    Copeland scroll pump



    Good morning everyone, Anyone had the problem of the croll pump making extremely loud noises a few minutes after start up ? Start is fine. I am calling for a service tech later today, but here in Las Vegas it's a darn good idea to have a diagnosis to any problem before you let anyone even look at your stuff !
    I feel that the time delay switch might be faulty ? Anyway, after you guys retire, you can sit on the computer all night too. LOL Have a great day, stay safe, and thanks for any help.



  2. #2
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: Copeland scroll pump

    Quote Originally Posted by westnlas View Post
    Good morning everyone, Anyone had the problem of the croll pump making extremely loud noises a few minutes after start up ? Start is fine. I am calling for a service tech later today, but here in Las Vegas it's a darn good idea to have a diagnosis to any problem before you let anyone even look at your stuff !
    I feel that the time delay switch might be faulty ?
    westnlas,

    I'm assuming this is a residential unit so I'll rule out 3-phase.

    It could be this:

    Some model scrolls have an internal pressure relief (IPR) valve. This valve opens at a discharge to suction differential of 375 to 450 psi (R-22) or 550 to 625 psi (R-410A). Usually due to a restriction in the system

    You should definitely call a service tech soon.

  3. #3
    westnlas's Avatar
    westnlas Guest

    Re: Copeland scroll pump

    Yes, it is a residential unit. When it first did it, I noticed the contacts on the relay contactor were badly burnt and arcing, so I replaced that part. I didn't like the look of the capacitor, so I had it checked, and it was good. A restriction could happen, but I didn't know the R22 could clog up. The only other thing could be a broken part in the line ? I've never had the system cracked since installed. Thanks a ton ! Now just finding the right guy to take a look at it. Like I said, stay safe, don't let experience make you complacent guys.

  4. #4
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16

    Re: Copeland scroll pump

    If motor runs but compressor does not compress, it is what westnlas mentioned, or it could be a temperature actuated unloader depending on Scroll model. But if the compressor keeps compressing you could be getting liquid slugs and either way you need to have the system checked soon. It is not normal for scrolls to make relays fail unless they are flooded with refrigerant on sturtup. Three phase systems would break the scrolls, single phase will cause motor protector trip (thus afecting contactor life) until the motor boils enough refrigerant to let the motor start. Any of these conditios will cause a failure soon. So call the technician now!

Similar Threads

  1. liquid ammonia pump calvitation
    By Kathleen in forum Trouble Shooting
    Replies: 23
    Last Post: 20-05-2011, 02:18 AM
  2. Help with condensor pump
    By Bakerbj in forum Air Conditioning
    Replies: 23
    Last Post: 14-06-2009, 12:39 AM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  5. System Pump Down
    By Brian_UK in forum Technical Speculations
    Replies: 16
    Last Post: 25-10-2001, 10:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •