    Expansion valve tips



    Found this im sure it will be of use.Although i disagree with the adjustment of the tev
    http://odeo.com/audio/15899933/play


    Transvestites are men who like to eat, drink, and be Mary.

  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Expansion valve tips

    Thanks for sharing Phil, i'll have a read.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Expansion valve tips

    Sorry Phil, I got a dead link there.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Expansion valve tips

    Last edited by philfridge; 24-06-2008 at 12:23 PM. Reason: added
    Transvestites are men who like to eat, drink, and be Mary.

  5. #5
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Expansion valve tips

    Quote Originally Posted by philfridge View Post
    Found this im sure it will be of use.Although i disagree with the adjustment of the tev
    http://odeo.com/audio/15899933/play
    phil,

    Okay, you must be looking for a debate.

    Why do you disagree with the adjustment statement?

  6. #6
    Join Date
    Apr 2008
    Location
    Gosport Hants
    Age
    63
    Posts
    24
    Rep Power
    0

    Re: Expansion valve tips

    superb site and just at my Amature level many thanks for that one.

    Got any more ??

    pom

  7. #7
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Expansion valve tips

    If only it was that easy. Ever heard of a searching expansion valve? Want to occupy yourself for many hours? Just sit there and watch a valve in the real world do it's thing.
    What a mess!!! The superheat goes down to 3 or 4 degrees then slowly rises to around 12 to 15 degrees. Then begins to repeat the cycle.
    Over and over and over it goes. It never settles on one value and stays!!!
    So, what's you superheat? Who the heck knows!!! Take your pick! Take an average! Flip a coin! Throw darts at a chart!
    Want to know the dirty little secret? Who cares!!! Want to know what really important?

    Pay attention to the compressor!!! It will tell you what you need to know about the superheat.
    Assuming the rest of the system is operating normally, the compressor on a medium temp system should have a moderately cool suction bell around the suction line.
    That's it!!!
    If the compressor body is sweating or cool up to the heads, superheat too low. If the suction line is warm at the compressor, superheat too high.
    The whole idea of superheat is to get just the right amount of refrigerant into the evaporator.
    Too much, it floods back and damages the compressor. Too little, you starve the evaporator, losing cooling capacity. Simple, simple, simple, that's my motto. Keep that refrigeration repair simple.
    Last edited by philfridge; 24-06-2008 at 03:58 PM.
    Transvestites are men who like to eat, drink, and be Mary.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Expansion valve tips

    Quote Originally Posted by philfridge
    Pay attention to the compressor!!! It will tell you what you need to know about the superheat.
    ...
    If the compressor body is sweating or cool up to the heads, superheat too low. If the suction line is warm at the compressor, superheat too high.
    Finally. A voice of sanity in the wilderness.

    I like the way you think. If the system load changes are relatively stable (and most are if they are designed right) you can watch what happens at the compressor. I mentioned something like this in another thread. Depending on the operating conditions you can quickly determine how well the TXv's are operating by looking at the compressor.

    I am beginning to think we should have locks on TXV's to keep them from being adjusted...


    This debate will continue ad nauseum because of a simple little thing like superheat.
    If all else fails, ask for help.


  9. #9
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Expansion valve tips

    Quote Originally Posted by philfridge View Post
    If only it was that easy. Ever heard of a searching expansion valve? Want to occupy yourself for many hours? Just sit there and watch a valve in the real world do it's thing.
    What a mess!!! The superheat goes down to 3 or 4 degrees then slowly rises to around 12 to 15 degrees. Then begins to repeat the cycle.
    Over and over and over it goes. It never settles on one value and stays!!!
    So, what's you superheat? Who the heck knows!!! Take your pick! Take an average! Flip a coin! Throw darts at a chart!
    Want to know the dirty little secret? Who cares!!! Want to know what really important?

    Pay attention to the compressor!!! It will tell you what you need to know about the superheat.
    Assuming the rest of the system is operating normally, the compressor on a medium temp system should have a moderately cool suction bell around the suction line.
    That's it!!!
    If the compressor body is sweating or cool up to the heads, superheat too low. If the suction line is warm at the compressor, superheat too high.
    The whole idea of superheat is to get just the right amount of refrigerant into the evaporator.
    Too much, it floods back and damages the compressor. Too little, you starve the evaporator, losing cooling capacity. Simple, simple, simple, that's my motto. Keep that refrigeration repair simple.
    If an expansion valve periodically oscillates in superheat, the valve is hunting.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Expansion valve tips

    Quote Originally Posted by philfridge
    Ever heard of a searching expansion valve?

    Quote Originally Posted by star882
    If an expansion valve periodically oscillates in superheat, the valve is hunting.
    Why repeat the same thing that philfridge mentioned? All you did was use different words.
    If all else fails, ask for help.


  11. #11
    Join Date
    Nov 2005
    Location
    USA
    Posts
    211
    Rep Power
    19

    Re: Expansion valve tips

    Quote Originally Posted by US Iceman View Post
    Why repeat the same thing that philfridge mentioned? All you did was use different words.
    In a properly operating system, the valve should not hunt.
    "If Hannah was an air handler, I would be a condensing unit so I could open her TXV and pump my refrigerant through her coils." - a HVAC friend of mine

  12. #12
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Expansion valve tips

    phil,

    I remember those days. The only superheat gauges we had were in a kit with two brass dial gauges, I think made by Marsh.

    They would peg out sitting in my hot van. Had to use ice water to re-calibrate them, what a pain.

    A Copeland engineer, now gone, use to teach in his class that the compressor belly should feel the same as a babies butt.

  13. #13
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Expansion valve tips

    Quote Originally Posted by US Iceman View Post

    I am beginning to think we should have locks on TXV's to keep them from being adjusted...

    Powell, take note.

    This is a brilliant idea and should not be frowned upon. This is because the TEVs are factory set and do not need to be messed about with. All Fridge Engineers need to check the whole system thouroughly before blaming the TEV as they seldom never go wrong or need adjustment ! . US iceman you have my vote.
    Transvestites are men who like to eat, drink, and be Mary.

  14. #14
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Expansion valve tips

    Quote Originally Posted by philfridge View Post

    Powell, take note.
    Take note to what?

    I agree with the comments made.

    powell

  15. #15
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: Expansion valve tips

    Quote Originally Posted by powell View Post
    Take note to what?

    I agree with the comments made.
    Oh sorry powell,
    Glad to see you on my side
    Transvestites are men who like to eat, drink, and be Mary.

  16. #16
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Expansion valve tips

    Quote Originally Posted by philfridge View Post
    The whole idea of superheat is to get just the right amount of refrigerant into the evaporator.
    Too much, it floods back and damages the compressor. Too little, you starve the evaporator, losing cooling capacity. Simple, simple, simple, that's my motto. Keep that refrigeration repair simple.

    Think you meant it the other way round ...large superheat starved evaporator. Small superheat risk of flooding back.

  17. #17
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Expansion valve tips

    i am generally on side with all you guy/galls ref tev's & the inherent problem with the tech man who 'insists' during a service call or maintenance to give the valve a 'tweek', its likes boys continually having a fumble whilst watching bay watch!

    what i would add further is that the adjustment screw is there for a purpose!

    it should be set during comissioning, to match the valve & orifice to the particular application. Then left.

    Billy Ray

  18. #18
    Join Date
    Dec 2002
    Location
    South Africa
    Age
    83
    Posts
    41
    Rep Power
    0

    Re: Expansion valve tips

    In my 20+ years service in refrigeration I have only had to adjust a TEV about 5 times and that was because the guy before me had adjusted the thing. My dad always said "If there is a screw with a spring. Leave it!" although he was refering to a carburetor at the time.

  19. #19
    Join Date
    Jan 2008
    Location
    Norfolk - England
    Posts
    95
    Rep Power
    17

    Re: Expansion valve tips

    Lets look at this from a different angle,

    These are 'made-up' figures for discussion purpose only.

    We select a cooler for an application, balanced against a condensing unit etc.

    At design conditions the cooler has a cooling capacity of 4.5kW.

    We now select a Ex. valve to match.

    Lets say a danfoss TE2.

    A No.2 orifice provides 3kW
    A No.3 provides 4kW
    A No. 4 provides 5kW

    etc, etc.

    Which one do we choose? And do we adjust it?

    Or do we look for another manufacturer which valve does 4.5kW & do not adjust?

    Billy Ray

  20. #20
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Expansion valve tips

    Hello Billy Ray

    I would choose the No4, but I would check the pressure drop accross the valve for the actual duty at the actual pressure drop.

    The No4 will probably need turned in a little when the load settles, dependant on actual pressure drop and subcooling.


    Kind Regards Andy D
    If you can't fix it leave it that no one else will:rolleyes:

  21. #21
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Expansion valve tips

    Quote Originally Posted by Billy Ray View Post
    We now select a Ex. valve to match.

    Lets say a danfoss TE2.

    A No.2 orifice provides 3kW
    A No.3 provides 4kW
    A No. 4 provides 5kW

    etc, etc.

    Which one do we choose? And do we adjust it?

    Or do we look for another manufacturer which valve does 4.5kW & do not adjust?

    Billy Ray
    Well lets go for the No. 3 as Danfoss TEV’s have a + 25% capacity so this unit will do the job admirably. Thing is though, I think we’re all getting side tracked about duty and evaporator capacity etc. It’s the bulb that determines the temperature and superheat value at the point where the bulb is located!

    The TEV is factory set , and will work at that value regardless of where the bulb is located. If you install to the perfect layout with the bulb and pilot line in the perfect place then the TEV should give you the perfect super heat. But we know this never happens and the bulb could be further away from the evaporator than the factory anticipated, thus the evaporator is prone to flood and carry over. Conversely the closer we position the bulb the more likely the evaporator will not be fully utilized and duty of the coil is likely to be reduced.
    In this situation surely then you would need to adjust the little screw. Opening it up to increase capacity and reducing it to restrict liquid flow. Iether way to maximise the capacity of the evaporator.

Similar Threads

  1. Expansion Valve Selection
    By raviperumal in forum Technical Speculations
    Replies: 12
    Last Post: 17-02-2010, 09:58 AM
  2. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Replies: 4
    Last Post: 08-06-2008, 06:52 PM
  3. Fitting an expansion valve question
    By Larry2 in forum Air Conditioning
    Replies: 20
    Last Post: 08-04-2008, 04:17 PM
  4. Expansion Valve
    By MILLWALL in forum Trouble Shooting
    Replies: 8
    Last Post: 28-09-2007, 07:13 PM
  5. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •