    -20 deg freezer



    Hi this box has 4 - 5 ton compressors
    where I need help is when the unit comes out of defrost it is so cold that the defrost tem / fan delay will not switch over to delay the fans from starting so the water will freeze back on the coil not on the fan shroud and fan blade. I have the bulb in the coil top center and I tried to replace the control I need to find a control the will keep the fans off till 10 deg most defrost term is @ 45 deg thanks



  2. #2
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: -20 deg freezer

    I think you have to chenge the defrost setting . We check the suction temp & decide on the time for the defrost.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: -20 deg freezer

    Quote Originally Posted by tonyhavcr View Post
    Hi this box has 4 - 5 ton compressors
    where I need help is when the unit comes out of defrost it is so cold that the defrost tem / fan delay will not switch over to delay the fans from starting so the water will freeze back on the coil not on the fan shroud and fan blade. I have the bulb in the coil top center and I tried to replace the control I need to find a control the will keep the fans off till 10 deg most defrost term is @ 45 deg thanks
    Hi Tony.
    Just a quick reply.
    It sounds as if you have tried a lot of options so my suggestion may be useless?
    Have you tried lowering the defrost sensor slightly?

    I must admit your last comment has me confused?
    surely there are lots of options or have I missed something?
    Cheers Grizzly

  4. #4
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: -20 deg freezer

    tony
    is there a drip down delay on this system? after defrost ?

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: -20 deg freezer

    Change the controller to one where the sensor is wired to an outside-of-box control - this way there are no mechanical switches inside.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: -20 deg freezer

    Ranco makes an adjustable 3 wire fan delay/defrost termination switch.

    part # F25-107

    I too, am confused by your last comment.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: -20 deg freezer

    The return bends on the evaporator will freeze first, not the fins. If the air temperature is cold enough it could be possible for this to simply bypass the fan delay and contribute to the problems.
    If all else fails, ask for help.


  8. #8
    Join Date
    Aug 2006
    Location
    Spencer ma.
    Age
    60
    Posts
    108
    Rep Power
    18

    Re: -20 deg freezer

    Thanks for the help : (you have to change the defrost setting) all 4 units have different defrost times.

    (I must admit your last comment has me confused?
    surely there are lots of options or have I missed something?
    Cheers Grizzly ) The defrost heaters are started by the time I have 4 defrost @ 45 mins they terminate by time or temp you want it to terminate by temp shorter defrosts for 1 this around 45deg.

    (is there a drip down delay on this system) No
    tony---1 there is no drip down delay but I did add a time delay to the evaporator fans and set it for 3 sec
    that will let the water freeze to the coil to see if adding one would help it didn't work.

    ( Ranco makes an adjustable 3 wire fan delay/defrost termination switch.) Thank you powell but ranco 3 wire fan delay/defrost termination switch bulb must be mounted vertical not horizontal I have the bulb horizontally in the coil.

    I will check on the job and get back with more info


  9. #9
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: -20 deg freezer

    Quote Originally Posted by tonyhavcr View Post
    Thank you powell but ranco 3 wire fan delay/defrost termination switch bulb must be mounted vertical not horizontal I have the bulb horizontally in the coil.
    tony,

    The bulb was redesigned. The revised design isn't position sensitive and the word "TOP" has been removed from the bulb.

    powell

  10. #10
    Join Date
    Aug 2006
    Location
    Spencer ma.
    Age
    60
    Posts
    108
    Rep Power
    18

    Re: -20 deg freezer

    (Tony,

    The bulb was redesigned. The revised design isn't position sensitive and the word "TOP" has been removed from the bulb.

    powell )

    thanks powell this shows how far behind we are in ma. us when I got one from my suppler last week all they had was the old type

    I went to the job found the evaporator fans froze to the shroud again.
    The evaporator was froze @ the top 3" down no more and was 4 to 5" thick.
    I did find this be for when I changed the control
    defrosted all the ice and tested all the heater and amped them all heaters look good .
    The bulb is is the middle of this ice.
    This is a 502 system 20 yrs old but works well the fan delay I have is a danfoss the doors are 20' in front of
    coil I do have air curtains. One other unit does the same the evap @ the top 3" but it stop in the middle of the coil so I got ice coil ice but this one is working fine and water does not come off the coil.

Similar Threads

  1. ice cream truck freezer
    By GaryC in forum Transport
    Replies: 7
    Last Post: 06-12-2008, 02:19 AM
  2. Freezer compressor running 20 Hours/day
    By rickcw in forum Domestic
    Replies: 12
    Last Post: 08-03-2008, 11:50 PM
  3. Need help quick with walk-in freezer issues!
    By hysiderafter in forum Commercial
    Replies: 5
    Last Post: 12-12-2007, 12:57 AM
  4. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM
  5. Project needs a freezer box.
    By NC-Joey in forum Fundamentals
    Replies: 14
    Last Post: 16-08-2007, 01:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •