    r407/410 leak



    hi,
    if i have a leak on either of these refrigerant on a liquid line, would the blend be still intact and re-usable..?

    rgrds phil



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: r407/410 leak

    Yes.



    Or Maybe No.



    Or it might.



    It all depends on who you are listening to.

    If it's only liquid that's escaped then I can't see how the mixture would have changed but we all take our chances and live with our decitions.

  3. #3
    Join Date
    Jan 2008
    Location
    Kent
    Age
    47
    Posts
    46
    Rep Power
    0

    Re: r407/410 leak

    I read that a topped-up R407C system would perform around 90% efficiency, even after multiple leaks - some academic study, I can't find it now unfortunately.

  4. #4
    Join Date
    Mar 2007
    Location
    Sheffield
    Age
    45
    Posts
    8
    Rep Power
    0

    Re: r407/410 leak

    If you have a leak on a system - anywhere - blended refrigerants will change their... er.. blend!

    In the case of R407c its made up of 3 different refrigerants which all boil off at different temperatures, therefore are in different molecular states and hence some will escape through the hole whilst larger molecules may be held.

    Recaim it man, fix it, pressure test it - it'll save you the headaches later.

  5. #5
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: r407/410 leak

    I was taught that if the system had lost more than 15 or 20% of the total charge then it must all be reclaimed vacced out and then recharged with the correct amount.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  6. #6
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: r407/410 leak

    Listen to si he makes good sense

    If it is a leak on the liquid line the only time it is not going to noticabley alter the blend is if it is a big leak and that aint good either

  7. #7
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: r407/410 leak

    On your system
    When the compressor stops & the pressure equalises ,,,, will the liquid line then still be 100% liquid ?

    After some refrigerant is lost & the system is running SOG will the liquid line still be 100% liquid ?

    With R407c you have to suspect that the system is not leaking an equal measure of the 3 which make the blend even if the leak is on the liquid line.
    So the possibilty is that you are left with an incorrect blend.
    As the high pressure refrigerants will tend to escape first ( R32 & R125 ) you could assume a high concentration of R134a left in the refrigerant in the system & you might notice the system running slightly lower discharge temp & pressure after topping up. ( after you have first fixed the leak )
    If the system has lost most of the refrigerant charge then whats left might be almost pure R134a.

  8. #8
    froidclim's Avatar
    froidclim Guest

    Re: r407/410 leak

    hello dear colegues
    concerning the leak of r407c i have a 2 questions
    1 what is the normal low pressure of r407c
    2 can we use the leak detector as for r134
    pls advise

  9. #9
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: r407/410 leak

    1) I would expect to see around 4.5bar on the low side when running correctly but there are factors to consider.

    2) Yes you can use a leak detector on 134a.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  10. #10
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: r407/410 leak

    It all depends where the leak is. If it is in places where the mixture is at right compositions, it won't affect the mixture, like liquid line and suction line.

    If the leat occurs in the midle of the evaporator or condenser it could affect composition.

    If the mixture is not at the right composition you will get some variable out or range, like discharge temperature or capacity.

    The only real way to tell is have a composition test on a sample of the mixture, and I've never done this.

    So to be en the safe side you better recover/recharge but you can first give a try.

    The leak detectors for HFCs need to be more sensible than HCFCs so you should check the manufacturer data.

Similar Threads

  1. Leak detectors
    By Temprite in forum Tools and Calculators
    Replies: 54
    Last Post: 18-08-2010, 04:15 PM
  2. Evasive gas leak
    By Feeze in forum Technical Discussions
    Replies: 24
    Last Post: 18-08-2008, 07:22 AM
  3. Help!!! Shell and Tube Evap Leak
    By tommy Gun in forum Trouble Shooting
    Replies: 7
    Last Post: 22-07-2007, 12:45 PM
  4. Tiff 5000 leak detector
    By davidchesson in forum Tools and Calculators
    Replies: 6
    Last Post: 06-11-2006, 04:26 AM
  5. Can't find leak with UV Dye
    By jd_boggs in forum Transport
    Replies: 6
    Last Post: 16-09-2006, 06:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •