    RC Group chillers



    New to the site so sorry if in wrong section. A couple of questions.
    I have just started new job in Russia and got RC group chillers with Copeland compressors.
    Firstly, while carrying out an initial inspection i found that there seems to be oil in the refrigeration system.
    Secondly, i have been told that the condensate water pressure is very irratic and is constantly overpressurizing then will drop depending on amount of stages running.
    If anyone can help as never worked on RC group chillers. Is this a common problem.
    No documentation available as i think locals using as loft insulation. lol.



  2. #2
    Join Date
    Mar 2008
    Location
    England
    Age
    54
    Posts
    273
    Rep Power
    17

    Re: RC Group chillers

    Quote Originally Posted by jonb View Post
    Firstly, while carrying out an initial inspection i found that there seems to be oil in the refrigeration system.

    Why would you not expect this oil to be there?
    Transvestites are men who like to eat, drink, and be Mary.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: RC Group chillers

    Quote Originally Posted by jonb View Post
    New to the site so sorry if in wrong section.
    Hi, welcome to RE!

    A couple of questions.
    I have just started new job in Russia and got RC group chillers with Copeland compressors.
    Firstly, while carrying out an initial inspection i found that there seems to be oil in the refrigeration system.
    If there is no oil in refrigeration system, compressor life expectancy would be 5 minutes. Or it is Turbocor (Danfoss, not Copeland) compressor inside of unit?

    Secondly, i have been told that the condensate water pressure is very irratic and is constantly overpressurizing then will drop depending on amount of stages running.
    That depend on type of condensation temperature regulation. What is in your case? Describe your condensation system!

    If anyone can help as never worked on RC group chillers. Is this a common problem.
    What is model no?
    Last edited by nike123; 12-06-2008 at 02:05 PM.

  4. #4
    Join Date
    Jun 2008
    Location
    Russia
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: RC Group chillers

    I knew as soon as posted that someone would say you need oil in system. I mis-stated, there is large amounts of oil, siteglass black. I understand that there is oil in system.
    nike123 - The compressor is DWM Copeland D6SH-350X.
    The condensation system is pump, chiller, dry coolers, heat exchanger controlled by a honeywell automation system.
    The model of the RC unit is Modello, no number on nameplate.
    Thanks for the response.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: RC Group chillers

    Quote Originally Posted by jonb View Post
    The model of the RC unit is Modello, no number on nameplate.
    Could you find here your model?
    General catalog

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: RC Group chillers

    Quote Originally Posted by jonb View Post
    I knew as soon as posted that someone would say you need oil in system. I mis-stated, there is large amounts of oil, siteglass black. I understand that there is oil in system.
    Oil should be checked after system stabilize in full load condition.

  7. #7
    Join Date
    Jun 2008
    Location
    Russia
    Age
    50
    Posts
    9
    Rep Power
    0

    Re: RC Group chillers

    The chiller was probably manufactured specially for the project as we have extreme conditions.
    The info is
    Model-Modello
    Unita Serie
    FRIGO.W.NRM
    204.F.2.G3
    Can't find anything in catalogue that looks anything like what we have.
    After carrying out several trials it seems as it likely to be an automation problem so gonna get Honeywell back to check.
    Cheers for the help

Similar Threads

  1. Air cooled chillers vibration isolation
    By vijay_study in forum Air Conditioning
    Replies: 3
    Last Post: 06-10-2009, 08:53 PM
  2. Direct Driven Chillers
    By james.waite in forum New Technologies
    Replies: 3
    Last Post: 16-05-2008, 10:56 PM
  3. low pressure amplification (for chillers)
    By knight rider in forum Technical Speculations
    Replies: 2
    Last Post: 11-05-2008, 11:21 PM
  4. Chillers versus packs
    By Peter_1 in forum Technical Speculations
    Replies: 15
    Last Post: 17-01-2004, 09:48 PM
  5. Centrifugal chillers
    By reggie in forum Industrial Compressors
    Replies: 2
    Last Post: 02-05-2002, 07:22 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •