Results 1 to 3 of 3
  1. #1
    Join Date
    Nov 2006
    Location
    INDIA
    Posts
    10
    Rep Power
    0

    Smile Function of Economiser and intercooler



    Dear sir,

    we have new installed compound refrigeration system with economier and intercooler and screw compressor
    I want to know that when we should use compound system and also want to know that function of economiser and inercooler.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Function of Economiser and intercooler

    Patil
    You are a bit short on details, if compounded with intercooler and economizer, there will be more than one screw compressor. Plus, can you enlighten all of us with your refrigeration experience, if any? It will prompt people to respond or not.
    Magoo

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Function of Economiser and intercooler

    An economizer is simply a process for providing liquid refrigerant (colder than condensing temperature) to the expansion device. This helps to improve the compressor capacity with little increase in power input.

    An intercooler simply desuperheats the discharge gas of a low stage (booster) compressor before the gas enters the high stage compressor. This increases the high stage compressor capacity and decreases the discharge temperature & oil cooling heat loads.

    A two stage system is used when you have low temperature requirements and want to minimize the total power input required by the compressors.

    How or where or when you use these depends on what you hope to achieve.
    If all else fails, ask for help.


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •