    Two stage Sabroe



    I have been doing a survey today on an old Sabroe pack. The compressors are TSMC 116S and are running on R69L. The compressors are over twenty years old, does anyone have a manual for these? and how can i tell that my interstage saturated pressure is most efficent. I seem to remember there was a calculation for working out the interstage pressure, something like ''the squre root of the sst x sdt''. Any ideas and feed back would be most welcome.

    Ian



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Two stage Sabroe

    Quote Originally Posted by Ian B
    and how can i tell that my interstage saturated pressure is most efficient. I seem to remember there was a calculation for working out the interstage pressure, something like ''the square root of the sst x sdt''.
    The equation you are describing is not necasserily the most efficient, it just allows you to find the same pressure ratios for both compressors. The actual equation is square root of (Suction Pressure of the low stage compressor X Discharge pressure of the high stage compressor), where both pressures are in absolute.

    The most efficient point of operation is one that allows you to minimize the total power input. That might mean you raise the interstage pressure and lower the high stage discharge pressure.
    If all else fails, ask for help.


  3. #3
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Two stage Sabroe

    IanB
    easiest way is to plot the conditions you have on Coolpack and then play with the interstage pressure and keep checking the calculated COP.
    Ian

  4. #4
    Join Date
    Jan 2008
    Location
    Rickmansworth
    Age
    47
    Posts
    6
    Rep Power
    0

    Re: Two stage Sabroe

    Hi Ian,

    Yeah i tried Coolpack, but my version doesnt have R69L(R403B) in it. Does your version?

    Ian

Similar Threads

  1. r-23 low stage, cascade system
    By johnny1 in forum Refrigerants
    Replies: 8
    Last Post: 21-11-2009, 09:01 PM
  2. Building a 3 stage cascade
    By NoL in forum CPU Overclockers
    Replies: 9
    Last Post: 27-03-2009, 08:42 PM
  3. Single compression vs two stage compression.
    By Pawel_Wisnik in forum Technical Discussions
    Replies: 0
    Last Post: 07-09-2007, 01:53 PM
  4. Single stage Vs 2 stage comp rack
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 0
    Last Post: 01-02-2007, 03:05 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •