after the filter in the grill, unless you want a room full of wasps and leaves and such.Jon

  9. #9
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: Cutting Corners

    You must establish the fresh air requirements for the space first accounting for any other natural or mechanical ventilation. All AC can only cope with a specific volume/quality of fresh air. This must be calculated in conjunction with the space load and may require additional heating.

    Check manufacturers literature!!!!!!!

    Jon has a good point about fire regs and you may need a fire damper and/or other measures to ensure fire compartment integrity.

  10. #10
    Join Date
    Jun 2008
    Location
    england
    Posts
    17
    Rep Power
    0

    Re: Cutting Corners

    Is the Nitrogen neccessary when brazing on all units or just on Multi systems?
    Or is it only neccessary when stated by the manufacturer to do so ?

  11. #11
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cutting Corners

    Quote Originally Posted by eggman08.2008 View Post
    Is the Nitrogen neccessary when brazing on all units or just on Multi systems?
    Or is it only neccessary when stated by the manufacturer to do so ?
    Nitrogen is always necessary when brazing copper to prevent oxidation, unless the torch gas has already a premixed anti-oxidising agent, like gasflux (http://www.gasflux.com/liquid.htm).

  12. #12
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Cutting Corners

    Quote Originally Posted by NoNickName View Post
    Nitrogen is always necessary when brazing copper to prevent oxidation, unless the torch gas has already a premixed anti-oxidising agent, like gasflux (http://www.gasflux.com/liquid.htm).
    seems like that stuff is only for the outside of the pipes to make the brazing look good.

    you would still need OFN on the inside of the pipe.


    --------------------

    Eggman, you should take two small pieces of copper pipe, heat one till it is glowing red and then let it cool down.

    then take the other pipe, allow a small tricle of OFN to flow through it as you heat it up till it's glowing red and then let it cool down.

    Make sure your boss is watching and get's an eye of the result
    -Cheers-

    Tycho

  13. #13
    Join Date
    Jun 2008
    Location
    england
    Posts
    17
    Rep Power
    0

    Re: Cutting Corners

    Thanks for the advice every one. It seems like i'l get better training by just asking questions on this site than from working with my boss!
    So you probally see a few more questions on this site from me in the future.

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Cutting Corners

    Quote Originally Posted by eggman08.2008 View Post
    Thanks for the advice every one. It seems like i'l get better training by just asking questions on this site than from working with my boss!
    So you probally see a few more questions on this site from me in the future.
    and, we don't charge for the advice.

    We do however accept virtual doughnuts (donuts)
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Cutting Corners

    If the compressor was to break down after a few months of use (due to oxidisation left in the pipework because you didn't use nitrogen) the manufacturers may ask for the compressor to be sent back for them to examine why it failed. once they cut it open and find out that it failed due to poor installation, they will void your warranty and you will have to pay out.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  16. #16
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Cutting Corners

    Quote Originally Posted by marc5180 View Post
    If the compressor was to break down after a few months of use (due to oxidisation left in the pipework because you didn't use nitrogen) the manufacturers may ask for the compressor to be sent back for them to examine why it failed. once they cut it open and find out that it failed due to poor installation, they will void your warranty and you will have to pay out.
    That what happens in a perfect world. In the real world, a sales dept. rep. of the compressor manufacturer will put the blame on the guys who engineered the compressor, and will offer a new compressor for free, blaming the engineers that are always trying to let away the customers with a flawful compressor.

Similar Threads

  1. Help cutting open 40ft reefer, we now have problems
    By adrian_uk17 in forum Industrial
    Replies: 50
    Last Post: 28-11-2010, 08:11 AM
  2. Cutting through Stainless Steel
    By Abe in forum Air Conditioning
    Replies: 14
    Last Post: 14-06-2009, 03:57 AM
  3. Cutting unistrut
    By Andy AC in forum Tools and Calculators
    Replies: 9
    Last Post: 27-05-2007, 09:32 PM
  4. Why Is It? - Seeing round corners
    By Brian_UK in forum Chit Chat & Service Stories
    Replies: 6
    Last Post: 08-12-2004, 06:51 PM
  5. does cutting hours cut quality
    By fzr1000 in forum Transport
    Replies: 7
    Last Post: 25-05-2004, 05:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •