    P & I Diagram for Central Plant



    Though all are used to prepare the P & I Diagrams, ( generally based on some old diagrams etc.) , What is the correct way of doing things?
    We came across one Consultant from UK & he had laid some basic principles.
    1. Show the Equipments almost close to the actual installation in P & ID. Those may not be dimensionally matching , but locations should be clear enough for the site persons for doing the project eventually.
    2. Show Reducers etc on the pipings. The Bends etc may not be feasible to show, but Reducers can be definitely added.
    3. Work out the vessel sizes from theory & do not follow some catalog's for selection the vessel if possible.
    4. Make it as much clear as much possible showing all details.

    There must be similar points from others.

    I could check few P & ID from Europe, & these points were not followed.

    Even in Our P& ID many of the times these points are missing.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: P & I Diagram for Central Plant

    Here's a link to an article I wrote last year on the subject. It is a short article, but addresses some of the topics you are asking about.
    http://www.coldsystemsllc.com/concepts/pid-jan2007.pdf
    If all else fails, ask for help.


  3. #3
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: P & I Diagram for Central Plant

    Yes it is a very good article.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: P & I Diagram for Central Plant

    The issue with P&ID's is that a lot of people have never done one before, so they don't know what the requirements are. That is not a commentary on anyone's ability. This is just a difficult topic.

    First and foremost I feel a P&ID should show every valve, instrument, pipe, or control tubing run on any one component. Most people show a compressor as a picture with a suction and discharge line attached. Anyone who has seen a screw compressor package will realize there is a lot more to showing the instrumentation and piping than what typically is shown on many common P&ID's.

    I like to have the main component (say a vessel) to have a specific tag number. Let's use a tag number of V-100 as an example. This simply shows the vessel has a unique number in some sequence of other vessels.

    I usually label the inlet service (or block) valves as SV-100, which denotes service valve 100 as the valve controlling the flow into the vessel. The outlet block valve is labeled as SV-101. Using this method someone looking at the drawing will see that any valve with a number of -100 is an inlet valve, while any valve labeled -101 is the outlet valve. You can do the same thing for any major component so that this contributes to easier comprehension & learning for the people. It helps them to become intuitive with the system operation.

    To continue the logic I use, any valve associated with this same vessel would continue to use the same numbering sequence. You can label the Pressure Relief Valves as PRV-100 & PRV-101, while the main three-way valve under the reliefs is called SV-103. SV-103 is a main valve such as the -100 & -101 valves are.

    The way I view this method is: The main valves on any component should have a similar format so that anytime someone sees a valve on a drawing they can instantly tell it's purpose.

    If you develop and follow a system that makes sense then after sometime each drawing you do someone will be able to pick it up and fully understand exactly what it means, where the valves are at, and what they do.

    It's also possible to show the basic orientation of piping if the drawing is carefully laid out. If the flow is down by gravity show that on the drawing. If the flow is supposed to enter on the top of the main header show that. If the flow comes off of the bottom of a pipe, then show it that way. Some will simply take the pipe off of the bottom of the line because it is easier to show on the drawing, but it's confusing to read and does not help to instruct how the piping is designed or what is required.

    Too many people try to place too much information on a single sheet. Spread out the information onto multiple sheets if need be. I have worked on systems where the single P&ID for a screw compressor took an entire sheet.

    You can draw all the air-cooling evaporators for one room on a single sheet. Then you have sufficient area to place the necessary information for that room. Place the line continuation markers at a common location on the sheets and identify what they are for and where they go to the next sheet.

    Use a pipe code to identify size, wall thickness, material, etc. For example: 3-40-CS-B106 might be used to show the pipe is 3" nominal diameter with a Schedule 40 wall thickness in a carbon steel material of a grade B and seamless. That's useful information to have and during design this is easy to do. Not so easy after the job is finished...

    And... it helps to develop a block flow diagram so that you can follow the process quickly from point A to point B. This can be a single line drawing only.

    Hope this helps...
    Last edited by US Iceman; 25-06-2008 at 03:12 PM. Reason: spelling
    If all else fails, ask for help.


  5. #5
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: P & I Diagram for Central Plant

    Dear Us ICEMAN,

    Many thanks for the detailed reply. We too do similar things, but there is always a scope for improvement.

    We shall take cognisance of these points in future.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: P & I Diagram for Central Plant

    If you think about the P&ID's conveying information about the refrigeration system then you see the issue of trying to put as much information as possible on the drawings.

    One thing I also do is to put a schedule of the equipment on each sheet. In this schedule you can put some of the basic performance data for the components next to the tag numbers and basic descriptions.

    What I like to see is this; when I pick up a P&ID I want to be able to learn as much about the system as I can. All of this information is available during design, which is a good time to do this.

    When you see a P&ID that has pretty pictures of a side view of a screw compressor package you know a lot of the details are missing. This is just a pet peeve of mine. I don't mean to be lecturing anyone...
    If all else fails, ask for help.


  7. #7
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18

    Re: P & I Diagram for Central Plant

    Hi smpsmp45
    we use also a code for the equipements and we related all the instrumentation to the equipment

    The Ammoniac trap has the code XX for instance
    Then a pressure indicator has the XX PI 001 and a relive valve for the ammonia trap is XX PRV 001

    It is very helfully for a main central control


    Regards
    Gwapa

  8. #8
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: P & I Diagram for Central Plant

    I think on this forum we should come together to form the basic guidelines for P & ID based on these inputs.

    US ICEman had sent a paper earlier written by him. Now we need to extrapolate on that further.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: P & I Diagram for Central Plant

    Quote Originally Posted by gwapa
    Then a pressure indicator has the XX PI 001 and a relive valve for the ammonia trap is XX PRV 001
    That's the sort of logic I like. The tag relates to the specific component, the valve itself, and a unique number. Having the instrument tags arranged with this or a similar order helps to provide information on the control addresses for ease of location also.

    I also like to see something for the control loops on the drawings. For example: a float switch controls a liquid line solenoid valve. A solid line connecting the float switch and solenoid shows the two are related in function. It's also common to use a different symbol for local or remote mounted instrumentation.

    The amount of information you can read from a well developed P&ID is worthwhile to help understand the system.
    If all else fails, ask for help.


  10. #10
    Join Date
    Mar 2007
    Location
    UAE
    Age
    43
    Posts
    78
    Rep Power
    18

    Re: P & I Diagram for Central Plant

    Here's a link to an article I wrote last year on the subject. It is a short article, but addresses some of the topics you are asking about.
    http://www.coldsystemsllc.com/concepts/pid-jan2007.pdf


    Dear sir,

    Can you pls send this file to my following id:

    jkumar@fanargroup.ae

  11. #11
    Twotone's Avatar
    Twotone Guest

    Re: P & I Diagram for Central Plant

    The article link in no longer working. How may I get a copy to read?

Similar Threads

  1. Single stage refrigeration system optimizing diagram
    By autt in forum System Optimization
    Replies: 34
    Last Post: 03-12-2008, 03:13 PM
  2. Tube Ice Plant -Ammonia
    By tjk2007 in forum Industrial
    Replies: 3
    Last Post: 25-04-2008, 09:41 PM
  3. Refrigeration plant Hydro test
    By psrao in forum New Technologies
    Replies: 17
    Last Post: 09-04-2008, 12:05 AM
  4. Soap Plant Load Calculations
    By tjk2007 in forum Fundamentals
    Replies: 0
    Last Post: 25-11-2007, 05:59 AM
  5. project of refrigeration plant
    By gesi in forum Fundamentals
    Replies: 5
    Last Post: 12-06-2006, 07:13 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •