Cleaning the system after compressor burnout
Do you need to remove and change the gad after a compressor burn out. The oil in the compressor passed a acid test.
-
25-06-2008, 10:43 PM #2
Re: Cleaning the system after compressor burnout
"Gad" I donīt know.
As for the refrigerant yes I would, just for supersticious behaviour.
I definitely would recover it and clean the system thoroughly. Having clean oil does not mean you have a clean high side! At least from compressor to the filter dryer.
Only if the refrigerant passed a composition test I would think in reusing it.
Not having acidity in the oil may mean that the test failed or the burnout was so fast that crankcase oil was not that much affected. With open compressors this would be nonsense.
Anyway a change in compressor will change this oil.
-
25-06-2008, 10:47 PM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Cleaning the system after compressor burnout
gad
As service manager you should know answer to this question!
You should recover refrigerant thru burn-out filter and then recharge it again thru burn-out filter, and it should be OK.
Could be some concern about non-condensables in refrigerant.
Of course, don't forget to put burn-out filter in liquid line and replace it after few hours of operation, with normal filter drier, if pressure drop at burn-out filter is OK. Also you should fit temporary suction line burn-out filter.
Check this Copeland AE bulletin on Powell site for detailed procedure.Last edited by nike123; 26-06-2008 at 06:14 AM.
-
26-06-2008, 01:04 AM #4
Re: Cleaning the system after compressor burnout
i'm back would you please post more articles I had my refs compressor change ( no burned out but it doesn't give the maximun coolness must I charge it with more *****
-
26-06-2008, 11:00 PM #5
-
17-11-2010, 08:20 PM #6
Re: Cleaning the system after compressor burnout
@GXMPLX fdhealy typo'd it is gas the s and d are next to each other .
and yes you would need to change the charge and flush the system otherwise you will ruin your new compressor.
i am not sure if a recycler can clean the charge after a burn out or if they have to dispose of it.
-
17-11-2010, 10:25 PM #7
Re: Cleaning the system after compressor burnout
^^ Two year old thread and OP wasn't polite enough to respond.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
18-11-2010, 07:30 AM #8
-
18-11-2010, 10:42 AM #9
Re: Cleaning the system after compressor burnout
hello orlando, a lot of problem that can be associated to your inquiry, to begin with, is the compressor that was installed have the correct capacity to reject heat from its load?
-
18-11-2010, 11:43 PM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
19-11-2010, 12:27 AM #11
Re: Cleaning the system after compressor burnout
Yes nike 123, what I meant is the capacity of the system itself to do this work which includes the comp and condenser. My apology for the wrong use of word.
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
Air conditioning system cleaning issue
By Lc_shi in forum Legal-Business-MarketingReplies: 2Last Post: 24-08-2006, 03:03 PM