    Walk In freezer,r404



    Ok. Ill start with the box. Approx 8'x8'x8'. The system is a 5.5ton techumseh based. (aw series, rotolock 6500 btuh,low temp, high starting torque 3 phase) Overpowered to say the least. Anyway, the compressor failed after 15 yrs of service. I attribute the failure to repeat overheats due to faulty condenser fan connection, and clogged, undersised filter drier, coupled with outside temps in excess of 100 degrees. (south carolina) The box is located in a kitchen, with no walls exposed to outside. Said kitchen is at 88 degrees f. I replaced the compressor with the cross referenced 6100 btuh that techumseh recomends, which is still 5 tons-plenty.My current problem is that i cannot get the unit below 20 degrees, and i think I know why.I charged the empy unit to a head pressure of 275 psi. this put my suction at about 30, which corresponds to about 10 f. It instantly (20 min) pulled the box down to about 20 f. Came back next day. SAme. Put a thermometer on the suction line now, as i like to check superheat after unit has cooled awhile. Temp was 57 f. this line has no insulation on it, but also no ice. I think my solution is to insulate the pipe, and charge to a 20 degree super. That will probably put my coil temp up about 20 degrees, as well as my head pressure up 50+psi. So my hope is that with the correct superheat(20-40 for r404 at compressor) I will have a saturated evap coil which will pull down the air temp, and head pressure, respectively. Sound right to you guys? This is only my second low temp 404 application, and I'm hoping to call on your experience, as my background is in heat pumps, natural gas, and medium temp.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Walk In freezer,r404

    Is this system with TEV or with capilary tube?

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Walk In freezer,r404

    Same thought Nike 123 but this is difficult to read.

    Ohhh, welcome from Belgium.

    If you post a question with the units you’re used to work with, place between brackets the other units. So if you normally work with SI units (bar, °C, m³/h..), place then between these units the proper IP units.

    You can do the conversion with a free software program Uconeer
    You can find it on http://www.katmarsoftware.com/uconeer.htm#download
    Or you can use the spreadsheet of Dan posted on http://www.refrigeration-engineer.co...0617#post50617 post 6.

    Otherwise, your post will not be read by many members.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Jun 2008
    Location
    South Carolina
    Age
    52
    Posts
    18
    Rep Power
    0

    Re: Walk In freezer,r404

    txv....................

  5. #5
    Join Date
    Jun 2008
    Location
    South Carolina
    Age
    52
    Posts
    18
    Rep Power
    0

    Re: Walk In freezer,r404

    txv? wait hmmmmm... that could be a problem hmmm

  6. #6
    Join Date
    Jun 2008
    Location
    South Carolina
    Age
    52
    Posts
    18
    Rep Power
    0

    Re: Walk In freezer,r404

    Nope ,no balance tube, no bulb, its either piston or cap tube. I dont want to open evap case if i dont have to.

  7. #7
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Walk In freezer,r404

    R404 wasn't widely in use 15 years ago?

    What gas was system originally on?

    Expansion device incorrect for gas?

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Walk In freezer,r404

    Quote Originally Posted by johnanthonyhome View Post
    Nope ,no balance tube, no bulb, its either piston or cap tube. I dont want to open evap case if i dont have to.
    Do you have sight-glass? I think that you should open evaporator case and measure capillary length and diameter or find data about expansion device. What was full model name of old compressor?
    Last edited by nike123; 15-06-2008 at 04:05 PM.

  9. #9
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    16

    Re: Walk In freezer,r404

    If I understood your last post you said the txv has no equaliser pipe or bulb making an automatic expantion valve completly unsuitable for low temperature work as there is no compensation for evap pressure drop and works much like a cappillary tube.Throw this away and replace it with an externally equalised txv.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Walk In freezer,r404

    Quote Originally Posted by casstrig View Post
    If I understood your last post you said the txv has no equaliser pipe or bulb making an automatic expantion valve completly unsuitable for low temperature work as there is no compensation for evap pressure drop and works much like a cappillary tube.Throw this away and replace it with an externally equalised txv.
    If you did not observed, this system has worked 15 years? And compressor has failed. Now we need to find reason why. I doubt that design problem will be hidden 15 years without damage.

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Walk In freezer,r404

    Quote Originally Posted by johnanthonyhome View Post
    Nope ,no balance tube, no bulb, its either piston or cap tube. I dont want to open evap case if i dont have to.
    Hello Johnanthonyhome

    are you getting subcooling on the liquid line?

    What is your head pressure like?

    Is the new compressor man enough?

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Walk In freezer,r404

    Quote Originally Posted by johnanthonyhome View Post
    Nope ,no balance tube, no bulb, its either piston or cap tube. I dont want to open evap case if i dont have to.
    Piston or cap tube, learning every day.
    What's a piston ?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  13. #13
    Join Date
    Jun 2008
    Location
    South Carolina
    Age
    52
    Posts
    18
    Rep Power
    0

    Re: Walk In freezer,r404

    a piston is a drilled orifice, in a cylindrical piece of brass, hence the term piston. It fits into a cup which is soldered to coil feed tubes. The liquid line then couples to the cup, making for easier replacement. Using diferent pistons, one could use the same evap coil for diferent tonages. This is advantageous in hvac. Whereas the same air handler could be used for a 1,1.5,2,2.5 ton condensing unit.

  14. #14
    Join Date
    Jun 2008
    Location
    South Carolina
    Age
    52
    Posts
    18
    Rep Power
    0

    Talking Re: Walk In freezer,r404

    Quote Originally Posted by nike123 View Post
    Is this system with TEV or with capilary tube?
    Thats it, Im opening the evaporator,cus if it is a txv-its either bad,or needs to be adjusted to new compressor. And your right, if its low temp-its almost certainly a txv. I will also measure superheat at the coil, as well as temps throughout the coil. Either way I'm thinking i have a starved coil-due to undercharge, or txv. I will be back with a solution, or more info. Thanks!~

  15. #15
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Walk In freezer,r404

    Quote Originally Posted by johnanthonyhome View Post
    Thats it, Im opening the evaporator,cus if it is a txv-its either bad,or needs to be adjusted to new compressor. And your right, if its low temp-its almost certainly a txv. I will also measure superheat at the coil, as well as temps throughout the coil. Either way I'm thinking i have a starved coil-due to undercharge, or txv. I will be back with a solution, or more info. Thanks!~

    First check that, if it is TXV, that it is for R404A refrigerant!

  16. #16
    Join Date
    Jun 2008
    Location
    ohio
    Age
    61
    Posts
    19
    Rep Power
    0

    Re: Walk In freezer,r404

    buddy you need to check super heat at the valve. your going to get cold ,open up evap check tonnage [stamped on valve body],and charge of power head[note the colour of the tag]. get on the phone with a good supplyhouse rep. and get the right valve. check line connections[size/type]. install per instructions with valve, bulb placement is critical. clean pipe, insulate bulb. good luck.

  17. #17
    Join Date
    Jun 2008
    Location
    South Carolina
    Age
    52
    Posts
    18
    Rep Power
    0

    Re: Walk In freezer,r404

    Problem resolved. Added refrigerant, brought superheat down to 30 faren. Head pressure high, opened txv 3/4 turn, corrected. Heres the kicker-opened thermostat to test-AND REALISED I HAD SET IT FOR -10 CELSIUS, WHICH IS +10 FARENHEEIGHT!!!!-CORRECTED. Runs like a swiss watch. Thanks

  18. #18
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Walk In freezer,r404

    good for you M8, so we all have learned a lesson here.

    we Belgium's "the piston valve "
    and the rest of you........, well i am sure you learned something.

    thnx anyway,

    Ice
    Last edited by Peter_1; 19-06-2008 at 08:44 PM.

  19. #19
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Walk In freezer,r404

    Ice, lacht u bitje met je luuzn zeggen wij dan in de West Vloanders.
    Wat vindt je trouwens van dit forum? Ik ben er wel fier op.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  20. #20
    jim thorpe's Avatar
    jim thorpe Guest

    Re: Walk In freezer,r404

    Go to your local refrigeration house and give them the specifications of the box and they will give you the information on the proper mechanicals for both condensing unit, evaporator unit, txv, filter, and timer. Relace ALL OF THEM! Do not risk losing your customer by repairing a single component. The system is 15 years old. It did it's duty. it is time to be replaced. Sell this to you customer, or be married to a system that may fail down the road and even though it is not what you replaced, in the customers eyes you were "just out there and fixed it"

  21. #21
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Walk In freezer,r404

    sorry peter voor de late respons,maar ik denk dat ik al veel nieuwe aanwinsten voor het forum heb gedaan,ben er zeker trots op om mee te mogen doen.

    Ice

Similar Threads

  1. walk in freezer
    By ail in forum Refrigerants
    Replies: 8
    Last Post: 29-11-2009, 11:44 PM
  2. superheating 5-8 dc right for walk in freezer r404
    By przemo2 in forum Technical Speculations
    Replies: 3
    Last Post: 09-03-2008, 01:56 PM
  3. walk in cooler EVAPORATOR coil icing up
    By kurt854 in forum Fundamentals
    Replies: 5
    Last Post: 14-06-2007, 07:28 PM
  4. Need Help Sizing New Unit For Walk In
    By refermadness in forum Fundamentals
    Replies: 5
    Last Post: 15-08-2006, 02:14 PM
  5. walk in Chiller--website
    By nik in forum Fundamentals
    Replies: 9
    Last Post: 23-06-2006, 07:46 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •