    checking Oil Level



    Hi chaps this should be a quickey an hopefully somthing you can clear up for me.

    Since being in this trade which is a while now so you think that i should know better, I have been told several differant ways to check the level of compressor oil so my question is ...

    When is the best time to get the correct level of oil to see if it needs topping up. When its just started, Stopped for awhile, Running for awhile ??

    Once you have the correct level how or what is the best top up method. The compressors i generally work on are a scroll type Danfoss Manurope model SM100S4VA (to be precise)

    Many thanks in advance guys

    Pom



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: checking Oil Level

    Oil level should only be checked after the compressor is working for a while.

    If the oil level is too low, you should find out where it is in the system.

    If a condenser is below the compressor, it can hold oil, the part that has oil in it, is not as hot as the rest of the condenser.

    the same in evaporators, the part with oil is not as cold as the rest of it.

    there are a few ways to return stubborn oil back to the compressor but that for another time.

    On danfoss scrolls, fill up while working through the suction valve or through the capped Schroeder on the side.

  3. #3
    Join Date
    Apr 2008
    Location
    Gosport Hants
    Age
    63
    Posts
    24
    Rep Power
    0

    Re: checking Oil Level

    Hey thanks for that chemi-cool.
    The compressor in question had a pinhole leak on the liquid line out of the condenser, Needless to say there is oil everywhere but before i shut the system down i checked the compressor whilst it was running and couldnt see a level. The only oil i could see was just running down the site glass on the side of the compressor.

    Pom

  4. #4
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    17

    Re: checking Oil Level

    I agree wth chemi-cool but may I add

    Topping should be done, if necessary, only once and keep close frequent observation at least until the first defrost.

    If you have to do it twice, having thermal load, I'd recover/open and check where the oil is!

    If the oil can be seen in the sight glass, topping should be unnessesary.

    Also learn how to read the sight glass, some are tricky.

    Too much oil=poor performance

  5. #5
    Join Date
    Apr 2008
    Location
    Gosport Hants
    Age
    63
    Posts
    24
    Rep Power
    0

    Re: checking Oil Level

    If you have to do it twice, having thermal load, I'd recover/open and check where the oil is!

    Sorry gxmplx not too sure what you mean by that.

    Pom

  6. #6
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,853
    Rep Power
    46

    Re: checking Oil Level

    I think he is saying that if you keep having to top the oil level up and it isn't leaking out and the system is not working with a low load, and hence not enough gas speed to bring the oil back to the compressor, that you need to find out where the oil is going rather than keep topping it up.
    e.g. we once had a tap in an oil return line that did not have a hole drilled in it through the 1/4" flared bit.

    Jon
    Last edited by monkey spanners; 28-06-2008 at 08:28 PM. Reason: more info

  7. #7
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    17

    Re: checking Oil Level

    Quote Originally Posted by monkey spanners View Post
    I think he is saying that if you keep having to top the oil level up and it isn't leaking out and the system is not working with a low load, and hence not enough gas speed to bring the oil back to the compressor, that you need to find out where the oil is going rather than keep topping it up.
    e.g. we once had a tap in an oil return line that did not have a hole drilled in it through the 1/4" flared bit.

    Jon
    Exactly TKS, at partial load a system may trap oil but never at full load.

    If it does, there is a design problem.

  8. #8
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    17

    Re: checking Oil Level

    I should have added that topping is not the solution for solving a partial load oil logging.

    In this case if you solved the leak I would wait at least after a defrost or if there's no defrost shut the system down and force it to come back at full load and observe oil level for a while.

    If oil keeps low refill once.

    There's no reason to fear a sight glass with low oil level in scrolls as long as you can see a level during low load operation.

    Always remember there is a time lag for oil to return to the compressor.

  9. #9
    Join Date
    Apr 2008
    Location
    Gosport Hants
    Age
    63
    Posts
    24
    Rep Power
    0

    Re: checking Oil Level

    Hey thanks for the advice Guys its very helpfull.

    I recon that the oil must generally be low as it had lost so much through the leak that ive just repaired so i am assuming that at least that much should go back in which would probably amount to just under a quarter of a pint in my reconning (going by the amount splashed all over the bottom of the Airedale unit).. althouth its always nice to get the well skilled views from yourselves.

    many thanks

    Pom

  10. #10
    Join Date
    Apr 2008
    Location
    Gosport Hants
    Age
    63
    Posts
    24
    Rep Power
    0

    Re: checking Oil Level

    Ermm ..unless its best not to for some reason of course ??

    Pom

Similar Threads

  1. Level 2 NVQ
    By Danny11 in forum Air Conditioning
    Replies: 22
    Last Post: 21-08-2010, 10:22 PM
  2. running the oil pump to check oil level
    By Ice Queen in forum Technical Discussions
    Replies: 7
    Last Post: 02-08-2008, 05:23 PM
  3. Risk in high compressor oil level?
    By Ice Queen in forum Trouble Shooting
    Replies: 0
    Last Post: 20-05-2008, 02:28 PM
  4. Oil level control question
    By racknovice in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 06-09-2007, 09:29 PM
  5. A useful article
    By chemi-cool in forum New Technologies
    Replies: 5
    Last Post: 21-07-2007, 03:25 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •