    Potential Relay not staying open



    I just got a new 3/4 HP 120volt compressor for a freezer. However the relay tries to close every 2 seconds or so over and over again. By doing this it continually is trying to engage the S side of the compressor. There is a Start capacitor before the relay but it doesn't seem to keep sufficient voltage for the relay to stay open.

    The relay is rated is listed on this page.

    http://www.jard.com/prelays.htm model jpr-63

    Please help.

    dave



  2. #2
    87mustang's Avatar
    87mustang Guest

    Re: Potential Relay not staying open

    Relays ( as we are talking potential type ) will short cycle for the following reasons,
    1- incorrect application
    2- low EMF (counter EMF)
    3- not positioned correctly (some are positiom sensitive)
    4- voltage problem from source or through the OLD thermostat.
    5- bad (?) compressor windings
    6- poor electrical contacts/path

    and there is always the famous- it came that way, and is defective.

  3. #3
    Join Date
    Apr 2005
    Location
    INDIA
    Age
    63
    Posts
    84
    Rep Power
    20

    Re: Potential Relay not staying open

    Mr, Lab.
    I thing U dont know any thing about compressor ?
    better contact a tech and get it tested!
    In my opinion,
    a, faulty starting cap,
    b, faulty olp,
    c, compressor motor is short,
    Regards,
    beni joseph.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Potential Relay not staying open

    I will have to agree with Mr Joseph on this one.

    I presume olp is over load protector?

    Chemi

  5. #5
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Potential Relay not staying open

    Potential relays are wired in parallel with start windings and are therefoe controlled by the back EMF of the start winding. You aparently have a mismatch If the start winding or the capacitor was defective you not be able to start the compressor. P.S. the start cap has nothing to do with the relay its function is to increase the phase shift between the run and start windings
    Last edited by wambat; 05-08-2005 at 08:20 PM.

Similar Threads

  1. Hinari and how far to open valves
    By stryker in forum Air Conditioning
    Replies: 6
    Last Post: 14-04-2008, 01:47 AM
  2. voltage drop on relay
    By Temprite in forum Electrical
    Replies: 4
    Last Post: 30-01-2006, 07:55 PM
  3. Open Type Compressors
    By shogun7 in forum Air Conditioning
    Replies: 1
    Last Post: 07-01-2005, 09:15 AM
  4. Freezer Potential Relay not staying open
    By labrosse in forum Trouble Shooting
    Replies: 0
    Last Post: 28-10-2003, 01:53 AM
  5. Alternating Relay Circuit
    By herefishy in forum Industrial
    Replies: 3
    Last Post: 09-07-2002, 06:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •