Thread: Slope if the cold store flooring
-
01-07-2008, 06:59 AM #1
Slope if the cold store flooring
In our projects, we never provide any slope for the flooring. If the ref. system is working properly, the moisture gets eliminated through defrost cycle. Some customers are still asking for slope in the cold store.
Any opinions on this?
-
01-07-2008, 10:42 AM #2
Re: Slope if the cold store flooring
at what temp. are u working?
-
01-07-2008, 03:09 PM #3
Re: Slope if the cold store flooring
If this is for a freezer then I think the floor slope is irrelevant. The water will freeze where it lands (if any water does reach the floor at all).
For a cooler where wet products are stored or a regular cleaning with water occurs, then the floor slope may not be a bad idea but... the slope would have to be minimal. The pallet racks could be leveled by the use of concrete pylons cast into the floor so that you have a true horizontal plane for the rack footing.
If the slope is included I suspect this will make the rack layouts even more difficult to design since I would think you would want the draining water to stay away from those areas where the product is being stored.If all else fails, ask for help.
-
01-07-2008, 04:23 PM #4
Re: Slope if the cold store flooring
That is right. We have been insisting on this point only. Storing materials shall be very difficult with slope. I think the client has agreed finally.
-
01-07-2008, 04:24 PM #5
Re: Slope if the cold store flooring
But I have seen Stork layouts for chicken processing & in that even ofr cold stores at -20 deg. they do insist on slope & drain system with complicated heating etc in the cold stores.
-
01-07-2008, 05:43 PM #6
Re: Slope if the cold store flooring
I heard Stork is doing this to make it easily to clean afterwards.
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
01-07-2008, 06:40 PM #7
Re: Slope if the cold store flooring
slope in freezers can be slippering and therefore dangerous.
-
01-07-2008, 06:46 PM #8
Re: Slope if the cold store flooring
depends where the slope goes to i suppose,you would not want it heading for the wall panels as it would saturate them after a time and also cause health issues and smells etc, wet fish is a good example where a drain is installed for washing out,never seen one anywhere else though !
-
01-07-2008, 07:08 PM #9
Re: Slope if the cold store flooring
One issue that may be forgotten is the fact that a floor drain offers a potential source for air flow into the cooler or freezer. If the floor drain does not have water in it, it will loose it's seal, which could allow free airflow into the space. This might add to the moisture load in the space.
If all else fails, ask for help.
-
02-07-2008, 02:02 AM #10
Re: Slope if the cold store flooring
When a customer insists on having a slope for floor cleaning, we also insist that the floor drain be located outside the room (usually in the ante room) with P-Trap located outside the building. P-traps located just below the floor drains usually becomes a future problem.
The cold room floor slope goes out through the door into the floor drain located at the ante room.
Of course, this work should be well supervised and water tested after the floor construction.
winfred
Pls. Remember K.I.S.S.
Keep It Simple, . . . . . .
-
03-07-2008, 07:30 AM #11
Re: Slope if the cold store flooring
Though we did some work with Stork, the client did not go in for the drains in the flooring as it was very very complicated matter. ofcourse the P traps was an issue, but the heaters & all that made it so complicated that time.
-
03-07-2008, 08:14 AM #12
Re: Slope if the cold store flooring
Can u tell whether your acu is floor mounted or ceiling mounted.
In case acu is floor mounted there might be chance of over flow of water in the drain tray during defrost thats why your client is asking for slope.
raj
-
03-07-2008, 08:59 AM #13
Re: Slope if the cold store flooring
winfred
Pls. Remember K.I.S.S.
Keep It Simple, . . . . . .
Similar Threads
-
Construction of new Cold Store
By lalthomas in forum System OptimizationReplies: 23Last Post: 19-04-2009, 02:01 AM -
Heat load dye to Reach truck in cold store
By smpsmp45 in forum NH3Replies: 15Last Post: 17-06-2008, 11:07 PM -
cold store flooring preparation
By smpsmp45 in forum NH3Replies: 3Last Post: 18-05-2008, 03:45 AM -
Expansion Joints in the cold store floor
By smpsmp45 in forum NH3Replies: 2Last Post: 17-05-2008, 07:47 AM -
Low Temperature Cold Store
By iceman007 in forum CommercialReplies: 12Last Post: 16-11-2005, 11:23 PM