    Question Extra Low Temperature System



    Hello Friends,
    Is there any one who has any experience in "Very Low Temperature Systems" ? (Under -120 F)


    Regards,
    Alireza



  2. #2
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    There are several in here who have experience with ultra-low temp systems.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46
    hello alireza,
    this is cooooooold what you are looking for, try also at: http://www.revco-sci.com they deal with that enviroment.
    good luck and watch your fingers, at that temperature they might fall off without you even notice!!

    chemi-cool

  4. #4
    Germada's Avatar
    Germada Guest
    Hello there,

    What do you want to know about Ultra low temperature??
    I am the service technician for Revco in Europe.

    Regards,

  5. #5
    Join Date
    Apr 2002
    Location
    Tehran-IRAN
    Age
    48
    Posts
    27
    Rep Power
    0
    Hello, Germada!
    Thanks to you for your reply. I'm looking for some suppliers of very low temperature refrigeration part such as thermometer, thermostat,....compressor , TEV,.......valves and some others.

    Regards,
    Alireza

  6. #6
    Join Date
    Apr 2002
    Location
    Tehran-IRAN
    Age
    48
    Posts
    27
    Rep Power
    0
    Dear Germada,
    I have many questions from you

    I Think, using of R-23 in refrigeration systems which required evaporator space temperature less than about -80 C is not proper. Simply because the R-23's Saturated pressure in -82 C is
    1.015 bar absolute.( equal to 0 bar guage in sea level).

    Working of the compressor in this condition, causes to decreasing of the compressor's life time and using of the oil separators or such things are not perfect ways to prevent of the compressor failures because of its working in the condition very close to vacuum.



    what is the best Refrigerant for temperature range of -100 C to -150 C ?


    Regards,
    Alireza

  7. #7
    Join Date
    Apr 2002
    Location
    Tehran-IRAN
    Age
    48
    Posts
    27
    Rep Power
    0
    ......................and how it is wonderful, touching the "Extra Low Temperatures"!!!!!

    You have to be very good lucky that you work in this part of refrigeration systems.

  8. #8
    Germada's Avatar
    Germada Guest
    Hello Alireza,

    First of all I will provid you with the name and address from the Revco dealer in your area.

    Talking about the -86°C units, these are 2 stage units provid with both a Copeland compressor (1 Hp).

    Gascharges from the 1e stage is a mixture from R134a and R404a.
    2e stage is a gasmixture from R404a and R508b, Amount is of course depending on the size of the machine.

    Yes, the compressor is running in vacuum, but these compressors are specialy designed for ultra low temperature freezers.
    So this is absolute no problem.

    The -140°C and the -150°C freezers are build with 1 Copeland scroll compressor ( 3,5 hp)

    The gas inside this machine is a mixture of 5 different gasses.

    R134a
    R142b
    R14
    R508b
    And the last gas is Argon.

    Question: Are you working on a unit?

    If you need more info please let me know and will help you out with any problem you have.
    I am working now for 13 years on these units.

    Best regards,
    Germada

  9. #9
    Join Date
    Apr 2002
    Location
    Tehran-IRAN
    Age
    48
    Posts
    27
    Rep Power
    0
    Dear Germada,

    Thank you very much for your wonderful answer.
    You opened a new horison front of my eyes about cascade refrigeration systems, I had never thought about mixing the refrigerants together for making required properties.My questions have been twice .

    A question :

    When we mix some Refrigerants together with special percents,how it is possible to determine the compresor's characteristics, such as Refrigeration capacity, Power consumption,........etc,that we are required to know for designing a system?

    Also, I don't know how much this thinking is correct :

    It is possible to use a compressor of an special refrigerant [for example R-502], to compress another refrigerant [for example R-13] in a condition with same compression ratio.[if we charge it with proper oil] I have never seen the special compressors of Copeland or other companies for R-13, R-14,.... and some other special refrigerants in the list of their products and it is why I think so.

    If I think correct, I'm wondred that how it is possible to guess the compressor specifications with this new Refrigerant.


    The extra low temperature system is a part of AC&R industry that always makes me mad of it.
    In my brain, it is the end of refrigeration engineering. I love to have a chance of working in this field, but Unfortunatelay, I have not any chance to work on this systems. I have worked on commercial AC&R systems for about 4 years and on Automotive A/C units [specially, bus A/C unit] for about 3 years.[I'm student yet.] But, these always have not limited me to thinking not on other applications, specially Ultra low temperatures.

    Best Regards,
    Alireza

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. Q=? h1=? mechanical schematics
    By fridg in forum Technical Speculations
    Replies: 22
    Last Post: 19-03-2006, 01:43 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •