    Question R134a Capillary lines



    Hello all,
    Somebody ask'd me a question today to which i did not know the definative answer so i open up to those brainy ones amonst you.

    Why does R134a block capillarys when no other gas seems to. ?.

    The only thing i can think of is POE oil more suseptable to cloging when overheated ?. Is this the answer or is it just one of those we know it happens so accept it facts of life

    Regards


    Raymond



  2. #2
    Join Date
    Oct 2003
    Location
    brazil
    Age
    59
    Posts
    43
    Rep Power
    0
    hi Raymond can to be philter dry ?

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    As I understand it, POE is highly detergent. It scrubs the system clean, and deposits all of the gunk in the drier and cap tube.

  4. #4
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25
    Hello Gary,
    I was always under the impression that one of the reasons for soldering with OFN blowing through on a R404 system was that the GAS was almost like a detergent and would pick all the burnings off the pipe. Is his not the case and it is actually the OIL that picks up any deposits on the pipework not the gas

    Regards

    Raymond

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    hello raymond.

    after it happend to me a few times in the past year, I made a small research and this is what I came out with:
    the problem accures mainly in domestic refrigerators.
    they differ from other systems by having a steel condenser.
    the residue found inside a cut open filter/drier was picked up with a magnet!! so it was not copper or aluminium (aluminum in usa).

    therefore my conclusion is that either the poe oil or the gas is "eating" the steel condenser and that stuff is blockingthe cup tube.

    as I've mantioned before, I take 5% off the cup tube and charge with r-12 ( no law against it in my country) and problems gone.

    ask your friend to open a fifter/drier with about 2cm of cup tube and check it out.


    chemi

Similar Threads

  1. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 12:44 AM
  2. metric capillary tube
    By tralex in forum Fundamentals
    Replies: 5
    Last Post: 21-02-2006, 06:57 AM
  3. Pressure Transmitter R134a Setpoints
    By cooltrain in forum Technical Speculations
    Replies: 0
    Last Post: 28-02-2005, 09:05 AM
  4. Replies: 5
    Last Post: 01-03-2004, 09:59 PM
  5. Minimal required R134a speed in suction line
    By DaBit in forum CPU Overclockers
    Replies: 32
    Last Post: 08-05-2002, 05:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •