Thread: 30GTN Chiller
-
27-06-2008, 04:23 AM #1
30GTN Chiller
B1 compressor EXV not opening and system undergoes to Vacuum.DP showing 226psi,SP showing 476psi. The Gauge pressure reading is 100psi and it redusing to 0psi
Compressor sensor,cooler sensor and EXV drive board replaced.But the Suction pressure still showing the same.
EXV checked through service test and it is working.
pl. give some answers.
Thanks.Last edited by vinod; 27-06-2008 at 06:57 AM.
-
27-06-2008, 05:54 AM #2
Re: 30GTN Chiller
Hi...How come the SP is 476psi when the EXV doesn't open?
-
27-06-2008, 11:31 AM #3
Re: 30GTN Chiller
hi vinod
did you check exv by manually.remove exv ,then check by service mode.if tehere any mechanical problem(motor bearing or rotor magnet)it should be cleared.when comp going to vacum,check exv status on output mode.30 gtn comfort link do not use transducer,using only thermistors.thats why display shows high suction pressure.
-
29-06-2008, 05:08 AM #4
-
29-06-2008, 04:08 PM #5
Re: 30GTN Chiller
Might be a stupid question but I will ask anyway.
Does this system have any form of hot gas bypass.
These are usually enabled during initial start-up?
If so could this be relevant?
Or are you saying that pressures are as expected when viewed with independant gauges.
There is definatly something wrong when a suction readout is higher than discharge.
With this in mind it is not likely to be the Expansion Valve.
Good one this keep us posted !
Grizzly
-
27-12-2009, 01:05 PM #6
Re: 30GTN Chiller
i need the software of confort link for 30gtn chillir anywone tell me how i get it
-
31-12-2009, 02:47 AM #7
Re: 30GTN Chiller
Hi vinod,
You should be check filter drier.
-
31-12-2009, 06:41 AM #8
Re: 30GTN Chiller
May be a stupid comment but is the compressor pumping?
Similar Threads
-
VRV/VRF vs Chiller (heat pump)
By nike123 in forum Technical DiscussionsReplies: 8Last Post: 09-06-2011, 03:21 PM -
process chiller help
By talon771 in forum IndustrialReplies: 8Last Post: 12-01-2011, 08:42 PM -
Dunham Bush Chiller Alarm
By Regulator in forum Air ConditioningReplies: 11Last Post: 08-12-2010, 01:42 AM -
DIY aquarium chiller
By BarraCuda in forum Technical DiscussionsReplies: 18Last Post: 06-10-2010, 11:02 PM -
York Screw Chiller How low will it go?????
By bruceboldy in forum Industrial CompressorsReplies: 11Last Post: 10-08-2007, 10:29 PM