    Converting mbar liters/s to grams per year



    I've got a mass spectrometer, measuring helium leakages from a known volume as a multiple of mbar l/s, e.g. 10e-5 mbar l/s is the leakage capable of changing the pressure by 0.01mbar in 0.1 liter of volume in a time of 100seconds.
    This is normal for all mass spectrometers.

    How this can be converted into grams/year as required per EN378-2?

    Thanks anybody



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Converting mbar liters/s to grams per year

    Try here. Who knows........

    http://www.onlineconversion.com



    Chemi

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Converting mbar liters/s to grams per year

    So,
    You got a pressure differential / volume / time.

    And you want to get a weight differential / time.

    Sorry M8, can't se how it can be done, its a bit like comparing apples and pears to me. Completely different units...


    You could obviously calculate the volume lost per /time unit and multiply this with the specific weight of your chosen gas...
    Just a thought.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Converting mbar liters/s to grams per year

    Doubt if you have a set of weighing scales suitable but..

    What is the weight of the helium at the start of the test and at the end ?

    Would these numbers help in the calculation?

    edit: I think my comments above are foolish having now read the article linked below. I also think that you are using a machine that is not designed to give you the answers that you want. (I could be wrong of course)

    http://www.fda.gov/ora/Inspect_ref/itg/itg20.html
    Last edited by Brian_UK; 09-06-2008 at 08:26 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Converting mbar liters/s to grams per year

    The viking: I'm not comparing apples to pears: pV = nRT, and as such a variation of pressure corresponds, everything else unchanged, to a variation in moles of gas.

    For Brian: I can't weigh the helium, because I'm just testing a leakage of few parts per million of helium gas into a controlled chamber. But you are right: I just would like to resolve the scale into something human readable, also because the EN378 gives me a max leakage rate as grams/years and not in ppm or mbar l/s

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Converting mbar liters/s to grams per year

    I can't answer your question but are you sure EN378 asks for gr/years?
    I can be wrong but I think EN378 asks for a leakage in %/year of the total gas charge in the system and there's also a specification about the accuracy of the leak checker which is in gr/years.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Mar 2006
    Location
    Norfolk
    Posts
    160
    Rep Power
    19

    Re: Converting mbar liters/s to grams per year

    From EN378

    ". Maximum leakage rates

    Refrigerant leaks shall be identified and repaired as soon as practicable by a competent person and the system shall only be put into service again when all leaks have been repaired and a competent person has inspected the installation. All measures, in accordance with the best available techniques, have to be taken in order to reduce the relative loss of refrigerant below a maximum of 5%."

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Converting mbar liters/s to grams per year

    Quote Originally Posted by Paulajayne
    All measures, in accordance with the best available techniques, have to be taken in order to reduce the relative loss of refrigerant below a maximum of 5%."
    That's interesting... 5% of what?

    The total refrigerant charge I would assume, but is there a rate at which the 5% is based on, or is it simply 5% of the total charge at any one time?
    If all else fails, ask for help.


  9. #9
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Converting mbar liters/s to grams per year

    Quote Originally Posted by NoNickName View Post
    The viking: I'm not comparing apples to pears: pV = nRT, and as such a variation of pressure corresponds, everything else unchanged, to a variation in moles of gas.
    OK,
    But to me, the formula given as mBar/l/s does not contain any weight reference...
    And you are asking for g/yr, which to me do contain a weight reference.
    Thus it will not be a simple formula and thus the second part of my previous post:

    Quote Originally Posted by The Viking View Post

    You could obviously calculate the volume lost per /time unit and multiply this with the specific weight of your chosen gas...
    Just a thought.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Converting mbar liters/s to grams per year

    Quote Originally Posted by US Iceman View Post
    That's interesting... 5% of what?

    The total refrigerant charge I would assume, but is there a rate at which the 5% is based on, or is it simply 5% of the total charge at any one time?
    No, it's 5% of the initial charge which can be found in the logbook.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Converting mbar liters/s to grams per year

    Thanks Peter. That makes sense.
    If all else fails, ask for help.


  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Converting mbar liters/s to grams per year

    Thanks all.
    For The Viking: the weight is grams of the selected refrigerant. In my case is grams of helium, which by chance is much lighter and molecularly smaller. So the helium leakage must be then be converted to refrigerant leakage by means of respective molecular radius.

    Peter: thanks for your input. Very much appreciated, so it looks like it really doesn't matter what it is the leak rate of a newly bought component?

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Converting mbar liters/s to grams per year

    No it doesn't matter, as long as you stay below 5% of the initial charge.
    Are you testing the compressors in vacuum or under pressure? At Copeland and Bitzer, they're testing the compressors under vacuum and the mass spectrometer is at the outlet of the vacuumpump.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Converting mbar liters/s to grams per year

    I'm pressurizing the compressor with helium and test it in a chamber.
    Last edited by NoNickName; 12-06-2008 at 03:35 PM.

  15. #15
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Converting mbar liters/s to grams per year

    So completely different as they do it at Copeland or Bitzer.
    They need much less gas to test and they can install their spectrometer on a safe place.
    They also heat the windings with a controlled DC current to speed up the vacuum process while heating the varnish.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  16. #16
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Converting mbar liters/s to grams per year

    Quote Originally Posted by Peter_1 View Post
    So completely different as they do it at Copeland or Bitzer.
    They need much less gas to test and they can install their spectrometer on a safe place.
    They also heat the windings with a controlled DC current to speed up the vacuum process while heating the varnish.
    I see but how do they test the compressor for leakages without pressurizing the compressor?

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Converting mbar liters/s to grams per year

    They put the compressor under vacuum with vacuum hoses coming through a platform.

    Above the compressor test stand hangs some sort of a shelter/hood in steel of +/- 1 to 2 mm thick.
    At the underside, there's a gasket.

    On this hood, there's a connection with a helium hose.

    They lower electrically this hood over the compressor housing and the gasket seals by his own weight on the flat platform where the compressor is standing on.

    As the housing is closed, they inject some helium in this housing and start at the vacuumpump the helium measurement which enters the compressor via eventual leaks.

    They know the amount of standard leaks through the
    gaskets (every gasket leaks a certain amount helium they told me) and the leakchecker records this preset value and gives a printout of an eventual leak.

    While this leakcheck is performing, they make ready another compressor on a second platform and on a tirth they disconnect an already tested compressor.

    There's a roller chain behind these test stands which delivers the compressors.

    I don't remember if the helium is exhausted by a fan before they lift up the hood.

    I think Daikin Europe here nearby is doing it the same way.

    Does this make sense Alles.?
    Last edited by Peter_1; 14-06-2008 at 05:43 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Converting mbar liters/s to grams per year

    Yeah, well it's not much different from what we do.