Results 1 to 8 of 8
Thread: flow rate
    Nov 2007
    India
    74
    flow rate
    How we can increase the ammonia flow rate without using overfeed pump
    May 2008
    New York
    93
    Re: flow rate
    What are you feeding? What is the current method? High pressure feed, Pumper drum?
    Nov 2007
    India
    74
    Re: flow rate
    now the feeding through surge drum. I want to increase the flow rate by 1.5 :1
    May 2008
    New York
    93
    Re: flow rate
    How high is the surge drum above the coil? Is the coil not performing properly or have your needs changed?
    Nov 2007
    India
    74
    Re: flow rate
    surge drum bottom is 500 mm above the wet return connection on coil.
    Aug 2005
    5,302
    Re: flow rate
    Quote Originally Posted by Rajkumar
    If the evaporator is gravity flooded via a surge drum, why do you need to increase the ammonia flow rate by 50%???
    Auckland
    74
    3,357
    37
    Re: flow rate
    Are you feeding sub-cooled liquid into surge drum, and what is the dry suction outlet relationship ? you are asking for trouble by changing levels in surge drum. Hopefully you have a spare compressor in stock, because you are bound to break something sooner than later. You change system balance and the system will bite you. Generally in the wallet. Iceman chime in around-a-bout now, with your wise and extended experience.
    magoo
    Aug 2005
    5,302
    Re: flow rate
    Quote Originally Posted by magoo
    Thanks for the vote of confidence!!
    I was hoping to draw out some more comments before I jumped into the fray. There seems to be a misunderstanding of how these systems work.
    If this is indeed a gravity flooded evaporator with a surge drum the flow rate is already greater than 1.5:1. At full load the circulating rate is probably around 8 or 10! The higher load creates a lot more gas, so the circulation rate actually increase as the load on the coil increases. It decreases as the load is reduced.
  1. flow switch connection
    By afeef in forum The Trail of Tears
    Last Post: 23-12-2009, 06:55 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. high volume flow rate
    By cakabo28 in forum Technical Discussions
    Last Post: 04-10-2007, 03:41 AM
  4. Shell/Tube flow rate?
    By reggie in forum Fundamentals
    Last Post: 17-11-2002, 05:41 PM
  5. R-134 Chilling Unit
    By enginerous in forum Industrial
    Last Post: 25-08-2002, 01:12 PM