    My company is planning to construct a 22000 cubic meter cold store to store 8000 MT (2 stores of 4000 MT each) of frozen fish at -20 degree celcius. Ambient temp is 35C and RH 65%. Can anybody suggest me the best suitable type of refrigeration and brand of equipmet for this project which is readly available.
    Cheers..
    Lal Thomas
  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Re: Construction of new Cold Store
    We have to ask, "What is the available equipment in Nigeria?"
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,699
    Rep Power
    46
    Thumbs up Re: Construction of new Cold Store
    Quote Originally Posted by lalthomas View Post
    Hi guys,
    Cheers..
    Lal Thomas
    Welcome Lal.
    None of the engineers on this forum will (nor should they) specify a particular manufacturer.
    As the forum then becomes a sales tool for whoever anyone works for. Which destroys the whole object of this forum!
    If Companies wish to advertise then they should speak to the boss Webram!
    Personally though with a project of that size I would recommend an Ammonia Plant.
    Cheers Grizzly
  4. #4
    Join Date
    Jan 2008
    Location
    Nigeria
    Age
    48
    Posts
    5
    Rep Power
    0
    Thanks.. We are looking for global sourcing. Infact there is nothing available in Nigeria. One company represents Sabroe and some other small firms, but everything has to come from outside.
  5. #5
    Join Date
    Sep 2006
    Location
    Venezuela
    Posts
    259
    Rep Power
    18
    Dear lalthomas
    I´m working in a cold store at -28°C plus dock area
    40 mx40m x 12m =20000m3
    The cold store will be located in a urban area so we selected R404A. May be if it will be located outside the city you could use ammonia
    We are using a rack of 5 compresor (screw) with economixer
    Regards
    Gwapa
  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,699
    Rep Power
    46
    Quote Originally Posted by gwapa View Post
    Dear lalthomas
    Regards
    Gwapa
    GWPA
    I assume by this statement.
    You don't work with Ammonia?
    Grizzly
  7. #7
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17
    Dear Mr lal,
    If your project is coming outside the city, I prefer ammonia based with liquid recirculation plant. If the plant in the city you prefebly go with R404A refrigerant.
    I have much experience in Ammonia plants.
    raj
  8. #8
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17
    We had done a project in Nigeria & have given offers to few more. If you can PMS me,. we can discuss it further
  9. #9
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17
    Dear Mr. Lal,
    We are using Screw as well as Reciprocating compreesor for the same based on ammonia.
    You can use private message service.
  10. #10
    Join Date
    Jan 2008
    Location
    Nigeria
    Age
    48
    Posts
    5
    Rep Power
    0
    Mr Gwapa,
    Thanks for the information. Our plant too is within the city only.
  11. #11
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37
    why not go really eco-freindly and try CO2 low stage and 404a high side, CO2 is readily available, plus super efficient and inexpensive.
    magoo
  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25
    What's not eco-friendly about ammonia?
    If all else fails, ask for help.
  13. #13
    Alberrto Mayer's Avatar
    Alberrto Mayer Guest
    Dear Laltomas
    I strongly suggest you to use ammonia and a pump recirculation system. To be located inside a city is no reason for not using that refrigerant, which besides of being natural is very efficient. There are many contractors available to built a plant using that refrigerant under safety conditions.
    Looking the ambient temperature and relative humidity you are able use evaporative condensation operating at 35gradC , assuming you have fresh water available.
    Best Regards
    Alberto Mayer
  14. #14
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20
    Nothing wrong with ammonia in a city, provide is it is installed and operated correctly. As for equipment, the larger players are Frick, FES-GEA and Mycom. There are number of others such as Sabroe (owned by York last I heard), Vilter and Hasegawa.
    Generally the way to build a plant is to hire a consultant to develop your specifications and go out for bids on the whole facility and select a general contractor who will work with one or several refrigeration contractors. You can have some input as to the acceptable manufacturers.
    A good consultant wil; be familiar with the equipment and manufacturers and where they best fit.
    Ken
  15. #15
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37
    I readily and totally agree with using ammonia within a city application. But in Nigeria, where everything is outsourced and probably includes serviceing. Currently working in Asia, a country light years ahead in technology by comparison. Given the huge enthusiasom, not the language problem. I am having a lot of greif, and it is in a city enviroment to boot.
    Now do you all begin to understand my earlier post ?.
    Open for more comment please.
    Magoo
  16. #16
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31
    Hi, lalthomas
    ... everything is very simple...
    ... you have to import everything.... assume that cold store isn't within downtown ... then ammonia is the best ... of course you must follow safety regulations regarding ammonia ....
    ... good advice is this ...
    Quote Originally Posted by TXiceman
    .... my advice .... stay away of cheap offers... you not need a bad cold store, but good, long lasting one ....
    if still in doubt .... put a question here ....
    Best regards, Josip
    It's impossible to make anything foolproof because fools are so ingenious...
    Don't ever underestimate the power of stupid people when they are in large groups.
    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.
  17. #17
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37
    has any of the participants in this post actually worked internationally, outside your comfort zone, and a long way from your computer room.
    Hands-up those that listen to international news reports. Not-a-lot I think, [outside your comfort zone ].
    Nigera is the kidnap for ransom capital in the world, Oil companies have left the place, corruption is rampant, the country is bankrupt, add that most internet scams start in Nigeria.
    Get the big picture.
    A collegue was there for 2 months, he muttered alot,shook continually and dribbled alot, when he got home. After RR he said " nightmare on elm street" was a walk in the park by comparison. Sleeping with hand gun, with one eye open and in a compound similar to a prison with the prisoners on the outside. Armed guards at all times, and shelling out money [USD] constantly to get things done, his company lost their shirt on the whole experience.
    magoo
  18. #18
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25
    I know at least on the participants in this thread has traveled to many locations for work. It would be interesting to see the viewpoints of others on this subject (perhaps by starting a new thread, which I will do).
  19. #19
    Join Date
    Jun 2006
    Location
    jiansu
    Posts
    38
    Rep Power
    0
    I think the ***** system is suitable.
  20. #20
    Join Date
    Apr 2006
    Location
    Canada
    Age
    53
    Posts
    154
    Rep Power
    19
    Lalthomas,
    Check your Private Messages.
  21. #21
    chill2freeze's Avatar
    chill2freeze Guest
    We are constructing a cold storage in India with total storage capacity of 8000 tons of potatoes. we invite suggetions and views of our friends on RE to assist and quote us for the same
  22. #22
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20
    chill2 freeze...I will repeat the same answer for you and I strongly urge you to hire a qualified consultant rather than try to poor-boy it and depend on some unqualified contractors.
    A good consultant will be familiar with the equipment and manufacturers and where they best fit.
    Ken
  23. #23
    Join Date
    Feb 2008
    Location
    Buenos Aires
    Posts
    8
    Rep Power
    0
    we had experience in bulk potaitos storage and we con do all the specificatiiosns and supply since Argentina
    See our page arceyasociados(dot)com(dot)ar and if want contac wit me
    Ing Luis M, Arce
  24. #24
    Join Date
    Feb 2008
    Location
    Buenos Aires
    Posts
    8
    Rep Power
    0
    we are a engeeniering grup that are doing cold rooms in a turn key systems. At this time we are doing a complete plant in Buenos Aires for 4000 pallets of 1000 Kg each of fried poates frozen ( -25ºC) 80 meters lenght, 30 meters wide and 14 meters hight. We did 20 years ago a frozen fish walk in cooler in ABBA. If yo want see our page arceyasociados(dot)com(dot)ar and contact wtih me in arceyasociados(arroba)arceyasociados(dot)com(dot)ar
    regards Luis M. Arce
Similar Threads
  1. Replies: 15
    Last Post: 17-06-2008, 11:07 PM
  2. Expansion Joints in the cold store floor
    By smpsmp45 in forum NH3
    Last Post: 17-05-2008, 07:47 AM
  3. Cold Store Racking Design
    By Ashley in forum Ye Old Wifes Tales
    Last Post: 06-12-2007, 10:58 PM
  4. Low Temperature Cold Store
    By iceman007 in forum Commercial
    Last Post: 16-11-2005, 11:23 PM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts