    Replaced water condensor



    I recently removed a water coil and replaced it with a air-cooled condensor on a air conditioner.The compressor is inside the building.It is a capilary system so I charged it with the superheat method with a chart I found online.75f ambient,50psi suction,line temp 30f.After running for quite a while the lines freeze-up and the top of the compressor is very cold.The A-coil lines are frozen also.I can't see the finned side of the coil to see if it is frozen over.Head pressure is 250psi at the compressor.The pressure returning from the outdoor condensor going to the a-coil is 180psi.Is this pressure too low?Do I need to put a cycling switch for the condensor fan?Is my charging method flawed?



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Replaced water condensor

    Hi Cretan
    Tricky one here, The head press should be rule of thumb - 18-21 K above the air on. A recent job I've seen where water was changed for air is 5 dead compressors on a unit with 3 comps. So I think floodback prevention is required. As for the charge you can go on superheat and current draw.
    Good luck

  3. #3
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: Replaced water condensor

    thanks for the reply.I checked the furnace filter and it was dirty.I cleaned it and am running the unit now.Will find out soon if that was the problem.So is 180 too low pressure after the condensor?

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Exclamation Re: Replaced water condensor

    Quote Originally Posted by cretan View Post
    So is 180 too low pressure after the condensor?

    That depends on outdoor ambient temperature.
    What is your outdoor temperature in moment of taking pressure reading?

    The real problem is big pressure diferential from compressor discharge (250PSI-180PSI=70PSI) to point where you measured 180 PSI. If that is measured after liquid line filter-drier, You should change filter drier and then see what pressure difference it is. If that is measured before filter, than your piping is not properly done/selected or you have to long pipes.
    Last edited by nike123; 17-06-2008 at 07:17 PM.

  5. #5
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Replaced water condensor

    I agree with nike123. the pressure drop doesn't make sense with that kind of drop the drier should be cold to the touch.
    Last edited by wambat; 17-06-2008 at 07:44 PM.

  6. #6
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: Replaced water condensor

    What is your outdoor temperature in moment of taking pressure reading?
    Was 75f when I took the reading.reading was before the drier.drier is after the condensor.

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 06:19 PM
  3. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •