10-06-2008, 02:04 PM #1
New System Evacuation Procedure
I have new Ice Rink system under construction. What is a recommended vacuum pressure we should evacuate system to and how long to keep it under such vacuum to approve the installation as vacuum-leek-free? Thanks.
-Witold1
-
10-06-2008, 08:46 PM #2
Re: New System Evacuation Procedure
I can only speak for Europe: leaktesting with vacuumed is prohibited. You must pressurize at 1.1 max operating pressure.
If you vacuum, you only have a pressure difference of 1 bar and this is not a real life situation.
I doubt this is common practice in the US.
Is it with NH3?
Why not with OFN?It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
10-06-2008, 11:05 PM #3
Re: New System Evacuation Procedure
What does it say in the project specification about the system tests to be performed.
What does the equipment supplier require?
This information should be available to you on site.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
11-06-2008, 01:16 AM #4
Re: New System Evacuation Procedure
Vacuums are used for dehydration of the refrigeration system only. If you want to ensure the system is pressure-tight, use a pressure test.
Then once you are sure the system is leak-free, then pull a vacuum to assure the system has NO moisture in it.If all else fails, ask for help.
Similar Threads
-
Daikin fault codes
By Chris2005 in forum Air ConditioningReplies: 45Last Post: 21-03-2012, 10:09 PM -
Leak Testing?
By Thana in forum Trouble ShootingReplies: 36Last Post: 31-08-2010, 02:57 PM -
System Burn Out Troubleshooting
By altaf22m in forum Technical DiscussionsReplies: 13Last Post: 07-05-2010, 09:24 AM -
Burn out System, Clean up procedure. & Troubleshooting.
By altaf22m in forum CommercialReplies: 19Last Post: 15-04-2008, 07:03 PM