    Cleaning the system after compressor burnout



    Do you need to remove and change the gad after a compressor burn out. The oil in the compressor passed a acid test.



  2. #2
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Cleaning the system after compressor burnout

    "Gad" I donīt know.

    As for the refrigerant yes I would, just for supersticious behaviour.

    I definitely would recover it and clean the system thoroughly. Having clean oil does not mean you have a clean high side! At least from compressor to the filter dryer.

    Only if the refrigerant passed a composition test I would think in reusing it.

    Not having acidity in the oil may mean that the test failed or the burnout was so fast that crankcase oil was not that much affected. With open compressors this would be nonsense.

    Anyway a change in compressor will change this oil.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cleaning the system after compressor burnout

    Quote Originally Posted by fdhealy View Post
    Do you need to remove and change the gad after a compressor burn out. The oil in the compressor passed a acid test.
    gad

    As service manager you should know answer to this question!

    You should recover refrigerant thru burn-out filter and then recharge it again thru burn-out filter, and it should be OK.

    Could be some concern about non-condensables in refrigerant.

    Of course, don't forget to put burn-out filter in liquid line and replace it after few hours of operation, with normal filter drier, if pressure drop at burn-out filter is OK. Also you should fit temporary suction line burn-out filter.
    Check this Copeland AE bulletin on Powell site for detailed procedure.
    Last edited by nike123; 26-06-2008 at 06:14 AM.

  4. #4
    Orlando's Avatar
    Orlando Guest

    Re: Cleaning the system after compressor burnout

    i'm back would you please post more articles I had my refs compressor change ( no burned out but it doesn't give the maximun coolness must I charge it with more *****

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Cleaning the system after compressor burnout

    Quote Originally Posted by Orlando View Post
    i'm back would you please post more articles I had my refs compressor change ( no burned out but it doesn't give the maximun coolness must I charge it with more *****
    A year since your last post and this time with a confusing question, I think
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2010
    Location
    usa
    Posts
    15
    Rep Power
    0

    Re: Cleaning the system after compressor burnout

    @GXMPLX fdhealy typo'd it is gas the s and d are next to each other .

    and yes you would need to change the charge and flush the system otherwise you will ruin your new compressor.

    i am not sure if a recycler can clean the charge after a burn out or if they have to dispose of it.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Cleaning the system after compressor burnout

    ^^ Two year old thread and OP wasn't polite enough to respond.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    229
    Rep Power
    15

    Re: Cleaning the system after compressor burnout

    Quote Originally Posted by ejonesss View Post
    and yes you would need to change the charge and flush the system otherwise you will ruin your new compressor.

    i am not sure if a recycler can clean the charge after a burn out or if they have to dispose of it.
    Any installer can clean the gas after a burn out if he has the correct method. So, he still can use the same amount of refrigerant after the cleaning process.

    Regards,

    Nando.

  9. #9
    Join Date
    Mar 2006
    Location
    Philippines
    Posts
    35
    Rep Power
    0

    Re: Cleaning the system after compressor burnout

    hello orlando, a lot of problem that can be associated to your inquiry, to begin with, is the compressor that was installed have the correct capacity to reject heat from its load?

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Cleaning the system after compressor burnout

    Quote Originally Posted by kaelte_technik View Post
    hello orlando, a lot of problem that can be associated to your inquiry, to begin with, is the compressor that was installed have the correct capacity to reject heat from its load?
    I would say that rejecting heat is task of condenser. Compressor has task to pump refrigerant in sufficient amount that evaporator is utilized as constructor of system intentioned.

  11. #11
    Join Date
    Mar 2006
    Location
    Philippines
    Posts
    35
    Rep Power
    0

    Re: Cleaning the system after compressor burnout

    Yes nike 123, what I meant is the capacity of the system itself to do this work which includes the comp and condenser. My apology for the wrong use of word.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions