I designed a refrigeration systems for a falling film chiller.
It is supposed to maintain 35F water temp for salad processing unit.
Both the systems has similar conditions.
One system is equipped with Bitzer Semi Herm. compressor and is running fine from last ONE year.
Second System has Copeland Scroll compressor, which has been replaced for FOUR times in last ONE year.
Last compressor only ran for 1 month and got seized.
Everytime after the compressor replacement, both the suction and liquid filters are replaced with the oil.
Last time, some acid was found in the system, which has been cleaned by changing the oil 4-5 times.
After changing last comp., oil acid test is found GOOD.
Copeland report says that failure happened due to refrigerant dilution.
System superheat is 18F, subcooling, discharge temp, etc all is within envelop.
Comp is appox 10' higher than falling film evap.
It has continous pump-down cycle and HG by-pass.
Indoor application, room maintained at 70-75F.
Comp. has Crank case heater, which was found to be defective in last compressor.
Can you suggest, what could be the reason????????
Can too much oil cause refrigerant dilution??
Any other paramets, which can be checked/adjusted?
Oil return in the system seems not to be problem.
Evap outlet has U bend for oil return!!
-
25-05-2008, 07:38 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Scroll Compressor Seizure
No! But liquid refrigerant in crankcase could cause oil dilution. That is the cause of last Copeland compressor seizure by Copeland report.
Also, you found that at last compressor crankcase heater is defective. That has caused compressor seizure, because measures as pump-down, obviously don't work satisfactory.
What are conditions around compressors regarding possibility that compressor is coldest place in instalation?
What was previous compressors cause for death?
Do you have refrigerant diagram to show!
Check this Copeland buletin:
http://www.hvacrinfo.com/cope_ae_bulletins/TAE1182.PDF
-
25-05-2008, 07:39 PM #3
Re: Scroll Compressor Seizure
Hi Jwasir,
How frequently does the compressor stop and start?
I have found that copeland scrolls seem to pump out some oil on starting, too frequent starting seems to lower the oil level quicker than it returns to the compressor, this was on milk tank dx systems.
Jon
-
25-05-2008, 09:55 PM #4
Re: Scroll Compressor Seizure
If the problem was reported as oil dilution then the compressor is most likely experiencing flooded starts or low suction superheat.
If the oil heater had failed that might be part of the total problem, but if compressors are failing every three months or so then I would concentrate on what might be causing the the liquid accumulation in the compressor.If all else fails, ask for help.
-
25-05-2008, 11:38 PM #5
Re: Scroll Compressor Seizure
[QUOTEWhat are conditions around compressors regarding possibility that compressor is coldest place in instalation?
What was previous compressors cause for death?
Do you have refrigerant diagram to show!
[/COLOR][/COLOR][/QUOTE]
Compressor is located above the Falling Film Chiller and ambient temp is around 70-72F.
Copelend report for previous comp is still pending.
Comp. runs for approx. 30-40 mins and stops for 10-15 mins.
We have continous pump down, how can we check and avoid flooded starts?????? Superheat seems to be ok.
-
26-05-2008, 03:22 AM #6
Re: Scroll Compressor Seizure
Originally Posted by jwasir
Originally Posted by jwasir
This is probably my best guess right now based on the comments so far.If all else fails, ask for help.
-
26-05-2008, 06:06 PM #7
Re: Scroll Compressor Seizure
I Can Double Check The Time With Hg.
How Can I Check/avoid Flooded Starts?
-
27-05-2008, 04:09 PM #8
Re: Scroll Compressor Seizure
Hi All,
After adjusting the HG by-pass, system runs for approx 2 hours and stops for 1/2 hr.
Again, the super heat seems to be fine 18F.
I would like to know what should be the right pressure for Pump Down?
Should the system be taken to 0 PSIG or some higher pressure?
Thanks in advance!
-
27-05-2008, 06:48 PM #9
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
08-06-2008, 12:52 PM #10
Re: Scroll Compressor Seizure
try to mount and inverter regulater system, so the comp. dont have to frequently stop and restart,but stays on a regular working base.
is it the correct type,ho has made power calculations??
Ice
Similar Threads
-
Copeland Scroll Advanced Protection Problems
By dwayne in forum Trouble ShootingReplies: 8Last Post: 24-09-2010, 06:54 AM -
use of digital scroll technology
By katyalrk in forum Technical DiscussionsReplies: 6Last Post: 11-11-2008, 02:12 PM -
copeland ZR scroll vs VR scroll
By Lc_shi in forum Technical SpeculationsReplies: 7Last Post: 03-09-2008, 04:27 PM -
Hermetic reciprocating versus hermetic scroll
By Cofreth in forum Technical DiscussionsReplies: 26Last Post: 19-11-2005, 06:29 PM