    supposedly a testing company has found lead in the refrigerant (low temp). The mechanicals were all experienced so I don't believe they used lead solder. Anyone have an idea where the lead might come from?



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Lead in refrigerant

    You did not really give us much information to use. What type of:
    1. compressors do you have?
    2. piping material is used?
    3. refrigerant is it?
    Is this the first time you have noticed lead, or is this the first time you have checked?

    and,

    What were you testing? The oil perhaps?
    If all else fails, ask for help.


  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Lead in refrigerant

    Also, the use of the word "Supposedly".

    Did they or didn't they ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    luv2golf's Avatar
    luv2golf Guest

    Re: Lead in refrigerant

    Sorry,
    Copeland Discuss
    R-22 (new when put in, not reclaim)
    Copper pipe

    5 ppm lead (not much but still, where did it come from)

    Moisture was at 77 ppm with white sludge.

    sounds like a serviceman breached the system

    Been operating for 1 1/2 yrs. Warr out after 12 months, different company servicing.

    thanks

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Lead in refrigerant

    If soft solder was not used, then what you may be seeing is residue material from compressor bearings.
    If all else fails, ask for help.


  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Lead in refrigerant

    Luv2golf
    As Iceman indicates it could well be from your "white metal" Bearings as these are generally an alloy of Lead and Tin.
    So especially as you state this Compressor has worn out after 12 months.
    Due in part to huge Copperisation no doubt?
    Based on the moisture content you quote.
    Grizzly

  7. #7
    Join Date
    Jan 2009
    Location
    USA
    Posts
    79
    Rep Power
    16

    Re: Lead in refrigerant

    I've come across the white metal from worn bearings a lot-you'll find the sump oil strainer blocked with this stuff if it's bad enough. Better find out why it's wearing bearings so quickly if it's a relatively new compresser.
    A lot of the stores here have 20+ year old stuff.
    This

  8. #8
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Lead in refrigerant

    Missed this thread when it first came out.
    I had a oil analysis done on a Frick Screw years ago and it came back with some strange things in it. The Frick Factor could not explain it. Then one day it dawned on me-Anti-Seize. Lots of stuff can be in that can.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  5. Refrigerant Reclamation
    By herefishy in forum Commercial
    Replies: 6
    Last Post: 23-07-2003, 08:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •