    How to calculate refrigerant charge required?



    Can someone please suggest how to calculate amount of refrigerant charge required in Dx system with flooded condensers?

    Thanks.



  2. #2
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: How to calculate refrigerant charge required?

    use COOLPACK.its free

    nice program for calculations.

    grtz, Ice

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: How to calculate refrigerant charge required?

    The total required charge for refrigerant in an air-cooled condenser depends on several things:

    1. Will the condenser have head pressure control valves? I'm assuming it does since you mentioned flooded condenser.
    2. If so, what is the lowest air temperature that will be encountered during operation? The colder the air is, the more refrigerant it takes to block off the condensing surface.
    3. The safest way is to use 100% of the condenser internal volume...
    If all else fails, ask for help.


  4. #4
    GXMPLX's Avatar
    GXMPLX is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2008
    Location
    weston
    Posts
    348
    Rep Power
    16
    Suggestion: First figure out what size of condenser you need in summer and winter conditions. The volumetric difference between the two is about the amount of liquid you need to flood the condenser in winter (try to use the same type of condenser if possible). Calculate the minimun subcooling you need to compensate for the pressure drop to the last expansion valve, chech condenser manufacturer's data to see how much subcooling it delivers. The differens is the minimun height you must have at the receiver, calculate the volume of liquid refrigerant in it. Add the volume of all liquid lines, add suction side volume times density of suction refrigeran in its average condition, if you don't have manufacturer data for condensers an evaporators, add 30% of condenser pipe volume and 70% evaporator pipe volume. MULTIPLY BY THE DENSITY OF REFRIGERANT AT AVERAGE HIGH SIDE CONDITIONS (USUALLY CONSENSING CONDITIONS) Think of a number between 1 and 10 and add that percent of what you calculated above (this is called a safety factor). If you are charging a perfectly working system the minimum charge should be such that you get enough SUBCOOLING at the outlet of the receiver to feed the expansion valves but you have to do this at maximum thermal load. Please remember it's a suggestion!
    Last edited by GXMPLX; 16-06-2008 at 10:37 PM. Reason: Just learned how to edit silly mistakes! Corrections Capitalized.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: How to calculate refrigerant charge required?

    To charge a system using a flooded condenser; it should be charge at maximum capacity at the coldest temperature. Otherwise you won't know if you have enough refrigerant in the system to block off the condenser surface.
    If all else fails, ask for help.


  6. #6
    Join Date
    Jun 2008
    Location
    India
    Posts
    37
    Rep Power
    0

    Re: How to calculate refrigerant charge required?

    see boiling point of refrigerant,

  7. #7
    frederick Smith's Avatar
    frederick Smith Guest

    Re: How to calculate refrigerant charge required?

    Charge system to no more than 80% of receiver capacity after pump-down. This provides sufficient refrigerant for low ambient operation without overcharging unit.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: How to calculate refrigerant charge required?

    Quote Originally Posted by icecube51 View Post
    use COOLPACK.its free

    nice program for calculations.

    grtz, Ice
    I don't think Coolpack can do this for you
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: How to calculate refrigerant charge required?

    Quote Originally Posted by refriengr View Post
    Can someone please suggest how to calculate amount of refrigerant charge required in Dx system with flooded condensers?

    Thanks.
    What do you mean in fact with a flooded condenser?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: How to calculate refrigerant charge required?

    Quote Originally Posted by Peter_1 View Post
    I don't think Coolpack can do this for you
    It can't.

    The difficult part about accurate refrigerant charge determination lies in understanding the refrigerant density in the 2-phase regions of condenser & evaporator.

    I have developed some software, still currently on trial, for estimating the refrigerant charge for simple refrigerant loops. It's been found to be pretty accurate, thus far - based on test results.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Daikin VRVIII - refrigerant charge
    By gwilliamson in forum Air Conditioning
    Replies: 13
    Last Post: 13-03-2008, 08:39 PM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  4. Calculating refrigerant charge
    By Consultant in forum Refrigerants
    Replies: 2
    Last Post: 10-05-2005, 03:39 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •