    PHE Evaporator



    Can we use Dx type PHE Evaporator for chilling water.



  2. #2
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: PHE Evaporator

    Can we use Ammonia Dx PHE?

    Raj

  3. #3
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: PHE Evaporator

    Hi Rajkumar
    Yes you can.
    I have seen them on ***** systems.
    They had mechanical or electronic type TX valve fitted.
    I haven't seen the NH3 one using at TX but have seen PHE connected to a pumped liquid system using a hand expansion valve instead of the TX.
    There was a recent post about this and I think it was sated thad the PHE has to be constructed to suit a TX valve.
    Paul

  4. #4
    Join Date
    Nov 2007
    Location
    India
    Age
    46
    Posts
    74
    Rep Power
    17

    Re: PHE Evaporator

    I have seen it in Mycom screw package catalouge

  5. #5
    Join Date
    Jun 2002
    Location
    Mumbai, India
    Age
    66
    Posts
    25
    Rep Power
    0

    Re: PHE Evaporator

    Rajkumar,
    There have been large scale failures when PHEs were used in India for chilled water application - reason being water containing dirt and dust clogs the very narrow passages resulting in low chilled water flow which leads to freezing of water in the PHE.
    And as the brazed PHE can't be repaired you just have to throw it away. Carrier Aircon had introduced compact chiller using PHEs as condenser and chiller and used to advertise it as a 40 Ton chiller on castor wheels which you can easily transport through an ordinary lift. The product was withdrawn from the market.

    A handful of installations using PHE as chiller have been successful. Some tips - use GI piping and elbows, instal an evaporator pressure regulating valve to ensure the evaporation pressure does not go below 27 Deg. F and maintain a clean system.

    Also flooded PHEs can be used for ammonia as DX ammonia system can be very tricky (oil return problems).

  6. #6
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: PHE Evaporator

    Hi S.M. Gokhale
    We have installed many PHE chilling either water or brine and have had no major problems with PHE's failing due to freeze up as all PHE's have a flow switch and an anti-freeze thermostat fitted. We also run the pump on for about 5 minutes after the call is lost.
    An EPR valve is also a good idea if you are running other lower temp evaporators on the same system.
    I presume by GI you mean galvanized iron pipe, if so I would not recommend the use of GI pipe, as the internal galvanizing can be destroyed by electrolysis and will rust from the inside out. This rust will also end up in the PHE and block it.
    We would only stainless steel, copper or PVC.
    Also S/S PHE's are susceptible to damage from high levels of Chlorides in the chilled solution.
    Paul

  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: PHE Evaporator

    PHE are the most common in laser cutting machines, used to cool the water for laser lamps,
    I maintain two factories and we don't have any problems except a probe that went crazy and the PHE froze and had to be replaced.

    For maximum protection, a HGBP can be fitted to protect it from freezing, make sure that probes, flow controls and the low pressure stat are checked on regular bases.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Absortpion Refrigeration - Evaporator Basics
    By knudo in forum Fundamentals
    Replies: 4
    Last Post: 28-08-2007, 08:03 AM
  3. What is the best location for a evaporator fan?
    By Jasno999 in forum Fundamentals
    Replies: 3
    Last Post: 21-02-2007, 12:34 AM
  4. Replies: 3
    Last Post: 06-11-2006, 05:04 AM
  5. Change evaporator
    By tralex in forum Fundamentals
    Replies: 6
    Last Post: 29-12-2005, 07:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •