Had quite a few call outs (about 4 in the last 2 months) for inverter split systems not working. These have ranged from Daikin, Mitsubishi and now Panasonic. All of these systems have so far been the victims of Gecko's crawling into the outside control board enclosure and getting fried by the high voltage produced in these systems.
The Daikin in particular almost went up in flames, with almost complete destruction of the board (and the gecko), luckily no other components or plugs were damaged.
The latest suspect is a Panasonic Inverter (CU-E9CKP5) It is giving an error code "F90" and corresponds to "Power Factor Protection".
I went outside and took a look and a cockroach had made it's home under one of the IC's bridging out two of the legs, but it had not fried, nor could I determine that it had been burnt due to the natural crispness and colour of the cockroach - although it's head did seem to be missing...
I removed the offender and tried the AC again, still comes up with the same error code.
Nothing else on the AC looks suspect, I'm on the verge of ordering a new card but just thought I'd see if anybody would know where the Power factor correction circuitry would be... I assume the outside board cause of the ****y, but I could be wrong.
Cheers for any help and has anybody else had problems with wildlife with these inverters running high voltage? If not why me?!
Sorry bout the essayLast edited by Brian_UK; 18-06-2008 at 08:40 PM. Reason: Overcame the board censor :-)
-
18-06-2008, 12:07 PM #2
Re: Panasonic inverter -Power factor protection
Yep lots of them up here,
Pretty common to see geckos and lizzards fried on the outdoor p.c. boards.
Mice/rats normaly like to craw up the paired coil when the hole isn't sealed and chew the crap out of the indoor wiring.
Even heard that the fugitsu inverters make the same sound as a mating green tree frog that attracts them, and yes again, get fried on the outdoor p.c. board. What a way to go. Under warranty of course.If I can make more than my wife can spend in a day, that's a good day....
-
25-06-2008, 07:54 AM #3
Re: Panasonic inverter -Power factor protection
I referred this customer to a panasonic dealer.
I rang panasonic and they would not give me any info.
-
28-06-2008, 01:17 PM #4
Re: Panasonic inverter -Power factor protection
The latest suspect is a Panasonic Inverter (CU-E9CKP5) It is giving an error code "F90" and corresponds to "Power Factor Protection".
F90=PFC control=• Voltage at PFC
Check you have correct voltage 240V ?
Replace Board ..
Replaced a few with the same problem ,
nothing visable anywhere but the board was dead...
Similar Threads
-
Testing Inverters
By fridge doctor in forum Air ConditioningReplies: 38Last Post: 15-06-2011, 06:52 AM -
Panasonic Inverter
By wat180 in forum Air ConditioningReplies: 3Last Post: 13-05-2008, 06:13 PM -
SR2 50 models electric SBY diagonostics made simple
By absolute-zero in forum TransportReplies: 5Last Post: 04-01-2008, 05:11 PM -
Panasonic air-con inverter unit
By Baron in Spain in forum Air ConditioningReplies: 4Last Post: 04-12-2007, 11:34 AM -
NEW 3-Phase IGBT Inverter Power IC
By theberes in forum New TechnologiesReplies: 14Last Post: 01-03-2004, 01:10 AM