    Arrow 30GTN Chiller



    B1 compressor EXV not opening and system undergoes to Vacuum.DP showing 226psi,SP showing 476psi. The Gauge pressure reading is 100psi and it redusing to 0psi
    Compressor sensor,cooler sensor and EXV drive board replaced.But the Suction pressure still showing the same.
    EXV checked through service test and it is working.
    pl. give some answers.

    Thanks.
    Last edited by vinod; 27-06-2008 at 06:57 AM.



  2. #2
    Join Date
    May 2008
    Location
    India
    Posts
    6
    Rep Power
    0

    Re: 30GTN Chiller

    Hi...How come the SP is 476psi when the EXV doesn't open?

  3. #3
    moideen's Avatar
    moideen is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Apr 2008
    Location
    u.a.e
    Age
    49
    Posts
    412
    Rep Power
    23

    Re: 30GTN Chiller

    Quote Originally Posted by vinod View Post
    B1 compressor EXV not opening and system undergoes to Vacuum.DP showing 226psi,SP showing 476psi. The Gauge pressure reading is 100psi and it redusing to 0psi
    Compressor sensor,cooler sensor and EXV drive board replaced.But the Suction pressure still showing the same.
    EXV checked through service test and it is working.
    pl. give some answers.

    Thanks.
    hi vinod
    did you check exv by manually.remove exv ,then check by service mode.if tehere any mechanical problem(motor bearing or rotor magnet)it should be cleared.when comp going to vacum,check exv status on output mode.30 gtn comfort link do not use transducer,using only thermistors.thats why display shows high suction pressure.

  4. #4
    Join Date
    Dec 2005
    Location
    uae
    Posts
    54
    Rep Power
    19

    Re: 30GTN Chiller

    Quote Originally Posted by moideen View Post
    hi vinod
    did you check exv by manually.remove exv ,then check by service mode.if tehere any mechanical problem(motor bearing or rotor magnet)it should be cleared.when comp going to vacum,check exv status on output mode.30 gtn comfort link do not use transducer,using only thermistors.thats why display shows high suction pressure.
    # EXV opened through service test and pressure variation indicating on manifold gauge.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: 30GTN Chiller

    Might be a stupid question but I will ask anyway.
    Does this system have any form of hot gas bypass.
    These are usually enabled during initial start-up?

    If so could this be relevant?

    Or are you saying that pressures are as expected when viewed with independant gauges.
    There is definatly something wrong when a suction readout is higher than discharge.
    With this in mind it is not likely to be the Expansion Valve.
    Good one this keep us posted !
    Grizzly

  6. #6
    shadman's Avatar
    shadman Guest

    Re: 30GTN Chiller

    i need the software of confort link for 30gtn chillir anywone tell me how i get it

  7. #7
    Join Date
    Dec 2009
    Location
    Myanmar
    Age
    40
    Posts
    6
    Rep Power
    0

    Re: 30GTN Chiller

    Hi vinod,
    You should be check filter drier.

  8. #8
    Join Date
    May 2009
    Location
    Sydney
    Posts
    73
    Rep Power
    15

    Re: 30GTN Chiller

    May be a stupid comment but is the compressor pumping?

Similar Threads

  1. VRV/VRF vs Chiller (heat pump)
    By nike123 in forum Technical Discussions
    Replies: 8
    Last Post: 09-06-2011, 03:21 PM
  2. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  3. Dunham Bush Chiller Alarm
    By Regulator in forum Air Conditioning
    Replies: 11
    Last Post: 08-12-2010, 01:42 AM
  4. DIY aquarium chiller
    By BarraCuda in forum Technical Discussions
    Replies: 18
    Last Post: 06-10-2010, 11:02 PM
  5. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •