    Daikin inverter checker.



    Hello there,

    I was wondering if anybody has a schematic of the inverter checker from Daikin. I have seen pictures of it and I would like to built one myself. I think it only has some resistors and leds on it. Thanks!

    Eric.



  2. #2
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin inverter checker.

    Hi.
    See attachment, this will help
    rdgs
    cool#9
    Attached Files Attached Files

  3. #3
    Join Date
    Oct 2007
    Location
    Belgium
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: Daikin inverter checker.

    Hello cool#9,

    That's what I was looking for!
    It's easy to build one yourself, thanks !!

    Eric.

  4. #4
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Daikin inverter checker.

    Quote Originally Posted by on4hf View Post
    Hello cool#9,

    That's what I was looking for!
    It's easy to build one yourself, thanks !!

    Eric.
    Hello
    Just take care to find exactly the same components and it will run well.
    Thanks to RE forum as we can share this kind of information !!
    cool#9

  5. #5
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Daikin inverter checker.

    where do you make the connections???
    indoor / outdoor ?? on power or command lines ??

    looks very nice, if i now how to use it, it would be complete.can it be used on other brands ??

    thnx,

    Ice

  6. #6
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    16
    Rep Power
    0

    Re: Daikin inverter checker.

    Just a word of warning for using these Invertor Checkers. Although they are very good as a quick reference tool you are far better off testing the output voltage between UVW and the DC - terminal with a multi meter.
    Most Daikins have a power transistor check mode that will allow the PCB to output voltage for 2 minutes without the compressor being connected.

    Trouble with invertor checker is if the voltage output is slightly uneven say:
    U -175 VAC
    V - 175 VAC
    W - 150 VAC
    System will fault out, but invertor checker lights will appear normal and you will probably conclude compressor failure incorrectly.

    Just my 2 cents worth from working on many Daikins over the years..

  7. #7
    Join Date
    Dec 2007
    Location
    London
    Age
    57
    Posts
    82
    Rep Power
    17

    Thumbs up Re: Daikin inverter checker.

    Quote Originally Posted by Reefer1 View Post
    Just a word of warning for using these Invertor Checkers. Although they are very good as a quick reference tool you are far better off testing the output voltage between UVW and the DC - terminal with a multi meter.
    Most Daikins have a power transistor check mode that will allow the PCB to output voltage for 2 minutes without the compressor being connected.

    Trouble with invertor checker is if the voltage output is slightly uneven say:
    U -175 VAC
    V - 175 VAC
    W - 150 VAC
    System will fault out, but invertor checker lights will appear normal and you will probably conclude compressor failure incorrectly.

    Just my 2 cents worth from working on many Daikins over the years..

    Spot on.Checker will tell you yes or no but the instrument will give you values.

  8. #8
    Join Date
    Aug 2008
    Location
    Bulgaria
    Age
    39
    Posts
    28
    Rep Power
    0

    Re: Daikin inverter checker.

    Is this working on other Invertors?

  9. #9
    Join Date
    Jun 2007
    Location
    Cyprus
    Age
    73
    Posts
    252
    Rep Power
    17

    Re: Daikin inverter checker.

    Yes Ewgeny, it works on all inverters irrespective of manufacture.
    Icecubes51, you remove the compressor leads and connect them to the device, thereby substituting the tester for the compressor so that the system (electronically speaking) still thinks the compressor is connected and reacts accordingly.

    Trevor

  10. #10
    Join Date
    Feb 2007
    Location
    Cardiff
    Posts
    7
    Rep Power
    0

    Re: Daikin inverter checker.

    I had an inverter PCB fail yesterday on a daikin 10kw split system. It will bring up an 'L5' fault on the controller. The Best way to check if the inverter board has failed is to meter across C1 and C2 which is marked as TP1 on the bottom left hand side of the board. In my case it was a 3phase unit so i should've been getting 580volts across those terminals when the system goes to start, i actually got around 35volts which proved that the board had failed. If it was a single phase unit you should follow the same procedure and you should read 380volts if not then the board has failed. Hope thats been of some use to someone out there!

Similar Threads

  1. Service checker Daikin
    By Cool100 in forum Air Conditioning
    Replies: 26
    Last Post: 22-03-2011, 12:53 PM
  2. daikin L0 inverter problem
    By robin r33 gtr in forum Air Conditioning
    Replies: 17
    Last Post: 11-03-2010, 11:25 PM
  3. Daikin Service CHecker Type III
    By Ben-Hur-Cool in forum Air Conditioning
    Replies: 27
    Last Post: 15-01-2010, 02:53 PM
  4. Daikin VRV Checker
    By bobjob in forum Air Conditioning
    Replies: 6
    Last Post: 04-01-2009, 08:10 PM
  5. Daikin Comp and inverter
    By WCC73 in forum Air Conditioning
    Replies: 5
    Last Post: 08-11-2008, 08:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •