    high suction pressure



    ive been working on a goodman a/c thats about 6 yrs old suction pressure is 200 head pressure is 200. did a amp check on the compressor it 23. rla is 12.1 . the amps seemed high is this normal? evaporator is a little dirty but not bad. inside fan is blowing good. thanks for any info



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: high suction pressure

    It would appear that the compressor has stalled and drawing lock rotor amps.

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: high suction pressure

    Quote Originally Posted by Magoo View Post
    It would appear that the compressor has stalled and drawing lock rotor amps.
    I would expect lock rotor amps to be 5-7 times of full load amps (rla).

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: high suction pressure

    Quote Originally Posted by david ashley View Post
    ive been working on a goodman a/c thats about 6 yrs old suction pressure is 200 head pressure is 200. did a amp check on the compressor it 23. rla is 12.1 . the amps seemed high is this normal? evaporator is a little dirty but not bad. inside fan is blowing good. thanks for any info
    Is that heat pump or only cooling A/C?

  5. #5
    Join Date
    May 2009
    Location
    texas
    Age
    60
    Posts
    7
    Rep Power
    0

    Re: high suction pressure

    no, this is not a heat pump.

  6. #6
    Join Date
    Aug 2007
    Location
    Perth, West Australia
    Age
    55
    Posts
    11
    Rep Power
    0

    Re: high suction pressure

    Let me get this straight. The compressor is running and the suction and head pressure are the same? If this were a hermetic with this problem, I would say that the discharge line inside the compressor has broken and the refrigerant is recirculating inside it. If this is the case, suction line entering will be warmer than expected and discharge line leaving will be cooler than expected.

  7. #7
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: high suction pressure

    Suction Pressure and discharge pressure both are 200 PSI seems that the system might have been recently topped up with refrigerant and it appears overcharged as both suction and discharge are same.
    Please remove refrigerant till suction is around 60 to 70 PSI for R-22 and check.

  8. #8
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: high suction pressure

    There are following possibilities
    1. Relay is functioning wrong

    2. The run and start winding getting short, check for Resistance of both
    3.the discharge line inside the compressor has broken and the refrigerant is recirculating inside it and for verification you can check the discharge will be colder than compressor dome temperature.

    4.You can also check for noise (abnormal) from the compressor.

    Thanks
    Amit Saxena

  9. #9
    Join Date
    Jul 2009
    Location
    Berkshire
    Age
    50
    Posts
    175
    Rep Power
    15

    Re: high suction pressure

    Quote Originally Posted by Magoo View Post
    It would appear that the compressor has stalled and drawing lock rotor amps.
    Should be (not always) a contactor overload to prevent sustained high current draw. Or the MCB or fuses supplying the unit may be way over the required rating. This should be checked too otherwise serious compressor damage or even fire could be caused.

  10. #10
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: high suction pressure

    ill go a carton that the start capacitor is open circuit,dont reckon locked rotor amps are high enough,and op has hearing problems,broken pipe would be under amp i reckon saturated.
    cheers fellas
    Last edited by lowcool; 09-08-2009 at 01:12 PM. Reason: had belt drive single phase to this current havent done a tin can but
    mmm to beer or not to beer...........lets drink breakfast

  11. #11
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: high suction pressure

    Of course with broken compressor valve(s) current drawn is much less than the rated one.

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: high suction pressure

    Are we assuming the compressor is a recip? Maybe it is a scroll.

  13. #13
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: high suction pressure

    what are the standing pressures and what happens to these when the comp gets power?


    can you pump test the comp?

  14. #14
    Join Date
    May 2009
    Location
    texas
    Age
    60
    Posts
    7
    Rep Power
    0

    Re: high suction pressure

    thank you all for the help

  15. #15
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: high suction pressure

    Low Cool.
    You are a cool guy, 99% of posts would not even remotely understand your post. But I do and your on the button.,

  16. #16
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: high suction pressure

    what you been on magoo?
    less time speakin,more time for drinkin!
    did have a chuckle over garys post didnt think of that one,i might see a goodman compressor one day
    Last edited by lowcool; 10-08-2009 at 01:35 PM.
    mmm to beer or not to beer...........lets drink breakfast

  17. #17
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: high suction pressure

    There are only 2 cases which we could get the said pressure's reading. It's ether compressor's valves are broken or a broken discharge line inside the compress's dome. which mean the compressor is pumping the refrigerant to the suction line directly ,this case will increases the drawn amps where the broken valve decreases the drawn amps
    Last edited by Shibhrac; 19-08-2009 at 01:01 PM.

Similar Threads

  1. need help! compressor kicking out on high pressure
    By SloFuse in forum Trouble Shooting
    Replies: 16
    Last Post: 19-08-2009, 04:46 PM
  2. Pressure drop through the suction line accumulator?
    By frank721 in forum Technical Discussions
    Replies: 61
    Last Post: 14-07-2009, 06:06 AM
  3. High Suction Temps
    By freezerman11 in forum Trouble Shooting
    Replies: 4
    Last Post: 30-06-2009, 08:11 PM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •