08-06-2008, 12:29 AM #1
Daikin inverter checker.
Hello there,
I was wondering if anybody has a schematic of the inverter checker from Daikin. I have seen pictures of it and I would like to built one myself. I think it only has some resistors and leds on it. Thanks!
Eric.
-
08-06-2008, 10:11 AM #2
Re: Daikin inverter checker.
Hi.
See attachment, this will help
rdgs
cool#9
-
10-06-2008, 09:31 PM #3
Re: Daikin inverter checker.
Hello cool#9,
That's what I was looking for!
It's easy to build one yourself, thanks !!
Eric.
-
11-06-2008, 06:56 PM #4
-
12-06-2008, 06:56 PM #5
Re: Daikin inverter checker.
where do you make the connections???
indoor / outdoor ?? on power or command lines ??
looks very nice, if i now how to use it, it would be complete.can it be used on other brands ??
thnx,
Ice
-
12-06-2008, 10:32 PM #6
Re: Daikin inverter checker.
Just a word of warning for using these Invertor Checkers. Although they are very good as a quick reference tool you are far better off testing the output voltage between UVW and the DC - terminal with a multi meter.
Most Daikins have a power transistor check mode that will allow the PCB to output voltage for 2 minutes without the compressor being connected.
Trouble with invertor checker is if the voltage output is slightly uneven say:
U -175 VAC
V - 175 VAC
W - 150 VAC
System will fault out, but invertor checker lights will appear normal and you will probably conclude compressor failure incorrectly.
Just my 2 cents worth from working on many Daikins over the years..
-
14-06-2008, 10:18 AM #7
-
20-08-2008, 01:10 PM #8
Re: Daikin inverter checker.
Is this working on other Invertors?
-
20-08-2008, 05:18 PM #9
Re: Daikin inverter checker.
Yes Ewgeny, it works on all inverters irrespective of manufacture.
Icecubes51, you remove the compressor leads and connect them to the device, thereby substituting the tester for the compressor so that the system (electronically speaking) still thinks the compressor is connected and reacts accordingly.
Trevor
-
20-08-2008, 07:22 PM #10
Re: Daikin inverter checker.
I had an inverter PCB fail yesterday on a daikin 10kw split system. It will bring up an 'L5' fault on the controller. The Best way to check if the inverter board has failed is to meter across C1 and C2 which is marked as TP1 on the bottom left hand side of the board. In my case it was a 3phase unit so i should've been getting 580volts across those terminals when the system goes to start, i actually got around 35volts which proved that the board had failed. If it was a single phase unit you should follow the same procedure and you should read 380volts if not then the board has failed. Hope thats been of some use to someone out there!
Similar Threads
-
Service checker Daikin
By Cool100 in forum Air ConditioningReplies: 26Last Post: 22-03-2011, 12:53 PM -
daikin L0 inverter problem
By robin r33 gtr in forum Air ConditioningReplies: 17Last Post: 11-03-2010, 11:25 PM -
Daikin Service CHecker Type III
By Ben-Hur-Cool in forum Air ConditioningReplies: 27Last Post: 15-01-2010, 02:53 PM -
Daikin VRV Checker
By bobjob in forum Air ConditioningReplies: 6Last Post: 04-01-2009, 08:10 PM -
Daikin Comp and inverter
By WCC73 in forum Air ConditioningReplies: 5Last Post: 08-11-2008, 08:44 PM