    Slope if the cold store flooring



    In our projects, we never provide any slope for the flooring. If the ref. system is working properly, the moisture gets eliminated through defrost cycle. Some customers are still asking for slope in the cold store.

    Any opinions on this?



  2. #2
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: Slope if the cold store flooring

    at what temp. are u working?

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Slope if the cold store flooring

    If this is for a freezer then I think the floor slope is irrelevant. The water will freeze where it lands (if any water does reach the floor at all).

    For a cooler where wet products are stored or a regular cleaning with water occurs, then the floor slope may not be a bad idea but... the slope would have to be minimal. The pallet racks could be leveled by the use of concrete pylons cast into the floor so that you have a true horizontal plane for the rack footing.

    If the slope is included I suspect this will make the rack layouts even more difficult to design since I would think you would want the draining water to stay away from those areas where the product is being stored.
    If all else fails, ask for help.


  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Slope if the cold store flooring

    That is right. We have been insisting on this point only. Storing materials shall be very difficult with slope. I think the client has agreed finally.

  5. #5
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Slope if the cold store flooring

    But I have seen Stork layouts for chicken processing & in that even ofr cold stores at -20 deg. they do insist on slope & drain system with complicated heating etc in the cold stores.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Slope if the cold store flooring

    I heard Stork is doing this to make it easily to clean afterwards.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Slope if the cold store flooring

    slope in freezers can be slippering and therefore dangerous.

  8. #8
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Slope if the cold store flooring

    depends where the slope goes to i suppose,you would not want it heading for the wall panels as it would saturate them after a time and also cause health issues and smells etc, wet fish is a good example where a drain is installed for washing out,never seen one anywhere else though !

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Slope if the cold store flooring

    One issue that may be forgotten is the fact that a floor drain offers a potential source for air flow into the cooler or freezer. If the floor drain does not have water in it, it will loose it's seal, which could allow free airflow into the space. This might add to the moisture load in the space.
    If all else fails, ask for help.


  10. #10
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18

    Re: Slope if the cold store flooring

    When a customer insists on having a slope for floor cleaning, we also insist that the floor drain be located outside the room (usually in the ante room) with P-Trap located outside the building. P-traps located just below the floor drains usually becomes a future problem.

    The cold room floor slope goes out through the door into the floor drain located at the ante room.
    Of course, this work should be well supervised and water tested after the floor construction.

    winfred
    Pls. Remember K.I.S.S.
    Keep It Simple, . . . . . .

  11. #11
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Slope if the cold store flooring

    Though we did some work with Stork, the client did not go in for the drains in the flooring as it was very very complicated matter. ofcourse the P traps was an issue, but the heaters & all that made it so complicated that time.

  12. #12
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: Slope if the cold store flooring

    Can u tell whether your acu is floor mounted or ceiling mounted.

    In case acu is floor mounted there might be chance of over flow of water in the drain tray during defrost thats why your client is asking for slope.

    raj

  13. #13
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18

    Re: Slope if the cold store flooring

    Quote Originally Posted by Rajkumar View Post
    Can u tell whether your acu is floor mounted or ceiling mounted.

    In case acu is floor mounted there might be chance of over flow of water in the drain tray during defrost thats why your client is asking for slope.

    raj

    I believe Floor or Ceiling mounted drain problem should be solved by properly installing the drain pipe system with right size, slope, heater, p traps etc.

    Floor slope is only for cleaning purposes.
    Also, at low room temperature, slope is no use during overflow.

    winfred
    Pls. Remember K.I.S.S.
    Keep It Simple, . . . . . .

Similar Threads

  1. Construction of new Cold Store
    By lalthomas in forum System Optimization
    Replies: 23
    Last Post: 19-04-2009, 02:01 AM
  2. Replies: 15
    Last Post: 17-06-2008, 11:07 PM
  3. cold store flooring preparation
    By smpsmp45 in forum NH3
    Replies: 3
    Last Post: 18-05-2008, 03:45 AM
  4. Expansion Joints in the cold store floor
    By smpsmp45 in forum NH3
    Replies: 2
    Last Post: 17-05-2008, 07:47 AM
  5. Low Temperature Cold Store
    By iceman007 in forum Commercial
    Replies: 12
    Last Post: 16-11-2005, 11:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •