    Sporlan Heat Reclaim Valve



    Has anybody encountered Sporlan Heat Reclaim and Condenser Split Valves leaking from the rubber O ring that seals the two halves of the valve body?
    We have found at least five in the last year, all have been 2 1/8", some are R404a some R507 most occur after installed for around a year, short cycling of the controls doesn't appear to be a problem, the latest two I found on a site last night that has only been running for 3 months, one rack constantly on heat reclaim and condenser split to reheat store, the other cycling, both splitters pissing gas
    Costing big $$$ in gas and we'll probably install around 40 or 50 of these valves next year, goodbye profits!
    I reckon the material is the problem, would be better of with the white O rings used on Rotalock service valves, dont know what they are made of, maybe teflon or neoprene but they last longer than these rubber numbers.
    Any others come across this? Faulty batch maybe?



  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    510
    Rep Power
    24
    No doubt the valves in question are the Type 16D. The date code on the valve would help, in addition to the refrigerant and brand of oil. But the Prof will check into this situation next week.
    Prof Sporlan

  3. #3
    Join Date
    Apr 2002
    Location
    Pennsylvania, USA
    Age
    55
    Posts
    78
    Rep Power
    0
    I've had a couple 16D's leak at that connection.

    All were on racks converted from 502/MO to 404a/POE, so I deduced that it was because of a combination of factors:

    • The gaskets were several years old.
    • The racks were being run at less than ideal discharge pressures with 502.
    • A deep vacuum was pulled on each system during the changeout of the gas, which I believe may have had an undesirable effect on the gasket, which was accustomed to having 225-250 psi positive pressure on it. (JMO)
    • The Polyolester oil's known solvency may have caused the older gasket material to break down.


    These were my assumptions.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    We've done a lot of retrofitting the past years on racks in supermarkets, mostly R22 --> R404a. After the 1st and 2 nd, we had several leaks on all kind af seals (mostly on shutt-off valves), heat reclaim valves, sometimes on the oil sight glass,
    After this experiences, the replacement of alle the shutt-off valves became a standard procedure.
    These valves where mainly of the brand Danfoss and Alco.
    Peter
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi
    o-rings and gaskets will leak when changing refrigerants, it's a fact of life
    the oils use with different refrigerants condition the seals, when you change the refrigerant, even if you change the oil for a new like for like you will have leaks.
    The only answer is to change all o-rings especially and gaskets of cetain types that you have found by experience in the past leak.
    Regards. Andy.

  6. #6
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    764
    Rep Power
    25
    I realise lots of seals don't like refrigerant and oil changes, but all of these are on brand new racks, cases, condensers and pipework, R404a and R507, polyolester oil- bitzer BSE32 (oil analysis after commissioning, replaced if required- usually not), all new. All systems pressure tested to 300 psi then evacuated to 500 microns, then leak tested on startup. All is good for between two to twelve months, as I said before, controls short cycling has been investigated and is not the problem. Will see if I've got the batch numbers in the truck... Model of the split valves is 16D17B-SC, stamped on the body (I guess this is the batch #) is 3-01 B SC. I know we have had heat reclaim valves leak under warranty too, model 16D17B can't remember the exact batch #'s but pretty sure they all end in -01B.
    Andy, wish I could change the O ring easily, have to unsweat or cut the valve out to get guts apart, valves are mounted at the condenser, between the headers, 2 1/8" pipe doesn't have much flex and I don't want to crack the condenser header, if I gotta unsweat it to get the O ring on then I'm gonna change the ******* of a thing, its becoming too common though and pretty costly, wouldn't care if the customer was paying... do parker and alco sell heat reclaim and condenser split valves? any good?

  7. #7
    BobClegg's Avatar
    BobClegg Guest

    Re: Sporlan Heat Reclaim Valve

    Check out PE Valve Company - They make serviceable 3 way & 4 way valves up to 175 Tons

  8. #8
    Join Date
    Jul 2001
    Location
    Sydney, Australia
    Posts
    764
    Rep Power
    25

    Re: Sporlan Heat Reclaim Valve

    Nah mate - will stick with the sporlan valves - as it turns out they reckognised the issue and the valves are now hermetically sealed - no gasket or o'ring to leak and they do the trick nicely.
    ...and she said "give it to me you big fridgie"

Similar Threads

  1. Heat Reclaim
    By chilled2005 in forum Supermarket Refrigeration
    Replies: 19
    Last Post: 05-05-2008, 05:32 PM
  2. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  3. heat pump capacity adjust
    By Lc_shi in forum Fundamentals
    Replies: 5
    Last Post: 14-02-2006, 08:32 AM
  4. Heat Reclaim
    By TAKO in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 07-06-2004, 03:41 PM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •