09-08-2009, 12:42 AM #1
high suction pressure
ive been working on a goodman a/c thats about 6 yrs old suction pressure is 200 head pressure is 200. did a amp check on the compressor it 23. rla is 12.1 . the amps seemed high is this normal? evaporator is a little dirty but not bad. inside fan is blowing good. thanks for any info
-
09-08-2009, 12:47 AM #2
Re: high suction pressure
It would appear that the compressor has stalled and drawing lock rotor amps.
-
09-08-2009, 01:31 AM #3
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
09-08-2009, 01:33 AM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
-
09-08-2009, 01:44 AM #5
Re: high suction pressure
no, this is not a heat pump.
-
09-08-2009, 04:17 AM #6
Re: high suction pressure
Let me get this straight. The compressor is running and the suction and head pressure are the same? If this were a hermetic with this problem, I would say that the discharge line inside the compressor has broken and the refrigerant is recirculating inside it. If this is the case, suction line entering will be warmer than expected and discharge line leaving will be cooler than expected.
-
09-08-2009, 08:22 AM #7
Re: high suction pressure
Suction Pressure and discharge pressure both are 200 PSI seems that the system might have been recently topped up with refrigerant and it appears overcharged as both suction and discharge are same.
Please remove refrigerant till suction is around 60 to 70 PSI for R-22 and check.
-
09-08-2009, 09:19 AM #8
Re: high suction pressure
There are following possibilities
1. Relay is functioning wrong
2. The run and start winding getting short, check for Resistance of both
3.the discharge line inside the compressor has broken and the refrigerant is recirculating inside it and for verification you can check the discharge will be colder than compressor dome temperature.
4.You can also check for noise (abnormal) from the compressor.
Thanks
Amit Saxena
-
09-08-2009, 09:49 AM #9
Re: high suction pressure
-
09-08-2009, 01:09 PM #10
Re: high suction pressure
ill go a carton that the start capacitor is open circuit,dont reckon locked rotor amps are high enough,and op has hearing problems,broken pipe would be under amp i reckon saturated.
cheers fellasLast edited by lowcool; 09-08-2009 at 01:12 PM. Reason: had belt drive single phase to this current havent done a tin can but
mmm to beer or not to beer...........lets drink breakfast
-
09-08-2009, 05:12 PM #11
Re: high suction pressure
Of course with broken compressor valve(s) current drawn is much less than the rated one.
-
09-08-2009, 05:39 PM #12
Re: high suction pressure
Are we assuming the compressor is a recip? Maybe it is a scroll.
-
09-08-2009, 08:17 PM #13
Re: high suction pressure
what are the standing pressures and what happens to these when the comp gets power?
can you pump test the comp?
-
10-08-2009, 03:40 AM #14
Re: high suction pressure
thank you all for the help
-
10-08-2009, 05:32 AM #15
Re: high suction pressure
Low Cool.
You are a cool guy, 99% of posts would not even remotely understand your post. But I do and your on the button.,
-
10-08-2009, 01:30 PM #16
Re: high suction pressure
what you been on magoo?
less time speakin,more time for drinkin!
did have a chuckle over garys post didnt think of that one,i might see a goodman compressor one dayLast edited by lowcool; 10-08-2009 at 01:35 PM.
mmm to beer or not to beer...........lets drink breakfast
-
19-08-2009, 12:10 PM #17
Re: high suction pressure
There are only 2 cases which we could get the said pressure's reading. It's ether compressor's valves are broken or a broken discharge line inside the compress's dome. which mean the compressor is pumping the refrigerant to the suction line directly ,this case will increases the drawn amps where the broken valve decreases the drawn amps
Last edited by Shibhrac; 19-08-2009 at 01:01 PM.
Similar Threads
-
need help! compressor kicking out on high pressure
By SloFuse in forum Trouble ShootingReplies: 16Last Post: 19-08-2009, 04:46 PM -
Pressure drop through the suction line accumulator?
By frank721 in forum Technical DiscussionsReplies: 61Last Post: 14-07-2009, 06:06 AM -
High Suction Temps
By freezerman11 in forum Trouble ShootingReplies: 4Last Post: 30-06-2009, 08:11 PM -
Benji
By benji in forum Trouble ShootingReplies: 29Last Post: 30-01-2008, 01:25 PM