Page 1 of 2 12 LastLast
Results 1 to 50 of 57
    Jun 2008
    Philadelphia
    69
    8
    Mapp gas for brazing???
    I don't use mapp gas, and I've noticed it mentioned. Is it used for brazing line-sets? What are the limitations?
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Mapp gas for brazing???
    You will need a diferent tip, No. 4 is what I use.
    I solder pipes up to 2 1\8 without any problems.
    Rods with 2% silver.
    Mar 2006
    uk northampton
    15
    I use mapgas on its own using a brazing torch and I find its only really good for anything upto 7/8, anything larger and I use any oxy rig
    11,025
    You can go to larger sizes with a double burner nozzle on Mappgas.
    Mar 2006
    uk northampton
    15
    ive seen them but I haven't used them...... whats the size capable
    Mar 2006
    Lancashire
    1,859
    28
    I have the Double nozzle one and it does up to 1" 3/8th.
    Marc
    Mar 2006
    uk northampton
    15
    thats good enough for majority of installs amd you dont have to carry a heavy rig everywhere
    Nov 2005
    211
    I have used MAPP gas for up to an evaporator block. It takes a while for the block but it works. For pipes, it's easy.
    There is also oxy-propane. Not sure how it compares to plain MAPP, however.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine
    Feb 2006
    derbyshire
    610
    its dead handy for smaller stuff and saves carting the bottles arround,you can get through a few refills though,install,s with a fair bit to do means setting the oxy/accet pack up with the pepper pot nozzle on.quicker,better and cheaper
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    May 2006
    Yorkshire
    72
    417
    We use MAPP gas with a shield attached it is quite good up to 7/8 copper tube only and the braze joint needs to be away from any large mass of metal as the heat can be drawn away just as fast as you apply it. Can be very difficult outdoors if there is a breeze, then some wind break needs to used.
    Mar 2008
    54
    273
    Used Mapp gas for twenty years no problem with shield upto 1 1/8 with single burner. I know you can get get the double burner which would braze the larger pipes quicker.
    Transvestites are men who like to eat, drink, and be Mary.
    May 2008
    66
    802
    its quick, nice to handle,easy on flask change ,no big bottles and flex to hump around, just be careful outdoors and windy.
    Ice
    Nov 2006
    63
    392
    Having been brought up on Oxy Acetylene I do not like MAPP Gas for brazing fridge pipe its OK for plumbers but it does too much damage to the pipe for my liking due to the lenght of time it takes to get the pipe up to temperature. Unless you are nitrogen purging you are going to get far more oxidisation in the pipework than with Oxy Acet due to the heat spread along the pipe, we did an experiment and on 7/8" we got three times as much oxidisation inside the pipe and it took 5 times as long as with Oxy Acet.
    Another issue is the annealing along more of the pipe due to the spread.
    Totally useless for doing coil end as you cannot get a small enough flame to not effect the other joints.
    My opinion is that its OK for plumbers but no good for fridge engineers and its only lazziness that stops Oxy Acet being used.
    I will not let it be used on fridge pipe in our department.
    Stand back and wait for the bullits.
    Ian
    May 2008
    170
    Rat-a-tat-tat
    Apr 2006
    stafford
    42
    974
    mapp gas up to 5/8 then find this a great hand for doing pot changes and leaks (see pic) anything really big (and can park near) its the big boy bottles
    Paul
    "KEEP IT COOL"
    snoring beagle's Avatar
    snoring beagle Guest
    I only use it for Harris Stay Bright 8. On smaller pipe up to 1 3/8. Any piping that vibrates or larger gets nitrogen and oxy-acetylene using silver.
    May 2008
    Northern NSW, Australia
    56
    32
    Love my mapp gas.
    Very handy, but haven't seen a double nozzle/burner. Tried to google it but got nothing.
    My little torch will do up to 1'1/8 if there's no wind and a little patience, other wise the oxcy comes out..
    If I can make more than my wife can spend in a day, that's a good day....
    11,025
    Jadeair, I got my double nozzle from Climate Center some time ago.
    Here's a link to the Rothenberger (USA) site that details the torch.
    http://www.rothenberger-usa.com/file...NAL-lo-res.pdf
  19. #19
    May 2008
    56
    32
    Thank's Brian, always on the look out for a new toy, I mean tool.
  20. #20
    11,025
    They do issue a warning with it as well - it makes a lot of noise!
    It does
  21. #21
    Feb 2007
    oldham
    49
    44
    you an get a accet only kit from boc,very handy and heats up quicker than mapp gas
  22. #22
    Mar 2006
    Lancashire
    1,859
    28
    I have just got the set that Superswill uses. Much better imo and heats up much faster than the mapp gas and has a smaller flame, handy for those tricky braizes.
    Marc
  23. #23
    nevgee's Avatar
    May 2006
    Yorkshire
    72
    417
    Quote Originally Posted by Pooh View Post
    ...... Unless you are nitrogen purging you are going to get far more oxidisation in the pipework than with Oxy Acet due to the heat spread along the pipe, ....... we got three times as much oxidisation inside the pipe and it took 5 times as long as with Oxy Acet.
    Ian
    Pooh !
    Surely you're not suggesting you don't purge with ofn when brazing?
  24. #24
    May 2008
    midlands
    64
    37
    Quote Originally Posted by nevgee View Post
    Pooh !
    ROFLMAO
  25. #25
    Oct 2007
    NZ
    85
    Quote Originally Posted by fazzamouse View Post
    but then youd have to deal with BOC
  26. #26
    Jan 2007
    South East
    48
    10
    great for lighting bbq too
  27. #27
    Apr 2007
    West Midlands
    45
    55
    Love the mapp gas, saves me dragging the oxy kit all over the place.....although if it's windy you'll struggle at anything over 5/8. Also its only good for simple brazing, don't try to braze anything like a reversing valve or anacondas as it takes so long to heat up there's massive heat spread!!!
  28. #28
    Apr 2002
    scotland
    114
    23
    no one use mapp gas and oxygen?
    its great!
    A lot of places are not letting us use Acetylene on their premises, this is mostly hospitals / medical.
  29. #29
    Jun 2006
    Ireland(ROI)
    44
    28
    If you are going to do more than 5 or 6 joints on more than 5/8 tube then you are as well bringing the oxy rig in from the van, it takes ages to get proper heat into the pipe with Mapp Gas.
    Also wouldn't use to brave TEV's or other components, the heat spreads too far and for too long, you risk damaging these components.
    I shout at my apprentices when I see them even getting a bottle of it out the van!
  30. #30
    Somerset
    69
    4,698
    Truth be told, I like a lot of the guys have said on this thread.
    Prefer to use Oxy acetylene as the hotter heat source, keeps the heat more local.
    As Richard b points out there are a rising number of sites. Who are banning the use of acetylene.
    I recently had to replace a liquid line filter (2) core assembly on 1 5/8" pipes with 1 end within say 8" of the liquid line isolation valve.
    This repair was outside when it was windy.
    I had already used my newly acquired double barrelled Turbo torch.
    To silver solder the two tails into the filter body (Prior to going to site. Just in case I needed to use the trusty porta pack)
    It worked fine.
    Not the same when on site though.
    Because of the total mass of the filter body, pipe and Isolation valve (which had to be covered with a wet rag as it held the system charge on the other side).
    When it came to brazing the pipes it ended up with 3 of us applying heat.
    1 with a turbo torch another with a maxi gas (same as shown by Superswill) and me with the double barrelled Turbo torch.
    Despite using 15% silver content rods ( they melt at lower temps!) there was so much residual heat around that the Isolation Valve started to smoke!!!!
    Luckily we managed to get enough heat at the joint for the braze to flow but it was a close call.
    So to summarise
    In some circumstances I have yet to discover a viable alternative to Oxy- Acety. (IE. Any pipes bigger than say 1.5")
    Hopefully a alternative will be found?
    But the dreaded H&S is making it harder to use
    PS HRP sell the D/Barrelled Turbo Torches.
  31. #31
    Feb 2006
    valencia
    15
    uniweld.com/catalog/air_gas/unitorch/rp3t3.htm
    have 3 tips.
  32. #32
    Jul 2007
    Australia
    1,845
    Quote Originally Posted by chris96 View Post
    Quote Originally Posted by leftjobrunning View Post
    Exactly my usage and beliefs. I use it for normal small diameter pipe joins, not for heaps of welds, or to anything that's going to suck up heat like compressors or be heat damaged like reversing valves or TX etc
  33. #33
    Jul 2008
    edinburgh
    47
    15
    Canny beat the old turbo torch on the small stuff,great for sweating/welding capillaries,dryers etc.
    Amazing for camping
  34. #34
    Devon
    73
    8
    Hi All, Mapp gas+turbo torch, just the job for a fast evap defrost.
  35. #35
    Feb 2009
    bruges
    45
    42
    Quote Originally Posted by Mazdamike View Post
    turbo torch great to start a BBQ
    3/8 1/2 not more (turbo torch)
  36. #36
    Mar 2006
    uk northampton
    15
    I use a Black & Decker paint stripper gun for defrosting
  37. #37
    Feb 2009
    telford
    2,092
    33
    i use mapp gas combined with oxy on my rig works 100% ,it contains some acetylene,the latter is the daddy but oh so heavy,when i use my rig outdoors it seems to attract a breeze?
  38. #38
    Spencer ma.
    108
    Oxy acetylene with Uniweld MTF-2 5 1/2" Cap'n Hook tips great for brass to copper. try it you will love it
  39. #39
    idecrio716's Avatar
    idecrio716 Guest
    mapp gas is only good for small pipes not more than 5/8,but a double torch will do the trick with a shield.
    i still love oxy-accyt.its fast and no risk of damaging any components due to longer time heating and heat travel through pipes.
    oxy accyt still saves money and effort.except for a hole in the pipe,hehehe!
  40. #40
    idecrio716's Avatar
    idecrio716 Guest
    before i used 2 mapp gas and 2 torches,combined and wrapped 2 mapp tanks with an electrical tape,with big pipes,crazy thing huh,but it works!!!!!!!!!!!!!!
    but then again,i turned back to oxy-accyt.hahaha
  41. #41
    Feb 2005
    london
    32
    I worked with an ozzie guy who used air/acetylene never seen one before or since
    only had to carry the one bottle super fast
    has anybody any info ?
  42. #42
    Aug 2007
    Sydney
    1,083
    23
    HI Guys and Girls
    There have been many advances in technology since 2008 when this post first started. At the ARBS exibition in Sydney this year I saw the new system - It uses a map gas and same size oxy bottle, only weighs about 7kg or less. Can do what the old oxy accetalyne did and costs about Au$500 for regs and hoses. Does anyone know how to make this message box I'm writing in bigger?
  43. #43
    3,856
    Quote Originally Posted by jsimon View Post
    I think Rothenberger make one, have a look in their catalogue.
    Jon
  44. #44
    Jun 2008
    NZ
    102
    I would post a link if I could, but uniweld's website have air-acetylene handles listed.
    There was one in the tool store when I worked at macca's - I used it once on a comp change in a ceiling with difficult access.... for the hassle it was to use and relatively poor heating I would have been better to have taken the time to drag an oxy bottle up as well.
  45. #45
    Mar 2010
    56
    5
    turbo 200 torch sold in Australia which is Mapp gas plus oxygen and is only 100 degrees cooler then oxy acetelyne. Tesuco sell here.
  46. #46
    Dec 2005
    Cheshire
    264
    21
    Quote Originally Posted by palmerm View Post
    Is this the one?
    http://techweld.co.uk/index.php?act=...&productId=619
    Does this use the normal mapp gas bottles and is it available through any uk refrig. wholesalers?
  47. #47
    Apr 2008
    West Yorkshire
    42
    Map gas is very convenient, I also have an oxy turbo kit, but it isnt that good. Flame always cuts out and on a windy day forget it.
  48. #48
    Jul 2007
    Australia
    1,845
    Quote Originally Posted by Slim R410a View Post
    Is this the one?
    looks good, I am really interested in it too.
    I have the standard hand held single mapp gas torch and I don't like it at all. Only have it for roof tops, ceiling spaces and for when I'm up a ladder. It does an inferior job to oxy/acet by a long long long way. I wouldn't dream of using it for a compressor change or any piping over 5/8"
    Even last week I was installing plumbing for my kitchen, and the little MAPP gas torch was a massive fail and I had to get out the oxy/acet. It was just a 1/2" tee piece and the MAPP would rather spend 10min trying to burn my house down and not heat the copper up, while the oxy/acet did the job in 40 seconds.
    But I'd rather have more room in my vehicle, (would allow me to have another cylinder of refrigerant in there) and stop paying $30 a month cylinder rental to BOC if a small mapp/oxy setup with disposable cylinders was around and well priced and readily available.
  49. #49
    3,856
    FSW do a oxy mapp set up that has a refillable oxy bottle and uses standard mapp bottles, theres no rental charge as you own the oxy bottle. Dave says its very good but i've not tried it yet. FSW and Climate do the smaller sets where both are disposable.
    Called in my local calor place recently and found they do returnable mapp bottles, am thinking of giving them a try as the disposable ones seem quite wastfull.
    Jon
  50. #50
    May 2008
    56
    32
    I've had a turbo 200 for about 6weeks now.
    I've used it to repair a cracked 1 1/8" pipe with no dramas and a compressor change.
    I still use my mapp gas on most smaller jobs, the turbo 200 where I need extra heat in a hurry and drag my oxcy out of the office when I have larger install jobs.
    I think the only problem I'll have with the turbo 200 is the oxcygen time only lasts 25min approx. and they cost $40 - $50 a bottle.
    Cheers Nick..